Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT P
Connection
2 x M8 socket, 4-pin, P-coded, red
Distributed Clocks
yes
Supply voltages
Connection
See EtherCAT P connection
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 3 A
Current consumption from US
100 mA
+ current consumption of the encoder
+ current consumption of the motor brake
+ auxiliary voltage for the limit switches
UP nominal voltage
UP sum current: IP,sum
max. 3 A
Current consumption from UP
None. UP is only forwarded.
Stepper motor
EPP7041-1002
EPP7041-3002
Motor type
2-phase stepper motor, unipolar or bipolar
Connection
1 x M12 socket
DC link voltage
8…48 VDC
Connection for the DC link voltage
M12 socket
M12 connector
Nominal current per phase
1.0 A
3.5 A
Peak current per phase
1.5 A
5.0 A at 50 °C
Step frequency
max. 32000 full steps per second
Microstepping
up to 64-fold
up to 256-fold
Current controller frequency
approx. 30 kHz
Resolution
approx. 5000 positions per revolution in typical applications
Protective functions
Overload protection, short-circuit protection
Encoder input
Number
1
encoder type
Incremental encoder with single-ended output drivers
Connection
1x M12 socket, 5-pin
Encoder supply
24 VDC from the control voltage US
max. 0.5 A, not short-circuit proof
signals
A, B, C; single-ended
(C = reference pulse / zero pulse)
Signal voltage "0"
-3…2 V
Signal voltage "1"
3.5…28 V
Pulse frequency
max. 400,000 increments per second (quadruple evaluation)
Digital inputs for limit switches
Number
2
Connection
M12 socket
Nominal voltage high level
24 VDC
Signal voltage "0"
-3…2 V
Signal voltage "1"
3.5…28 V
Input current
5 mA
Digital output for the motor brake
Connection
M12 socket
Output voltage high level
Output current
max. 0.5 A
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
Ambient temperature during storage
-40 … +85 °C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 conforms to EN 60529
Approvals
Approvals
CE, UL in preparation
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms