Control word
Bit
15
14
13
12
11
10
9
8
7
6
5
4
3
2
1
0
OL7
OL6
OL5
OL4
OL3
OL2
OL1
OL0
SC
IR
RA
TR
Bit no.
OL7…OL0
(OutLength)
1dec…22dec
The number of output bytes available for the transmission from the controller to the box.
Note: If you have set the size of the send data to 50 x 1 word, the output variables “Data Out n” have the data type “Word”. A Word has a size of two bytes.
Multiply the number of output variables to be sent by two in order to calculate the number of output bytes.
7 .. 4
reserved
3
SC
(SendContinuous)
rise
Continuous sending of data from the FIFO.
The send buffer is filled (up to 128 bytes) by the controller. The buffer content is sent with rising edge of bit SC. Once the data has been transferred, this is acknowledged by the box to the controller by setting the SW.2 bit. SW.2 is cancelled with CW.3.
2
IR
(InitRequest)
1bin
The controller requests the box to initialize. The send and receive functions are blocked, the FIFO pointers are reset, and the interface is initialized with the values of the responsible objects (baud rate 4073, data frame 4074, feature bits 4075). The execution of the initialization is acknowledged by the box with the SW.2 (IA) bit.
0bin
The controller once again requests the box to prepare for serial data exchange.
1
RA
(ReceiveAccepted)
toggle
The controller acknowledges receipt of data by changing the state of this bit. Only then can new data be transferred from the box to the controller.
0
TR
(TransmitRequest)
toggle
Via a change of state of this bit the controller notifies the box that the DataOut bytes contain the number of bytes indicated via the OL bits. The box acknowledges receipt of the data in the status byte by changing the state of the SW.0 (TA) bit. Only then can new data be transferred from the controller to the box.