User calibration
The intended purpose of the user calibration is to calibrate the device, for example, in a smaller output signal range than that calibrated by the vendor. As a result, a higher accuracy can be attained for the smaller output signal range.
The correction function has the same form as the correction function of the vendor calibration:
YU = GU * XU + OU
YU: Output value after user calibration
XU: Output value before user calibration
GU : Gain
OU : Offset
Enabling the user calibration
The user calibration is disabled in the factory. It can be enabled individually for each output. To do this, set the corresponding CoE parameter "Enable user calibration" to TRUE:
Connection
1
0x8030:07
2
0x8040:07
Setting the calibration coefficients
Set the calibration coefficients via the CoE parameters "User calibration offset" and "User calibration gain":
Connection
1
0x8030:15
0x8030:16
2
0x8040:15
0x8040:16