Technical data
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT P
Connection
2 x M8 socket, 4-pin, P-coded, red
Supply voltages
Connection
See EtherCAT P connection
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current: IS,sum
max. 3 A
Current consumption from US
100 mA
Rated voltage UP
UP sum current: IP,sum
max. 3 A
Current consumption from UP
None. UP is only forwarded.
RTD inputs
Number
4
Connectors
4 x M12 socket
Sensor types
  • Platinum RTD: Pt100, Pt200, Pt500, Pt1000
  • Nickel RTD: Ni100, Ni120, Ni1000
  • Resistance/potentiometer up to 4095 Ω
Connection technology
  • 2-wire connection
  • 3-wire connection
  • 4-wire connection
Electrical isolation
The measuring channels have a common isolated ground potential.
Measuring current RL+, RL-
Max. 0.5 mA, load-dependent
Measuring range
Platinum RTD: -200…+850 °C
Nickel RTD: -60…+250 °C (Ni120: -60…+320 °C)
Resistance: 0…4095 Ω
Measuring error
max. ±0.5 K (Pt sensors in 4-wire connection)
Digital resolution
16 Bit
Value of an LSB
Temperature measurement:
   Standard: 0.1 °C
   High-precision: 0.01 °C
Resistance measurement:
   Measuring range 1023 Ω: 1/64 Ω
   Measuring range 4095 Ω: 1/16 Ω
Filter
Digital filter. Cut-off frequency parameterizable: 5 Hz … 30 kHz..
Conversion time
2…800 ms, depending on the parameterization
Default: approx. 85 ms
Diagnostics
  • Open-circuit recognition
  • Limit value monitoring
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
-25 … +55 °C according to cULus
Ambient temperature during storage
-40 … +85 °C
Vibration resistance, shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
Additional checks
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 (conforms to EN 60529)
Housing data
Dimensions W x H x D
30 mm x 126 mm x 26.5 mm (without connectors)
Weight
approx. 165 g
Installation position
variable
Material
PA6 (polyamide)
Approvals / markings
Approvals / markings *)
CE, cULus
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms