Selection of the analog signal type, index 0xF800:0n
In delivery state, all channels of the EP31xx are set for analog voltage measurement (-10 V …+10 V).
Notice
Setting the correct signal type before connecting the sensors
Set the correct signal type before connecting the sensors!
This setting can be made individually for each channel in the CoE object 0xF800:0n. Changes are immediately effective.
Settings 1:
EP31x4-0002: Selection of the signal type
In the case of the EP31x2 the signal type -20 mA to +20 mA can additionally be selected (see illustration below).
Settings 2:
EP31x2: Selection of the signal type
Presentation, index 0x80n0:02
The measured value output is set in factory to two's complement representation (signed integer).
Index 0x80n0:02 offers the possibility to change the method of representation of the measured value.
The negative output value is represented in two’s complement (negated + 1).
Maximum representation range with 16-bit = -32768 .. +32767dec
Input signal
Value
+/- 10 V
0...20 mA
4...20 mA
0...10 V
decimal
hexadecimal
10 V
20 mA
20 mA
10 V
32767
0x7FFF
5 V
10 mA
12 mA
5 V
16383
0x3FFF
0 V
0 mA
4 mA
0 V
0
0x0000
-5 V
-16383
0xC001
-10 V
-32767
0x8000
Overview of further representations
The output value is represented with 15-bit resolution without sign, therefore polarity detection is no longer possible.
Maximum representation range with 16-bit = 0 .. +32767dec
The output value is displayed in magnitude-sign format: MSB=1 (highest bit) in the case of negative values.
Input values (+/- 10 V)
Representation (values dec. / values hex.)
unsigned integer
Absolute value with MSB as sign
10
32767 / 0x7FFF
32767 / 0x7FFF
5 V
16383 / 0x3FFF
16383 / 0x3FFF
0 V
0 / 0x0000
0 / 0x0000
-5
16384 / 0x4000
[-16384] / 0xC000
-10
32767 / 0x7FFF
[-32767] / 0xFFFF
Settings 3:
Presentation types
The presentation types Unsigned integer and Absolute value with MSB as sign have no function for unipolar modules. There is no change in the presentation in the positive range.
Siemens bits, index 0x80n0:05
If this bit is set, status displays are superimposed on the lowest three bits. In the error case "overrange" or "underrange", bit 0 is set.
Underrange and overrange, index 0x60n00:01, 0x60n00:02
Underrange and overrange is indicated as follows:
The threshold values for the mentioned bits and the LED can be found in chapter Measuring ranges.
Limit 1 ad Limit 2, index 0x80n0:13, index 0x80n0:14
If the limits of the values that can be entered in indices 0x80n0:13 and 0x80n0:14 are violated, the bits in indices 0x60n0:03 and 0x60n0:05 are set accordingly (see sample below). The indices 0x80n0:07 or 0x80n0:08 serve to activate the limit value monitoring.
Output limit n (2-bit):
Settings 4:
Limit evaluation
The limit evaluation assumes a signed representation. The conversion to the desired representation (index 0x80n0:02) only takes place after the limit evaluation.
Settings 5:
Linking in the PLC with 2-bit values
    • PLC:
      IEC61131-PLC contains no 2-bit data type that can be linked with this process data directly. In order to transmit the limit information, therefore, define an input byte, e.g.
      Settings 6:
      and link the limit to the VariableSizeMismatch dialog as described in the chapter Process data.
    • Additional task
      2-bit variables can be created in the System Manager.
      Settings 7:
      Linking of 2-bit variable to additional task
    Sample
    Channel 1; Limit 1 and Limit 2 enabled, Limit 1 = 2.8 V, Limit 2 = 7.4 V, representation: signed integer
    Entry in index (Limit 1): 0x8000:13
    (2.8 V / 10 V) x 216 / 2 - 1 = 9,174dec
    Entry in index (Limit 2): 0x8000:14
    (7.4 V / 10 V) x 216 / 2 - 1 = 24,247dec
    Output:
    Input channel 1
    Index 0x6000:03
    Index 60x6000:05
    1.8 V
    0x01hex, (Limit 1, limit value undershot)
    0x01hex, (Limit 2, limit value undershot)
    2.8 V
    0x03hex, (Limit 1, limit value reached)
    4.2 V
    0x02hex, (Limit 1, limit value exceeded)
    8.5 V
    0x02hex, (Limit 2, limit value exceeded)
    Swap Limit index 0x80n0:0E
    The limit function can be inverted by SwapLimitBits in index 0x80n0:0E.
    Output Limit n (2-bit):
    SwapLimitBits setting
    Value
    FALSE (default setting)
    • 0: not active
    • 1: value < limit value
    • 2: value > limit value
    • 3: Value is equal to the limit value
    TRUE
    • 0: not active
    • 1: value > limit value
    • 2: value < limit value
    The Swap Limit function is available according to the table below
    EtherCAT Box
    Swap Limit function from rev.
    EP3162-0002
    -0016
    EP3174-0002
    -0018
    EP3174-0092
    -0016
    EP3182-1002
    -0017
    EP3184-0002
    -0017
    EP3184-1002
    -0018