EP31x4 - Object description and parameterization
EP31x4 - Object description and parameterization 1:
Parameterization
You can parameterize the box via the "CoE - Online" tab in TwinCAT.
EP31x4 - Object description and parameterization 2:
EtherCAT XML Device Description
The presentation matches that of the EtherCAT XML Device Description.
Recommendation: download the latest XML file from https://www.beckhoff.com/ and install it according to the installation instructions.
Introduction
The following section first describes the objects required for normal operation, followed by a complete overview of missing objects.
Objects to be parameterized during commissioning
Index 1011 Restore default parameters
Index (hex)
Meaning
Data type
Flags
Default
1011:0
UINT8
RO
0x01 (1dec)
1011:01
SubIndex 001
If this object is set to “0x64616F6C” in the set value dialog, all backup objects are reset to their delivery state.
UINT32
RW
0x00000000 (0dec)
Index 8000 AI Settings (parameterization of channel 1)
Index (hex)
Meaning
Data type
Flags
Default
8000:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
8000:01
Enable user scale
1
User scale is active.
BOOLEAN
RW
0x00 (0dec)
8000:02
Presentation
0
Signed presentation
BIT3
RW
0x00 (0dec)
1
Unsigned presentation
2
Absolute value with MSB as sign (signed amount representation)
8000:05
Siemens bits
1
Status indicators are displayed on the lowest 3 bits in the status word.
BOOLEAN
RW
0x00 (0dec)
8000:06
Enable filter
1
Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary
BOOLEAN
RW
0x01 (1dec)
8000:07
Enable limit 1
1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
8000:08
Enable limit 2
1
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
8000:0A
Enable user calibration
1
Enabling of the user calibration
BOOLEAN
RW
0x00 (0dec)
8000:0B
Enable vendor calibration
1
Enabling of the vendor calibration
BOOLEAN
RW
0x01 (1dec)
8000:0E
Swap limit bits
1
Swaps the two limit bits, in order to achieve compatibility with older hardware versions.
BOOLEAN
RW
0x00 (0dec)
8000:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
8000:12
User scale gain
User scale gain.
The gain is represented in fixed-point format, with the factor 2-16.
The value 1 corresponds to 65535dec (0x00010000hex) and is limited to +/- 0x7FFFF
INT32
RW
0x00010000 (65536dec)
8000:13
Limit 1
First limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:14
Limit 2
Second limit value for setting the status bits
INT16
RW
0x0000 (0dec)
8000:15
Filter settings
This object determines the digital filter settings for all channels of the module, if it is activated via Enable filter (index 0x80n0:06). The possible settings are sequentially numbered.
UINT16
RW
0x0000 (0dec)
0
50 Hz FIR
1
60 Hz FIR
2
IIR 1
3
IIR 2
4
IIR 3
5
IIR 4
6
IIR 5
7
IIR 6
8
IIR 7
9
IIR 8
8000:17
User calibration offset
User calibration: Offset
INT16
RW
0x0000 (0dec)
8000:18
User calibration gain
User calibration: Gain
INT16
RW
0x0000 (0dec)
Index 8010 AI Settings (parameterization of channel 2)
Index (hex)
Meaning
Data type
Flags
Default
8010:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
8010:01
Enable user scale
1
BOOLEAN
RW
0x00 (0dec)
8010:02
Presentation
0
Signed presentation
BIT3
RW
0x00 (0dec)
1
2
8010:05
Siemens bits
1
BOOLEAN
RW
0x00 (0dec)
8010:06
Enable filter
1
BOOLEAN
RW
0x01 (1dec)
8010:07
Enable limit 1
1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
8010:08
Enable limit 2
1
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
8010:0A
1
Enables user calibration
BOOLEAN
RW
0x00 (0dec)
8010:0B
1
BOOLEAN
RW
0x01 (1dec)
8010:0E
Swap limit bits
1
BOOLEAN
RW
0x00 (0dec)
8010:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
8010:12
User scale gain
User scale gain.
INT32
RW
8010:13
Limit 1
INT16
RW
0x0000 (0dec)
8010:14
Limit 2
INT16
RW
0x0000 (0dec)
8010:15
Filter settings
This object shows the digital filter settings. The filter settings can only be read here. They are set via channel 1 for all channels of the module.
UINT16
RW
0x0000 (0dec)
0
50 Hz FIR
1
60 Hz FIR
2
IIR 1
3
IIR 2
4
IIR 3
5
IIR 4
6
IIR 5
7
IIR 6
8
IIR 7
9
IIR 8
8010:17
INT16
RW
0x0000 (0dec)
8010:18
INT16
RW
0x0000 (0dec)
Index 8020 AI Settings (parameterization of channel 3)
Index (hex)
Meaning
Data type
Flags
Default
8020:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
8020:01
Enable user scale
1
BOOLEAN
RW
0x00 (0dec)
8020:02
Presentation
0
Signed presentation
BIT3
RW
0x00 (0dec)
1
2
8020:05
Siemens bits
1
BOOLEAN
RW
0x00 (0dec)
8020:06
Enable filter
1
BOOLEAN
RW
0x01 (1dec)
8020:07
Enable limit 1
1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
8020:08
Enable limit 2
1
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
8020:0A
1
BOOLEAN
RW
0x00 (0dec)
8020:0B
1
BOOLEAN
RW
0x01 (1dec)
8020:0E
Swap limit bits
1
BOOLEAN
RW
0x00 (0dec)
8020:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
8020:12
User scale gain
User scale gain.
INT32
RW
8020:13
Limit 1
INT16
RW
0x0000 (0dec)
8020:14
Limit 2
INT16
RW
0x0000 (0dec)
8020:15
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz FIR
1
60 Hz FIR
2
IIR 1
3
IIR 2
4
IIR 3
5
IIR 4
6
IIR 5
7
IIR 6
8
IIR 7
9
IIR 8
8020:17
INT16
RW
0x0000 (0dec)
8020:18
INT16
RW
0x0000 (0dec)
Index 8030 AI Settings (parameterization of channel 4)
Index (hex)
Meaning
Data type
Flags
Default
8030:0
AI Settings
Maximum subindex
UINT8
RO
0x18 (24dec)
8030:01
Enable user scale
1
BOOLEAN
RW
0x00 (0dec)
8030:02
Presentation
0
Signed presentation
BIT3
RW
0x00 (0dec)
1
2
8030:05
Siemens bits
1
BOOLEAN
RW
0x00 (0dec)
8030:06
Enable filter
1
BOOLEAN
RW
0x01 (1dec)
8030:07
Enable limit 1
1
Limit 1 enabled
BOOLEAN
RW
0x00 (0dec)
8030:08
Enable limit 2
1
Limit 2 enabled
BOOLEAN
RW
0x00 (0dec)
8030:0A
1
BOOLEAN
RW
0x00 (0dec)
8030:0B
1
BOOLEAN
RW
0x01 (1dec)
8030:0E
Swap limit bits
1
BOOLEAN
RW
0x00 (0dec)
8030:11
User scale offset
User scale offset
INT16
RW
0x0000 (0dec)
8030:12
User scale gain
User scale gain.
INT32
RW
8030:13
Limit 1
INT16
RW
0x0000 (0dec)
8030:14
Limit 2
INT16
RW
0x0000 (0dec)
8030:15
Filter settings
UINT16
RW
0x0000 (0dec)
0
50 Hz FIR
1
60 Hz FIR
2
IIR 1
3
IIR 2
4
IIR 3
5
IIR 4
6
IIR 5
7
IIR 6
8
IIR 7
9
IIR 8
8030:17
INT16
RW
0x0000 (0dec)
8030:18
INT16
RW
0x0000 (0dec)
Index F800 AI Range Settings (EP3174/EP3184 from firmware version 04)
Index (hex)
Meaning
Data type
Flags
Default
F800:0
AI Range Settings
Maximum subindex
UINT8
RO
0x04 (4dec)
F800:01
Input type Ch1
Input signal range for channel 1
UINT16
RW
0x0000 (0dec)
0
-10 V...+10 V
1
0 mA...20 mA
2
4 mA...20 mA
6
0 V...10 V
F800:02
Input type Ch2
Input signal range for channel 2 (values see channel 1)
UINT16
RW
0x0000 (0dec)
F800:03*
Input type Ch3
Input signal range for channel 3 (values see channel 1)
UINT16
RW
0x0000 (0dec)
F800:04*
Input type Ch4
Input signal range for channel 4 (values see channel 1)
UINT16
RW
0x0000 (0dec)
F800:05
Enable Filter Settings Per Channel
BOOLEAN
RW
Standard objects (0x1000-0x1FFF)
The standard objects have the same meaning for all EtherCAT slaves.
Index 1000 Device type
Index (hex)
Meaning
Data type
Flags
Default
1000:0
Device type
Device type of the EtherCAT slave: The Lo-Word contains the CoE profile used (5001). The Hi-Word contains the module profile according to the modular device profile.
UINT32
RO
0x00001389 (5001dec)
Index 1008 Device name
Index (hex)
Meaning
Data type
Flags
Default
1008:0
Device name
Device name of the EtherCAT slave
STRING
RO
EP3174-0002,
EP3174-0092,
EP3184-0002,
EP3184-1002
Index 1009 Hardware version
Index (hex)
Meaning
Data type
Flags
Default
1009:0
Hardware version
Hardware version of the EtherCAT slave
STRING
RO
01
Index 100A Software Version
Index (hex)
Meaning
Data type
Flags
Default
100A:0
Software version
Firmware version of the EtherCAT slave
STRING
RO
01
Index 1018 Identity
Index (hex)
Meaning
Data type
Flags
Default
1018:0
Identity
Information for identifying the slave
UINT8
RO
0x04 (4dec)
1018:01
Vendor ID
Vendor ID of the EtherCAT slave
UINT32
RO
0x00000002 (2dec)
1018:02
Product code
Product code of the EtherCAT slave
UINT32
RO
0x0C664052 (208027730dec)
1018:03
Revision
Revision number of the EtherCAT slave; the Low Word (bit 0-15) indicates the special terminal number, the High Word (bit 16-31) refers to the device description
UINT32
RO
0x00000000 (0dec)
1018:04
Serial number
Serial number of the EtherCAT slave; the Low Byte (bit 0-7) of the Low Word contains the year of production, the High Byte (bit 8-15) of the Low Word contains the week of production, the High Word (bit 16-31) is 0
UINT32
RO
0x00000000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
10F0:0
Information for standardized loading and saving of backup entries
UINT8
RO
0x01 (1dec)
10F0:01
Checksum
Checksum across all backup entries of the EtherCAT slave
UINT32
RO
0x00000000 (0dec)
Index 1800 AI TxPDO-Par Standard Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1800:0
PDO parameter TxPDO 1
UINT8
RO
0x06 (6dec)
1800:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 1
OCTET-STRING[2]
RO
01 1A
Index 1801 AI TxPDO-Par Compact Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1801:0
PDO parameter TxPDO 2
UINT8
RO
0x06 (6dec)
1801:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 2
OCTET-STRING[2]
RO
00 1A
Index 1802 AI TxPDO-Par Standard Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1802:0
PDO parameter TxPDO 3
UINT8
RO
0x06 (6dec)
1802:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 3
OCTET-STRING[2]
RO
03 1A
Index 1803 AI TxPDO-Par Compact Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1803:0
PDO parameter TxPDO 4
UINT8
RO
0x06 (6dec)
1803:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 4
OCTET-STRING[2]
RO
02 1A
Index 1804 AI TxPDO-Par Standard Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1804:0
PDO parameter TxPDO 5
UINT8
RO
0x06 (6dec)
1804:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 5
OCTET-STRING[2]
RO
05 1A
Index 1805 AI TxPDO-Par Compact Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1805:0
PDO parameter TxPDO 6
UINT8
RO
0x06 (6dec)
1805:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 6
OCTET-STRING[2]
RO
04 1A
Index 1806 AI TxPDO-Par Standard Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1806:0
PDO parameter TxPDO 7
UINT8
RO
0x06 (6dec)
1806:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 7
OCTET-STRING[2]
RO
07 1A
Index 1807 AI TxPDO-Par Compact Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1807:0
PDO parameter TxPDO 8
UINT8
RO
0x06 (6dec)
1807:06
Exclude TxPDOs
Specifies the TxPDOs (index of TxPDO mapping objects) that must not be transferred together with TxPDO 8
OCTET-STRING[2]
RO
06 1A
Index 1A00 AI TxPDO-Map Standard Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A00:0
PDO Mapping TxPDO 1
UINT8
RO
0x0B (11dec)
1A00:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x01 (Underrange))
UINT32
RO
0x6000:01, 1
1A00:02
SubIndex 002
2. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x02 (Overrange))
UINT32
RO
0x6000:02, 1
1A00:03
SubIndex 003
3. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x03 (Limit 1))
UINT32
RO
0x6000:03, 2
1A00:04
SubIndex 004
4. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x05 (Limit 2))
UINT32
RO
0x6000:05, 2
1A00:05
SubIndex 005
5. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x07 (Error))
UINT32
RO
0x6000:07, 1
1A00:06
SubIndex 006
6. PDO Mapping entry (1 bits align)
UINT32
RO
0x0000:00, 1
1A00:07
SubIndex 007
7. PDO Mapping entry (5 bits align)
UINT32
RO
0x0000:00, 5
1A00:08
SubIndex 008
8. PDO Mapping entry (object 0x1C32, entry 0x20)
UINT32
RO
0x6000:0E, 1
1A00:09
SubIndex 009
9. PDO Mapping entry (object 0x1800 (AI TxPDO-Par Standard Ch.1), entry 0x07 (TxPDO State))
UINT32
RO
0x6000:0F, 1
1A00:0A
SubIndex 010
10. PDO Mapping entry (object 0x1800 (AI TxPDO-Par Standard Ch.1), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6000:10, 1
1A00:0B
SubIndex 011
11. PDO Mapping entry (object 0x1800 (AI TxPDO-Par Standard Ch.1), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6000:11, 16
Index 1A01 AI TxPDO-Map Compact Ch.1
Index (hex)
Meaning
Data type
Flags
Default
1A01:0
PDO Mapping TxPDO 2
UINT8
RO
0x01 (1dec)
1A01:01
SubIndex 001
1. PDO Mapping entry (object 0x6000 (AI Inputs), entry 0x11 (Value))
UINT32
RO
0x6000:11, 16
Index 1A02 AI TxPDO-Map Standard Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A02:0
PDO Mapping TxPDO 3
UINT8
RO
0x0B (11dec)
1A02:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x01 (Underrange))
UINT32
RO
0x6010:01, 1
1A02:02
SubIndex 002
2. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x02 (Overrange))
UINT32
RO
0x6010:02, 1
1A02:03
SubIndex 003
3. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x03 (Limit 1))
UINT32
RO
0x6010:03, 2
1A02:04
SubIndex 004
4. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x05 (Limit 2))
UINT32
RO
0x6010:05, 2
1A02:05
SubIndex 005
5. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x07 (Error))
UINT32
RO
0x6010:07, 1
1A02:06
SubIndex 006
UINT32
RO
0x0000:00, 1
1A02:07
SubIndex 007
UINT32
RO
0x0000:00, 6
1A02:08
SubIndex 008
UINT32
RO
0x1802:07, 1
1A02:09
SubIndex 009
9. PDO Mapping entry (object 0x1802 (AI TxPDO-Par Standard Ch.2), entry 0x07 (TxPDO State))
UINT32
RO
0x1802:09, 1
1A02:0A
SubIndex 010
10. PDO Mapping entry (object 0x1802 (AI TxPDO-Par Standard Ch.2), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6010:10, 1
1A02:0B
SubIndex 011
11. PDO Mapping entry (object 0x1802 (AI TxPDO-Par Standard Ch.2), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6010:11, 16
Index 1A03 AI TxPDO-Map Compact Ch.2
Index (hex)
Meaning
Data type
Flags
Default
1A03:0
PDO Mapping TxPDO 4
UINT8
RO
0x01 (1dec)
1A03:01
SubIndex 001
1. PDO Mapping entry (object 0x6010 (AI Inputs), entry 0x11 (Value))
UINT32
RO
0x6010:11, 16
Index 1A04 AI TxPDO-Map Standard Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1A04:0
PDO Mapping TxPDO 5
UINT8
RO
0x0B (11dec)
1A04:01
SubIndex 001
1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x01 (Underrange))
UINT32
RO
0x6020:01, 1
1A04:02
SubIndex 002
2. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x02 (Overrange))
UINT32
RO
0x6020:02, 1
1A04:03
SubIndex 003
3. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x03 (Limit 1))
UINT32
RO
0x6020:03, 2
1A04:04
SubIndex 004
4. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x05 (Limit 2))
UINT32
RO
0x6020:05, 2
1A04:05
SubIndex 005
5. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x07 (Error))
UINT32
RO
0x6020:07, 1
1A04:06
SubIndex 006
UINT32
RO
0x0000:00, 1
1A04:07
SubIndex 007
UINT32
RO
0x0000:00, 5
1A04:08
SubIndex 008
UINT32
RO
0x6020:0E, 1
1A04:09
SubIndex 009
9. PDO Mapping entry (object 0x1804 (AI TxPDO-Par Standard Ch.3), entry 0x07 (TxPDO State))
UINT32
RO
0x6020:0F, 1
1A04:0A
SubIndex 010
10. PDO Mapping entry (object 0x1804 (AI TxPDO-Par Standard Ch.3), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6020:10, 1
1A04:0B
SubIndex 011
11. PDO Mapping entry (object 0x1804 (AI TxPDO-Par Standard Ch.3), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6020:11, 16
Index 1A05 AI TxPDO-Map Compact Ch.3
Index (hex)
Meaning
Data type
Flags
Default
1A05:0
PDO Mapping TxPDO 6
UINT8
RO
0x01 (1dec)
1A05:01
SubIndex 001
1. PDO Mapping entry (object 0x6020 (AI Inputs), entry 0x11 (Value))
UINT32
RO
0x6020:11, 16
Index 1A06 AI TxPDO-Map Standard Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1A06:0
PDO Mapping TxPDO 7
UINT8
RO
0x0B (11dec)
1A06:01
SubIndex 001
1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x01 (Underrange))
UINT32
RO
0x6030:01, 1
1A06:02
SubIndex 002
2. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x02 (Overrange))
UINT32
RO
0x6030:02, 1
1A06:03
SubIndex 003
3. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x03 (Limit 1))
UINT32
RO
0x6030:03, 2
1A06:04
SubIndex 004
4. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x05 (Limit 2))
UINT32
RO
0x6030:05, 2
1A06:05
SubIndex 005
5. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x07 (Error))
UINT32
RO
0x6030:07, 1
1A06:06
SubIndex 006
UINT32
RO
0x0000:00, 1
1A06:07
SubIndex 007
UINT32
RO
0x0000:00, 5
1A06:08
SubIndex 008
UINT32
RO
0x6030:0E, 1
1A06:09
SubIndex 009
9. PDO Mapping entry (object 0x1806 (AI TxPDO-Par Standard Ch.4), entry 0x07 (TxPDO State))
UINT32
RO
0x6030:0F, 1
1A06:0A
SubIndex 010
10. PDO Mapping entry (object 0x1806 (AI TxPDO-Par Standard Ch.4), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6030:10, 1
1A06:0B
SubIndex 011
11. PDO Mapping entry (object 0x1806 (AI TxPDO-Par Standard Ch.4), entry 0x09 (TxPDO Toggle))
UINT32
RO
0x6030:11, 16
Index 1A07 AI TxPDO-Map Compact Ch.4
Index (hex)
Meaning
Data type
Flags
Default
1A07:0
PDO Mapping TxPDO 8
UINT8
RO
0x01 (1dec)
1A07:01
SubIndex 001
1. PDO Mapping entry (object 0x6030 (AI Inputs), entry 0x11 (Value))
UINT32
RO
0x6030:11, 16
Index 1C00 Sync manager type
Index (hex)
Meaning
Data type
Flags
Default
1C00:0
Sync manager type
Using the Sync Managers
UINT8
RO
0x04 (4dec)
1C00:01
SubIndex 001
Sync-Manager Type Channel 1: Mailbox Write
UINT8
RO
0x01 (1dec)
1C00:02
SubIndex 002
Sync-Manager Type Channel 2: Mailbox Read
UINT8
RO
0x02 (2dec)
1C00:03
SubIndex 003
Sync-Manager Type Channel 3: Process Data Write (Outputs)
UINT8
RO
0x03 (3dec)
1C00:04
SubIndex 004
Sync-Manager Type Channel 4: Process Data Read (Inputs)
UINT8
RO
0x04 (4dec)
Index 1C12 RxPDO assign (EP31x4-x002)
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x00 (0dec)
Index 1C12 RxPDO assign (EP3174-0092)
Index (hex)
Meaning
Data type
Flags
Default
1C12:0
RxPDO assign
PDO Assign Outputs
UINT8
RW
0x01 (1dec)
1C12:01
SubIndex 001
1. allocated RxPDO (contains the index of the associated RxPDO mapping object)
UINT16
RW
0x1610 (5648dec)
Index 1C13 TxPDO assign (EP31x4-x002)
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x05 (5dec)
1C13:01
Subindex 001
1. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A00 (6656dec)
1C13:02
Subindex 002
2. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A02 (6658dec)
1C13:03
Subindex 003
3. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A04 (6660dec)
1C13:04
Subindex 004
4. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A06 (6662dec)
Index 1C13 TxPDO assign (EP3174-0092)
Index (hex)
Meaning
Data type
Flags
Default
1C13:0
TxPDO assign
PDO Assign Inputs
UINT8
RW
0x04 (4dec)
1C13:01
Subindex 001
UINT16
RW
0x1A00 (6656dec)
1C13:02
Subindex 002
UINT16
RW
0x1A02 (6658dec)
1C13:03
Subindex 003
UINT16
RW
0x1A04 (6660dec)
1C13:04
Subindex 004
UINT16
RW
0x1A06 (6662dec)
1C13:05
Subindex 005
5. allocated TxPDO (contains the index of the associated TxPDO mapping object)
UINT16
RW
0x1A10 (6672dec)
Index 1C32 SM output parameter (EP3174-0092)
Index (hex)
Meaning
Data type
Flags
Default
1C32:0
SM output parameter
Synchronization parameters for the outputs
UINT8
RO
0x20 (32dec)
1C32:01
Sync mode
Current synchronization mode:
  • 0: Free Run
  • 1: Synchronous with SM 2 event
  • 2: DC - Synchron with SYNC0 Event
  • 3: DC - Synchron with SYNC1 Event
UINT16
RW
0x0001 (1dec)
1C32:02
Cycle time
Cycle time (in ns):
  • Free Run: Cycle time of the local timer
  • Synchron with SM 2 Event: Master cycle time
  • DC mode: SYNC0/SYNC1 Cycle Time
UINT32
RW
0x000F4240 (1000000dec)
1C32:03
Shift time
Time between SYNC0 event and output of the outputs (in ns, DC mode only)
UINT32
RO
0x000448E0 (280800dec)
1C32:04
Sync modes supported
Supported synchronization modes:
  • Bit 0 = 1: free run is supported
  • Bit 1 = 1: Synchron with SM 2 Event is supported
  • Bit 3:2 = 10: DC mode is supported
  • Bit 5:4 = 01: Output Shift with SYNC1 event (only DC mode)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C32:08)
UINT16
RO
0xC00B (49159dec)
1C32:05
Minimum cycle time
Minimum cycle time (in ns)
UINT32
RO
0x00041EB0 (270000dec)
1C32:06
Calc and copy time
Minimum time between SYNC0 and SYNC1 event (in ns, DC mode only)
UINT32
RO
0x000087F0 (34800dec)
1C32:07
Minimum delay time
UINT32
RO
0x0003C0F0 (246000dec)
1C32:08
Command
UINT16
RW
0x0000 (0dec)
1C32:09
Maximum Delay time
Time between SYNC1 event and output of the outputs (in ns, DC mode only)
UINT32
RO
1C32:0B
SM event missed counter
UINT16
RO
0x0000 (0dec)
1C32:0C
Cycle exceeded counter
Number of occasions the cycle time was exceeded in OPERATIONAL (cycle was not completed in time or the next cycle began too early)
UINT16
RO
0x0000 (0dec)
1C32:0D
Shift too short counter
Number of occasions that the interval between SYNC0 and SYNC1 event was too short (DC mode only)
UINT16
RO
0x0000 (0dec)
1C32:20
Sync error
The synchronization was not correct in the last cycle (outputs were output too late; DC mode only)
BOOLEAN
RO
0x00 (0dec)
Index 1C33 SM input parameter
Index (hex)
Meaning
Data type
Flags
Default
1C33:0
SM input parameter
Synchronization parameters for the inputs
UINT8
RO
0x20 (32dec)
1C33:01
Sync mode
  • 0: Free Run
  • 1: Synchron with SM 3 Event (no outputs available)
  • 34: Synchron with SM 2 Event (outputs available)
UINT16
RW
0x0022 (34dec)
1C33:02
Cycle time
UINT32
RW
1C33:03
Shift time
Time between SYNC0 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
EP31x4-x002:
0x00001388 (5000dec)
EP3174-0092:
0x0002FC10 (195600dec)
1C33:04
  • Bit 0: free run is supported
  • Bit 1: Synchron with SM 2 Event is supported (outputs available)
  • Bit 1: Synchron with SM 3 Event is supported (no outputs available)
  • Bit 2-3 = 01: DC mode is supported
  • Bit 4-5 = 01: Input Shift through local event (outputs available)
  • Bit 4-5 = 10: Input Shift with SYNC1 event (no outputs available)
  • Bit 14 = 1: dynamic times (measurement through writing of 0x1C33:08)
UINT16
RO
0xC00B (49163dec)
1C33:05
Minimum cycle time
UINT32
RO
EP31x4-x002:
0x0003D090 (250000dec)
EP3174-0092:
1C33:06
Calc and copy time
Time between reading of the inputs and availability of the inputs for the master (in ns, only DC mode)
UINT32
RO
EP31x4-x002:
0x00002710 (10000dec)
EP3174-0092:
0x00000708 (1800dec)
1C33:07
Minimum delay time
UINT32
RO
EP31x4-x002:
EP3174-0092:
1C33:08
Command
UINT16
RW
0x0000 (0dec)
1C33:09
Maximum Delay time
Time between SYNC1 event and reading of the inputs (in ns, only DC mode)
UINT32
RO
EP31x4-x002:
EP3174-0092:
1C33:0B
UINT16
RO
0x0000 (0dec)
1C33:0C
UINT16
RO
0x0000 (0dec)
1C33:0D
UINT16
RO
0x0000 (0dec)
1C33:20
Sync error
BOOLEAN
RO
0x00 (0dec)
Profile-specific objects (0x6000-0xFFFF)
The profile-specific objects have the same meaning for all EtherCAT slaves that support the profile 5001.
Index 6000 AI Inputs
Index (hex)
Meaning
Data type
Flags
Default
6000:0
AI inputs
Maximum subindex
UINT8
RO
0x11 (17dec)
6000:01
Underrange
Is set if the value falls below the operating range of the sensor or the process data contains the lowest possible value.
BOOLEAN
RO
0x00 (0dec)
6000:02
Overrange
Is set if the value exceeds the operating range of the sensor or the process data contains the highest possible value.
BOOLEAN
RO
0x00 (0dec)
6000:03
Limit 1
Only when limit check is active
BIT2
RO
0x00 (0dec)
1
Value below set limit
2
Set limit exceeded
3
Set limit reached
6000:05
Limit 2
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6000:07
Error
The error bit is set if the process data is invalid (wire breakage, overrange, underrange).
BOOLEAN
RO
0x00 (0dec)
6000:0E
Sync error
BOOLEAN
RO
0x00 (0dec)
6000:0F
TxPDO State
Validity of the data of the associated TxPDO
BOOLEAN
RO
0x00 (0dec)
0
valid
1
invalid
6000:10
TxPDO Toggle
TxPDO toggle is toggled by the slave when the data of the associated TxPDO is updated.
BOOLEAN
RO
0x00 (0dec)
6000:11
Value
Analog input date
INT16
RO
0x0000 (0dec)
Index 6010 AI Inputs
Index (hex)
Meaning
Data type
Flags
Default
6010:0
AI inputs
Maximum subindex
UINT8
RO
0x11 (17dec)
6010:01
Underrange
BOOLEAN
RO
0x00 (0dec)
6010:02
Overrange
BOOLEAN
RO
0x00 (0dec)
6010:03
Limit 1
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6010:05
Limit 2
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6010:07
Error
BOOLEAN
RO
0x00 (0dec)
6010:0E
Sync error
BOOLEAN
RO
0x00 (0dec)
6010:0F
TxPDO State
BOOLEAN
RO
0x00 (0dec)
0
valid
1
invalid
6010:10
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
6010:11
Value
Analog input date
INT16
RO
0x0000 (0dec)
Index 6020 AI Inputs
Index (hex)
Meaning
Data type
Flags
Default
6020:0
AI inputs
Maximum subindex
UINT8
RO
0x11 (17dec)
6020:01
Underrange
BOOLEAN
RO
0x00 (0dec)
6020:02
Overrange
BOOLEAN
RO
0x00 (0dec)
6020:03
Limit 1
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6020:05
Limit 2
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6020:07
Error
BOOLEAN
RO
0x00 (0dec)
6020:0E
Sync error
BOOLEAN
RO
0x00 (0dec)
6020:0F
TxPDO State
BOOLEAN
RO
0x00 (0dec)
0
valid
1
invalid
6020:10
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
6020:11
Value
Analog input date
INT16
RO
0x0000 (0dec)
Index 6030 AI Inputs
Index (hex)
Meaning
Data type
Flags
Default
6030:0
AI inputs
Maximum subindex
UINT8
RO
0x11 (17dec)
6030:01
Underrange
BOOLEAN
RO
0x00 (0dec)
6030:02
Overrange
BOOLEAN
RO
0x00 (0dec)
6030:03
Limit 1
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6030:05
Limit 2
BIT2
RO
0x00 (0dec)
1
2
Set limit exceeded
3
Set limit reached
6030:07
Error
BOOLEAN
RO
0x00 (0dec)
6030:0E
Sync error
BOOLEAN
RO
0x00 (0dec)
6030:0F
TxPDO State
BOOLEAN
RO
0x00 (0dec)
0
valid
1
invalid
6030:10
TxPDO Toggle
BOOLEAN
RO
0x00 (0dec)
6030:11
Value
Analog input date
INT16
RO
0x0000 (0dec)
Index 800E AI Internal data
Index (hex)
Meaning
Data type
Flags
Default
800E:0
AI internal data
Maximum subindex
UINT8
RO
0x01 (1dec)
800E:01
ADC raw value
Raw value of the analog/digital converter
INT16
RO
0x0000 (0dec)
Index 800F AI Vendor data
Index (hex)
Meaning
Data type
Flags
Default
800F:0
AI vendor data
Maximum subindex
UINT8
RO
0x06 (6dec)
800F:01
R0 Offset
Offset (vendor calibration)
INT16
RW
0x0000 (0dec)
800F:02
R0 Gain
Gain (vendor calibration)
INT16
RW
0x4000 (16384dec)
800F:03
R1 Offset
INT16
RW
0x0000 (0dec)
800F:04
R1 Gain
INT16
RW
0x4000 (16384dec)
800F:05
R2 Offset
INT16
RW
0x0000 (0dec)
800F:06
R2 Gain
INT16
RW
0x4000 (16384dec)
Index 801E AI Internal data
Index (hex)
Meaning
Data type
Flags
Default
801E:0
AI internal data
Maximum subindex
UINT8
RO
0x01 (1dec)
801E:01
ADC raw value
INT16
RO
0x0000 (0dec)
Index 801F AI Vendor data
Index (hex)
Meaning
Data type
Flags
Default
801F:0
AI vendor data
Maximum subindex
UINT8
RO
0x06 (6dec)
801F:01
R0 Offset
INT16
RW
0x0000 (0dec)
801F:02
R0 Gain
INT16
RW
0x4000 (16384dec)
801F:03
R1 Offset
INT16
RW
0x0000 (0dec)
801F:04
R1 Gain
INT16
RW
0x4000 (16384dec)
801F:05
R2 Offset
INT16
RW
0x0000 (0dec)
801F:06
R2 Gain
INT16
RW
0x4000 (16384dec)
Index 802E AI Internal data
Index (hex)
Meaning
Data type
Flags
Default
802E:0
AI internal data
Maximum subindex
UINT8
RO
0x01 (1dec)
802E:01
ADC raw value
INT16
RO
0x0000 (0dec)
Index 802F AI Vendor data
Index (hex)
Meaning
Data type
Flags
Default
802F:0
AI vendor data
Maximum subindex
UINT8
RO
0x06 (6dec)
802F:01
R0 Offset
INT16
RW
0x0000 (0dec)
802F:02
R0 Gain
INT16
RW
0x4000 (16384dec)
802F:03
R1 Offset
INT16
RW
0x0000 (0dec)
802F:04
R1 Gain
INT16
RW
0x4000 (16384dec)
802F:05
R2 Offset
INT16
RW
0x0000 (0dec)
802F:06
R2 Gain
INT16
RW
0x4000 (16384dec)
Index 803E AI Internal data
Index (hex)
Meaning
Data type
Flags
Default
803E:0
AI internal data
Maximum subindex
UINT8
RO
0x01 (1dec)
803E:01
ADC raw value
INT16
RO
0x0000 (0dec)
Index 803F AI Vendor data
Index (hex)
Meaning
Data type
Flags
Default
803F:0
AI vendor data
Maximum subindex
UINT8
RO
0x06 (6dec)
803F:01
R0 Offset
INT16
RW
0x0000 (0dec)
803F:02
R0 Gain
INT16
RW
0x4000 (16384dec)
803F:03
R1 Offset
INT16
RW
0x0000 (0dec)
803F:04
R1 Gain
INT16
RW
0x4000 (16384dec)
803F:05
R2 Offset
INT16
RW
0x0000 (0dec)
803F:06
R2 Gain
INT16
RW
0x4000 (16384dec)
Index (hex)
Meaning
Data type
Flags
Default
F000:0
General information for the modular device profile
UINT8
RO
0x02 (2dec)
F000:01
Module index distance
Index distance of the objects of the individual channels
UINT16
RO
0x0010 (16dec)
F000:02
Maximum number of modules
Number of channels
UINT16
RO
EP31x4-x002:
0x0004 (4dec)
EP3174-092:
0x0005 (5dec)
Index F008 Code word
Index (hex)
Meaning
Data type
Flags
Default
F008:0
Code word
reserved
UINT32
RW
0x00000000 (0dec)
Index F010 Module list
Index (hex)
Meaning
Data type
Flags
Default
F010:0
Module list
Maximum subindex
UINT8
RW
0x05 (5dec)
F010:01
SubIndex 001
UINT32
RW
0x0000012C (300dec)
F010:02
SubIndex 002
UINT32
RW
0x0000012C (300dec)
F010:03
SubIndex 003
UINT32
RW
0x0000012C (300dec)
F010:04
SubIndex 004
UINT32
RW
0x0000012C (300dec)
F010:05*
SubIndex 005
UINT32
RW
0x000003B6 (950dec)
*) EP3174-0092 only