Technical data - EP1809-0042
All values are typical values over the entire temperature range, unless stated otherwise.
EtherCAT
Connection
2 x M12 socket, 4-pin, D-coded, shielded
Electrical isolation
500 V
Supply voltages
Connection
Input: 7/8" plug, 5-pin, 16-UN thread
Downstream connection: 7/8" socket, 5-pin, 16-UN thread
US nominal voltage
24 VDC (-15 % / +20 %)
US sum current
max. 16 A at 40 °C
Current consumption from US
130 mA + sensor supply
Rated voltage UP
UP sum current
max. 16 A at 40 °C
Current consumption from UP
None. UP is only forwarded.
Electrical isolation GNDS / GNDP
yes
Digital inputs
Number
16
Connection
8 x M12 socket, 5-pin, A-coded
Cable length
max. 30 m
Nominal input voltage
24 VDC (-15 %/+20 %)
Input filter
3 ms
Signal voltage "0"
-3 … +5 V (similar to EN 61131-2, type 3)
Signal voltage "1"
+11 … +30 V (similar to EN 61131-2, type 3)
Input current
6 mA (similar to EN 61131-2, type 3)
Supply of the module electronics
from the control voltage US
Current consumption of the module electronics
130 mA
Sensor power supply
24 VDC from US
max. 0.5 A in total, short-circuit proof
Housing data
Dimensions W x H x D
60 mm x 150 mm x 26,5 mm (without connectors)
Weight
approx. 440 g
Installation position
variable
Material
PA6 (polyamide)
Environmental conditions
Ambient temperature during operation
-25 … +60 °C
Ambient temperature during storage
-40 … +85 °C
Vibration / shock resistance
conforms to EN 60068-2-6 / EN 60068-2-27
EMC immunity / emission
conforms to EN 61000-6-2 / EN 61000-6-4
Protection class
IP65, IP66, IP67 conforms to EN 60529
Approvals / markings
Approvals / markings *)
CE, UL under preparation
Additional tests
The devices have undergone the following additional tests:
Test
Explanation
Vibration
10 frequency sweeps in 3 axes
5 Hz < f < 60 Hz displacement 0.35 mm, constant amplitude
60.1 Hz < f < 500 Hz acceleration 5 g, constant amplitude
Shocks
1000 shocks in each direction, in 3 axes
35 g, 11 ms