Configuration data
Index 8000 FB settings
Index (hex)
Meaning
Data type
Flags
Default
8000:0
FB Settings
Observer settings
UINT8
RO
0x16 (22dec)
8000:11
Device type
Description of the available feedback profiles (incremental encoder and Hall sensor)
UINT32
RW
0x00000605 (1541dec)
8000:14
Observer bandwidth
Bandwidth of the velocity observer
Unit: [Hz]
Typical value range: 200 ... 500 Hz
UINT16
RW
0x00C8 (200dec)
8000:15
Observer feed-forward
Load ratio
Unit: [%]
100% = load-free
50% = mass moments of inertia of input and output are equal
Pre-control for velocity measurement.
UINT8
RW
0x00 (0dec)
8000:16
Sub-increment bits
Bitwise shift to left from target and actual position and following error
UINT8
RW
0x00 (0dec)
Index 8001 FB Touch probe Settings
Index (hex)
Meaning
Data type
Flags
Default
8001:0
Maximum subindex
UINT8
RO
0x12 (18dec)
8001:11
Touch probe 1 source
Position value digital input 1:
1: Touch probe input 1
5: Hardware zero impluse
INT16
RW
0x0001 (1dec)
8001:12
Touch probe 2 source
Position value digital input 2:
2: Touch probe input 2
INT16
RW
0x0002 (2dec)
Index 8008 FB Settings ENC
Index (hex)
Meaning
Data type
Flags
Default
8008:0
FB Settings ENC
Maximum subindex
UINT8
RO
0x13 (19dec)
8008:01
Invert feedback direction
Inversion of the encoder counting direction. Adjusted by the Scan Feedback feature.
BOOLEAN
RW
0x00 (0dec)
8008:02
Enable power supply
Enabling the encoder supply voltage
BOOLEAN
RW
0x00 (0dec)
8008:05
Enable ENC C input
Enabling the C-input of the module for the evaluation of the C-track at the incremental encoder
BOOLEAN
RW
0x01 (1dec)
8008:11
Supply voltage output
Voltage level of encoder supply
Unit: [mV]
Typical value range: 2 ... 24 V
UINT32
RW
0x00001388 (5000dec)
8008:12
Encoder type
Encoder type selection:
0: disabled
1: RS422 differential
2: TTL single ended
3: HTL differential
4: HTL single ended (default)
5: RS422 differential - high impedance input
6: TTL single ended - input filters disabled
7: open collector
UINT16
RW
0x0004 (4dec)
8008:13
Encoder Increments per Revolution
Resolution of the encoder after 4-fold evaluation
UINT32
RW
0x00001000 (4096dec)
Index 800A FB Settings Hall
Index (hex)
Meaning
Data type
Flags
Default
800A:0
FB Settings Hall
Maximum subindex
UINT8
RO
0x14 (20dec)
800A:02
Enable power supply
Activates voltage supply for the Hall sensor
BOOLEAN
RW
0x00 (0dec)
800A:05
Enable extrapolation
Extrapolation of the measured values of the Hall sensor.
This does not improve the physical resolution.
BOOLEAN
RW
0x00 (0dec)
800A:11
Voltage level of the supply voltage for the Hall sensor,
Unit: [mV]
Typical value range: 2 … 4 V
UINT32
RW
800A:12
Phasing
Arrangement of the Hall sensors. Determined by the Scan Feedback function.
See chapter Scan Feedback.
0: A-B: 60° / B-C. 60
1: A-B: 120° / B-C. 120° (default)
2: A-B: 240° / B-C. 240
3: A-B: 300° / B-C. 300
4: A-B: 60° / B-C. 240
5: A-B: 120° / B-C. 300
6: A-B: 240° / B-C. 60
7: A-B: 300° / B-C. 120
UINT8
RW
0x01 (1dec)
800A:13
Hall commutation adjust
Commutation offset of the Hall sensors in 60° increments. Determined by the Scan Feedback function.
0: 0° (default)
1: 60°
2: 120°
3: 180°
4: 240°
5: 300°
UINT8
RW
0x00 (0dec)
800A:14
Hall sensor type
Enable or disable the Open Collector Hall sensor inputs
0: disabled
1: open collector (default)
UINT8
RW
0x01 (1dec)
Index 8010 DRV Amplifier Settings
Index (hex)
Meaning
Data type
Flags
Default
8010:0
Amplifier settings
UINT8
RO
0x64 (100dec)
8010:01
Enable TxPDOToggle
Activate or deactivate the TxPDO toggle in bit 10 of the status word
BOOLEAN
RW
0x00 (0dec)
8010:02
Enable input cycle counter
1: enabled
Two-bit counter that is incremented with each process data cycle up to a maximum value of 3, after which it starts again at 0
The low bit is represented in bit 10 and the high bit in bit 14 of the Status word.
BOOLEAN
RW
0x00 (0dec)
8010:04
Repeat find commutation
Repeat the commutation angle determination. (Effective for all FOC operation modes)
BOOLEAN
RW
0x01 (1dec)
8010:05
Enable cogging torque compensation
Enable or disable the cogging torque compensation (for FOC operation modes only).
BOOLEAN
RW
0x00 (0dec)
8010:12
Current loop integral time
Integral component of current controller
Unit: 0.1 ms
UINT16
RW
0x000A (10dec)
8010:13
Current loop proportional gain
Proportional component of current controller
Unit: 0.1 V/A
UINT16
RW
0x000A (10dec)
8010:14
Velocity loop integral time (current mode)
Integral component of velocity controller
Unit: 0.1 ms
(For feedback systems with field-oriented control (FOC). See chapter Configuration of the feedback system)
UINT32
RW
0x00000032 (50dec)
8010:15
Velocity loop proportional gain (current mode)
Proportional component of velocity controller
Unit: µA / (°/s)
UINT32
RW
0x00000014 (20dec)
8010:17
Position loop proportional gain
Proportional component of position controller
Unit: (°/s) / °
UINT32
RW
0x0000000A (10dec)
8010:19
Nominal DC link voltage
Injected DC link voltage
Unit: mV
UINT32
RW
0x0000BB80 (48000dec)
8010:1A
Min DC link voltage
Minimum DC link voltage
Unit: mV
UINT32
RW
0x00001A90 (6800dec)
8010:1B
Max DC link voltage
Maximum DC link voltage
Unit: mV
UINT32
RW
0x0000EA60 (60000dec)
8010:29
Amplifier I2T warn level
I²T model warning threshold
Unit: %
UINT8
RW
0x50 (80dec)
8010:2A
Amplifier I2T error level
I²T model error threshold
Unit: %
UINT8
RW
0x69 (105dec)
8010:2B
Amplifier Temperature warn level
Warning threshold for overtemperature of the module
Unit: 0.1 °C
UINT16
RW
0x0320 (800dec)
8010:2C
Amplifier Temperature error level
Error threshold for overtemperature of the module
Unit: 0.1 °C
UINT16
RW
0x03E8 (1000dec)
8010:31
Velocity limitation
Limitation of the velocity setpoint setting
Unit: 1/min
UINT32
RW
0x000186A0 (100000dec)
8010:33
Stand still window
Standstill window
Unit: 1/min
Velocity range for which the axis is considered to be at a standstill.
UINT16
RW
0x0000 (0dec)
Index (hex)
Meaning
Data type
Flags
Default
8010:39
Select info data 1
Selection "Info data 1"
Optional display of additional information in the cyclic process data.
Permitted values:
UINT8
RW
0x02 (2dec)
2
DC link voltage (mV) (default)
4
PCB temperature - module temperature (0.1 °C)
7
I2T Motor
Unit: [%]
8
I2T Amplifier
Unit: [%]
10
Digital inputs
Bit0: Digital Input 1 Level
Bit1: Digital Input 2 Level
Bit2: unused
Bit3: unused
Bit4: Encoder A
Bit5: Encoder B
Bit6: Encoder C
Bit7: unused
Bit8: Hall Sensor U
Bit9: Hall Sensor V
Bit10: Hall Sensor W
Bit 11: unused
Bit12: Hardware Enable Input Level (required for STO functionality)
12
Phase Voltage U
Unit: [mV]
13
Phase Voltage V
Unit: [mV]
14
Phase Voltage W
Unit: [mV]
8010:3A
Select info data 2
Selection "Info data 2"
UINT8
RW
0x04 (4dec)
2
4
7
I2T Motor
Unit: [%]
8
I2T Amplifier
Unit: [%]
10
Digital inputs
Bit2: unused
Bit3: unused
Bit4: Encoder A
Bit5: Encoder B
Bit6: Encoder C
Bit7: unused
Bit8: Hall Sensor U
Bit9: Hall Sensor V
Bit 11: unused
12
Phase Voltage U
Unit: [mV]
13
Phase Voltage V
Unit: [mV]
14
Phase Voltage W
Unit: [mV]
Index (hex)
Meaning
Data type
Flags
Default
8010:50
Following error window
Following error monitoring: following error window
Unit: reference to increments of the raw position data. Can be scaled in the PLC if necessary.
0xFFFFFFFF (-1dec) =
following error monitoring OFF
Any other value =
following error monitoring ON
Unit: [inc]
Applies in conjunction with index 0x8010:51 "Following error time out."
UINT32
RW
0xFFFFFFFF (-1dec)
8010:51
Following error monitoring: timeout
Unit: ms
If the following error is larger than the following error window for a time that exceeds the timeout, this leads to an error reaction.
UINT16
RW
0x0000 (0dec)
8010:54
Feature bits
Reserved
UINT32
RW
0x00000000 (0dec)
8010:57
Position loop Velocity feed forward gain
Velocity pre-control of the position controller
Unit:
UINT8
RW
0x64 (100dec)
8010:58
Select info data 3
Selection "Info data 3"
Permitted values:
UINT8
RW
0x07 (7dec)
2
4
7
I2T Motor
Unit: [%]
8
I2T Amplifier
Unit: [%]
10
Digital inputs
Bit2: unused
Bit3: unused
Bit4: Encoder A
Bit5: Encoder B
Bit6: Encoder C
Bit7: unused
Bit8: Hall Sensor U
Bit9: Hall Sensor V
Bit 11: unused
12
Phase Voltage U
Unit: [mV]
13
Phase Voltage V
Unit: [mV]
14
Phase Voltage W
Unit: [mV]
8010:59
Error suppression mask
Bit 0: suppresses detection of a wire break of the motor phases
Bit 1: suppresses commutation angle monitoring
UINT32
RW
0x00000000 (0dec)
8010:5A
Velocitiy loop integral time (voltage mode)
Unit: 0.1 ms
(For feedback systems with six-step. See controller optimization Sensorless operation and Operation with Hall sensors only)
UINT32
RW
0x000001F4 (500dec)
8010:5B
Velocity loop proportional gain (voltage mode)
Unit: µV / (°/s)
UINT32
RW
0x00000064 (100dec)
8010:5C
Velocity loop voltage feed forward gain (voltage mode)
Velocity pre-control of the velocity controller
Unit: %
UINT8
RW
0x32 (50dec)
8010:5E
Sensorless offset voltage scaling
Configures the voltage output at standstill
Unit: %
UINT16
RW
0x0032 (50dec)
8010:5F
Sensorless observer bandwidth
Bandwidth of the position/velocity observer in sensorless operation
Unit:Hz
UINT16
RW
0x0064 (100dec)
8010:60
Sensorless max. acceleration
Max. acceleration
Unit:° / s2
UINT32
RW
0x0000186A0 (100000dec)
8010:61
Cogging torque compensation
Contains the coefficients of the cogging torque compensation. These are determined by the Cogging Scan function. See chapter Scan Motor Cogging
OCTET-STRING[16]
RW
{0}
8010:62
Position loop deadband window
Deadband window of the position controller [Inc]
For position deviations smaller than the defined range, the following applies (provided the target velocity is within the "Stand still window" (see parameter: 0x8010:33)):
0 - 75% position controller switched off
75 - 100% linear transition of the position controller gain
UINT32
RW
0x00000000 (0dec)
8010:63
Find commutation time
Defines the time for determining the commutation angle [0.1 s]
This process is divided into two phases. In total, it takes twice the time specified here. Required time depends on application
UINT16
RW
0x0009 (9dec)
8010:64
Commutation type
Method for determining the commutation angle:
1: FOC with incremental encoder (default)
2: Six Step with hall
3: Six Step sensorless
4: FOC with incremental encoder and hall
UINT8
RW
0x01 (1dec)
Index 8011 DRV Motor Settings
Index (hex)
Meaning
Data type
Flags
Default
8011:0
DRV Motor Settings
Maximum subindex
UINT8
RO
0x31 (49dec)
8011:11
Max current
Peak current
Unit: mA
Limitation by maximum output current of the EJ7411 module.
The motor current values are to be specified as peak value.
UINT32
RW
0x00001770 (6000dec)
8011:12
Rated current
Nominal current of the motor
Unit: mA
Corresponds to the maximum continuous motor output current.
"Target Torque", "Torque actual value" and "Torque limitation" are scaled relative to the "rated current" in per mill
UINT32
RW
0x000003E8 (1000dec)
8011:13
Motor pole pairs
Number of pole pairs
UINT8
RW
0x01 (1dec)
8011:16
Torque constant
Torque constant
Unit: mNm / A
UINT32
RW
0x00000032 (50dec)
8011:18
Rotor moment of inertia
Moment of inertia of the motor including mechanics
Unit: g cm2
UINT32
RW
0x00000064 (100dec)
8011:19
Winding inductance
Winding inductance
Unit: 0.01 mH
UINT16
RW
0x0064 (100dec)
8011:1B
Motor speed limitation
Unit: 1/min
UINT32
RW
Index (hex)
Meaning
Data type
Flags
Default
8011:29
I2T warn level
I2T motor warning threshold
Unit: %
UINT8
RW
0x50 (80dec)
8011:2A
I2T error level
I2T motor error threshold
Unit: %
UINT8
RW
0x69 (105dec)
8011:2D
Motor thermal time constant
Motor thermal time constant of the winding
Unit: 0.1 s
UINT16
RW
0x0028 (40dec)
8011:2E
Rated speed
Nominal speed
Unit: 1 /min
UINT32
RW
8011:2F
Rated voltage
Nominal voltage of the motor
Unit: mV
UINT32
RW
0x0000B880 (48000dec)
8011:30
Winding resistance
Winding resistance phase - phase
Unit: mOhm
UINT32
RW
8011:31
Voltage constant
Voltage constant
Unit: µV / (1 / min)
Specifies the voltage induced by the motor as a generator (counter-electromotive force).
UINT32
RW
Index 8012 DRV brake settings
Index (hex)
Meaning
Data type
Flags
Default
8012:0
DRV brake settings
Maximum subindex
UINT8
RO
0x14 (20dec)
8012:01
Manual override (release)
Manual release of the motor holding brake
Intended for commissioning purposes.
BOOLEAN
RW
0x00 (0dec)
8012:11
Release delay
Time that the holding brake requires to open (release) after power was applied.
Unit: ms
UINT16
RW
0x0000 (0dec)
8012:12
Application delay
Time that the holding brake requires to close (hold) after the power was switched off.
Unit: ms
UINT16
RW
0x0000 (0dec)
8012:13
Emergency application timeout
Time that the amplifier waits until the speed reaches the standstill window after a stop request.
If the set waiting time is exceeded, the holding brake is triggered independently of the speed.
Unit: ms
  • Note:
    This parameter must be adjusted to at least the longest time of "coasting" of the axis.
  • In the case of suspended axes, this parameter should be set to a very short time in order to prevent the axis/load from sagging.
UINT16
RW
0x0000 (0dec)
8012:14
Brake moment of inertia
Motor brake moment of inertia
Unit: g cm2
UINT16
RW
0x0000 (0dec)
The following note refers to the DMC objects 0x6040, 0x7040, 0x8040 and 0x8041.
Configuration data 1:
INT64 data type for all positions in the drive motion control
The data type INT64 is used for all positions in the drive motion control.
  • The single-turn position is located in the lower 32 bits.
  • The multi-turn position is located in the upper 32 bits.
Index 8040 DMC Settings
Index (hex)
Meaning
Data type
Flags
Default
8040:0
DMC Settings
Settings for Drive Motion Control.
UINT8
RW
0x17 (23dec)
8040:07
Emergency deceleration
Deceleration for the emergency stop ramp.
Indication in milliseconds from nominal motor speed to standstill.
UINT16
RW
0x64 (100dec)
8040:08
Calibration position
If homing is successful, the "Actual position" is set to this value.
Observe the note on the data type!
UINT64
RW
0x00 (0dec)
8040:09
Calibration velocity (towards plc cam)
Speed for driving on the referencing cams.
Is specified in 10,000ths of 0x8011:1B "Motor speed limitation".
UINT16
RW
0x64 (100dec)
8040:0A
Calibration velocity (off plc cam)
Speed to drive down from the referencing cam.
UINT16
RW
0x0A (10dec)
8040:0E
Modulo factor
Modulo factor for modulo travel commands.
The default value of 2^32 corresponds to a single-turn revolution and thus e.g. 360°.
UINT64
RW
0x100000000 (4294967296dec)
8040:12
Block calibration torque limit
Torque limitation for block calibration.
The value is specified in 1000ths of 0x8011:12 "Rated current".
UINT16
RW
0x64 (100dec)
8040:13
Block calibration stop distance
Specifies the distance by which to move out of the block after calibration.
UINT64
RW
8040:14
Block calibration lag threshold
Maximum permissible following error during block calibration.
UINT64
RW
8040:15
Target position window
General position target window for travel commands for reaching the InTarget state.
The "Target position window" is valid in connection with 0x8040:16 "Target position monitor time".
UINT64
RW
0x16C16C1 (23860929dec)
8040:16
The actual position must be within the position target window 0x8040:15 for the specified time to reach the InTarget state.
Unit: ms.
UINT16
RW
0x14 (20dec)
8040:17
Target position timeout
Specifies the time for the timer to start when the setpoint generator reaches the target position.
If the InTarget condition (see 0x8040:15 and 0x8040:16) is not reached within this time,
  • the travel command is aborted.
  • The function block for the travel command returns an error.
Unit: ms.
UINT16
RW
0x1770 (6000dec)
Index 8041 DMC Features
Index (hex)
Meaning
Data type
Flags
Default
8041:0
DMC Features
Drive Motion Control functions
UINT8
RW
0x1B (27dec)
8041:13
Invert calibration cam search direction
For the default homing sequence the direction for referencing cam search can be inverted.
  • FALSE:
    the cam is looked for in the direction of positive movement.
  • TRUE:
    the cam is looked for in the direction of negative movement.
BOOLEAN
RW
0x00 (0dec)
8041:14
Invert sync impulse search direction
For the default homing sequence the direction for sync pulse search can be inverted.
  • FALSE:
    sync pulse is looked for in the direction of positive movement.
  • TRUE:
    sync pulse is looked for in the direction of negative movement.
BOOLEAN
RW
0x01 (1dec)
8041:19
Calibration cam source
Signal source of the referencing cam:
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)
8041:1A
Calibration cam active level
Signal level of the referencing cam that is evaluated as "active".
UINT8
RW
0x00 (0dec)
8041:1B
Latch source
Signal source of the latch signal:
  • 0: Input 1
  • 1: Input 2
UINT8
RW
0x00 (0dec)