Cofiguration data
Index 8000 ENC Settings Ch.1
8000:0 | ENC Settings Ch.1 | Max. Subindex | UINT8 | RO | 0x0E (14dec) |
8000:08 | Disable filter | 0: Activates the input filter (inputs A, /A, B, /B, C, /C only) 1: Deactivates the input filter | BOOLEAN | RW | 0x00 (0dec) |
8000:0A | Enable micro increments | If activated, the terminal interpolates micro-increments between the integral encoder increments in DC mode. The lower 8 bits of the counter value are used in each case for the display. A 32-bit counter thus becomes a 24+8-bit counter, a 16-bit counter becomes a 8+8-bit counter. | BOOLEAN | RW | 0x00 (0dec) |
8000:0E | Reversion of rotation | Activates reversion of rotation | BOOLEAN | RW | 0x00 (0dec) |
Index 8010 ENC Settings Ch.2
8010:0 | ENC Settings Ch.2 | Max. Subindex | UINT8 | RO | 0x0E (14dec) |
8010:08 | Disable filter | 0: Activates the input filter (inputs A, /A, B, /B, C, /C only) 1: Deactivates the input filter | BOOLEAN | RW | 0x00 (0dec) |
8010:0A | Enable micro increments | If activated, the terminal interpolates micro-increments between the integral encoder increments in DC mode. The lower 8 bits of the counter value are used in each case for the display. A 32-bit counter thus becomes a 24+8-bit counter, a 16-bit counter becomes a 8+8-bit counter. | BOOLEAN | RW | 0x00 (0dec) |
8010:0E | Reversion of rotation | Activates reversion of rotation | BOOLEAN | RW | 0x00 (0dec) |
Index 8020 DCM Motor Settings Ch.1
8020:0 | DCM Motor Settings Ch.1 | Max. Subindex | UINT8 | RO | 0x0F (15dec) |
8020:01 | Maximal current | Maximum permanent motor coil current Unit: 1 mA | UINT16 | RW | 0x1388 (5000dec) |
8020:02 | Nominal current | Motor nominal current Unit: 1 mA | UINT16 | RW | 0x0DAC (3500dec) |
8020:03 | Nominal voltage | Nominal voltage (supply voltage) of the motor Unit:1 mV | UINT16 | RW | 0xC350 (50000dec) |
8020:04 | Motor coil resistance | Internal resistance of the motor Unit: 0.01 ohm | UINT16 | RW | 0x0064 (100dec) |
8020:05 | Reduced current (positive) | Reduced torque in positive direction of rotation Unit: 1 mA | UINT16 | RW | 0x07D0 (2000dec) |
8020:06 | Reduced current (negative) | Reduced torque in negative direction of rotation Unit: 1 mA | UINT16 | RW | 0x07D0 (2000dec) |
8020:07 | Encoder increments (4-fold) | Number of encoder increments per revolution with quadruple evaluation | UINT16 | RW | 0x0000 (0dec) |
8020:08 | Maximal motor velocity | Nominal speed of the motor at the nominal voltage Unit: 1 rpm | UINT16 | RW | 0x0000 (0dec) |
8020:0C | Time for switch-off at overload | Time for switch-off at overload Unit: 1 ms | UINT16 | RW | 0x00C8 (200dec) |
8020:0D | Time for current lowering at overload | Time for current lowering at overload (from max. current to nominal current) Unit: 1 ms | UINT16 | RW | 0x07D0 (2000dec) |
8020:0E | Torque auto-reduction threshold (positive) | Process data threshold for automatic torque reduction in the positive direction of rotation Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
8020:0F | Torque auto-reduction threshold (negative) | Process data threshold for automatic torque reduction in the negative direction of rotation Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
Index 8021 DCM Controller Settings Ch.1
8021:0 | DCM Controller Settings Ch.1 | Max. Subindex | UINT8 | RO | 0x12 (18dec) |
8021:01 | Kp factor (curr.) | Kp control factor of the current controller | UINT16 | RW | 0x00C8 (200dec) |
8021:02 | Ki factor (curr.) | Ki control factor of the current controller | UINT16 | RW | 0x0002 (2dec) |
8021:03 | Inner window (curr.) | Inner window for the I component Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
8021:05 | Outer window (curr.) | Outer window for the I component Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
8021:06 | Filter cut off frequency (curr.) | Limit frequency of the current controller Unit: 1 Hz | UINT16 | RW | 0x0000 (0dec) |
8021:11 | Voltage adjustment enable | Activates the compensation of voltage fluctuations (only in the operating mode "Direct velocity") | BOOLEAN | RW | 0x00 (0dec) |
8021:12 | Current adjustment enable | Activates the R x I compensation | BOOLEAN | RW | 0x00 (0dec) |
Index 8022 DCM Features Ch.1
8022:0 | DCM Features Ch.1 | Max. Subindex | UINT8 | RO | 0x36 (54dec) |
8022:01 | Operation mode | Operation mode 0: Automatic ...: reserved 15: Chopper resistor | BIT4 | RW | 0x00 (0dec) |
8022:09 | Invert motor polarity | Inverts the direction of rotation of the motor | BOOLEAN | RW | 0x00 (0dec) |
8022:0A | Torque error enable | Activates the automatic overload cut-off (see also subindex 0x8020:0C) | BOOLEAN | RW | 0x00 (0dec) |
8022:0B | Torque auto reduce | Activates the automatic torque reduction (see also subindex 0x8020:0D – 0x8020:0F) | BOOLEAN | RW | 0x00 (0dec) |
8022:11 | Select info data 1 | Selection "Info data 1" 0: Status word ....: reserved 7: Motor velocity ...: reserved 101: Internal temperature ...: reserved 103: Control voltage ...: reserved 150: Status word (drive controller) ...: reserved | UINT8 | RW | 0x01 (1dec) |
8022:19 | Select info data 2 | Selection "Info data 2" see subindex 0x8022:11 | UINT8 | RW | 0x02 (2dec) |
8022:30 | Invert digital input 1 | Inversion of digital input 1 | BOOLEAN | RW | 0x00 (0dec) |
8022:31 | Invert digital input 2 | Inversion of digital input 2 | BOOLEAN | RW | 0x00 (0dec) |
8022:32 | Function for input 1 | Function of digital input 1 0: Normal input …: reserved | BIT4 | RW | 0x00 (0dec) |
8022:36 | Function for input 2 | Function of digital input 2 see subindex 0x8022:32 | BIT4 | RW | 0x00 (0dec) |
Index 8023 DCM Controller Settings 2 Ch.1
8023:0 | DCM Controller Settings 2 Ch.1 | Max. Subindex | UINT8 | RO | 0x08 (8dec) |
8023:01 | Kp factor (velo./pos.) | Kp control factor of the velocity/position controller | UINT16 | RW | 0x00C8 (200dec) |
8023:02 | Ki factor (velo./pos.) | Ki control factor of the velocity/position controller | UINT16 | RW | 0x0002 (2dec) |
8023:03 | Inner window (velo./pos.) | Inner window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8023:05 | Outer window (velo./pos.) | Outer window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8023:06 | Filter cut off frequency (velo./pos.) | Limit frequency of the velocity/position controller Unit: 1 Hz | UINT16 | RW | 0x0000 (0dec) |
8023:07 | Ka factor (velo./pos.) | Ka control factor of the velocity/position controller | UINT16 | RW | 0x0000 (0dec) |
8023:08 | Kd factor (velo./pos.) | Kd control factor of the velocity/position controller | UINT16 | RW | 0x0014 (20dec) |
Index 8030 DCM Motor Settings Ch.2
8030:0 | DCM Motor Settings Ch.2 | Max. Subindex | UINT8 | RO | 0x0F (15dec) |
8030:01 | Maximal current | Maximum permanent motor coil current Unit: 1 mA | UINT16 | RW | 0x1388 (5000dec) |
8030:02 | Nominal current | Motor nominal current Unit: 1 mA | UINT16 | RW | 0x0DAC (3500dec) |
8030:03 | Nominal voltage | Nominal voltage (supply voltage) of the motor Unit: 1 mV | UINT16 | RW | 0xC350 (50000dec) |
8030:04 | Motor coil resistance | Internal resistance of the motor Unit: 0.01 ohm | UINT16 | RW | 0x0064 (100dec) |
8030:05 | Reduced current (positive) | Reduced torque in positive direction of rotation Unit: 1 mA | UINT16 | RW | 0x07D0 (2000dec) |
8030:06 | Reduced current (negative) | Reduced torque in negative direction of rotation Unit: 1 mA | UINT16 | RW | 0x07D0 (2000dec) |
8030:07 | Encoder increments (4-fold) | Number of encoder increments per revolution with quadruple evaluation | UINT16 | RW | 0x0000 (0dec) |
8030:08 | Maximal motor velocity | Rated motor velocity at nominal voltage Unit: 1 rpm | UINT16 | RW | 0x0000 (0dec) |
8030:0C | Time for switch-off at overload | Time for switch-off at overload Unit: 1 ms | UINT16 | RW | 0x00C8 (200dec) |
8030:0D | Time for current lowering at overload | Time for current lowering at overload (from max. current to nominal current) Unit: 1 ms | UINT16 | RW | 0x07D0 (2000dec) |
8030:0E | Torque auto-reduction threshold (positive) | Process data threshold for automatic torque reduction in the positive direction of rotation Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
8030:0F | Torque auto-reduction threshold (negative) | Process data threshold for automatic torque reduction in the negative direction of rotation Unit: 1 % | UINT8 | RW | 0x00 (0dec) |
Index 8031 DCM Controller Settings Ch.2
8031:0 | DCM Controller Settings Ch.2 | Max. Subindex | UINT8 | RO | 0x12 (18dec) |
8031:01 | Kp factor (curr.) | Kp control factor of the current controller | UINT16 | RW | 0x00C8 (200dec) |
8031:02 | Ki factor (curr.) | Ki control factor of the current controller | UINT16 | RW | 0x0002 (2dec) |
8031:03 | Inner window (curr.) | Inner window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8031:05 | Outer window (curr.) | Outer window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8031:06 | Filter cut off frequency (curr.) | Limit frequency of the current controller Unit: 1 Hz | UINT16 | RW | 0x0000 (0dec) |
8031:11 | Voltage adjustment enable | Activates the compensation of voltage fluctuations (only in the operating mode "Direct velocity") | BOOLEAN | RW | 0x00 (0dec) |
8031:12 | Current adjustment enable | Activates the R x I compensation | BOOLEAN | RW | 0x00 (0dec) |
Index 8032 DCM Features Ch.2
8032:0 | DCM Features Ch.2 | Max. Subindex | UINT8 | RO | 0x36 (54dec) |
8032:01 | Operation mode | Operation mode 0: Automatic ...: reserved 15: Chopper resistor | BIT4 | RW | 0x00 (0dec) |
8032:09 | Invert motor polarity | Inverts the direction of rotation of the motor | BOOLEAN | RW | 0x00 (0dec) |
8032:0A | Torque error enable | Activates the automatic overload cut-off (see also subindex 0x8030:0C) | BOOLEAN | RW | 0x00 (0dec) |
8032:0B | Torque auto reduce | Activates the automatic torque reduction (see also subindex 0x8030:0D – 0x8030:0F) | BOOLEAN | RW | 0x00 (0dec) |
8032:11 | Select info data 1 | Selection "Info data 1" 0: Status word ....: reserved 7: Motor velocity ...: reserved 101: Internal temperature ...: reserved 103: Control voltage ...: reserved 150: Status word (drive controller) ...: reserved | UINT8 | RW | 0x01 (1dec) |
8032:19 | Select info data 2 | Selection "Info data 2" see subindex 0x8032:11 | UINT8 | RW | 0x02 (2dec) |
8032:30 | Invert digital input 1 | Inversion of digital input 1 | BOOLEAN | RW | 0x00 (0dec) |
8032:31 | Invert digital input 2 | Inversion of digital input 2 | BOOLEAN | RW | 0x00 (0dec) |
8032:32 | Function for input 1 | Function of digital input 1 0: Normal input | BIT4 | RW | 0x00 (0dec) |
8032:36 | Function for input 2 | Function of digital input 2 see subindex 0x8032:32 | BIT4 | RW | 0x00 (0dec) |
Index 8033 DCM Controller Settings 2 Ch.2
8033:0 | DCM Controller Settings 2 Ch.2 | Max. Subindex | UINT8 | RO | 0x08 (8dec) |
8033:01 | Kp factor (velo./pos.) | Kp control factor of the velocity/position controller | UINT16 | RW | 0x00C8 (200dec) |
8033:02 | Ki factor (velo./pos.) | Ki control factor of the velocity/position controller | UINT16 | RW | 0x0002 (2dec) |
8033:03 | Inner window (velo./pos.) | Inner window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8033:05 | Outer window (velo./pos.) | Outer window for the I component Unit: 1% | UINT8 | RW | 0x00 (0dec) |
8033:06 | Filter cut off frequency (velo./pos.) | Limit frequency of the velocity/position controller Unit: 1 Hz | UINT16 | RW | 0x0000 (0dec) |
8033:07 | Ka factor (velo./pos.) | Ka control factor of the velocity/position controller | UINT16 | RW | 0x0000 (0dec) |
8033:08 | Kd factor (velo./pos.) | Kd control factor of the velocity/position controller | UINT16 | RW | 0x0014 (20dec) |
Index 8040 POS Settings Ch.1
8040:0 | POS Settings Ch.1 | Max. Subindex | UINT8 | RO | 0x10 (16dec) |
8040:01 | Velocity min. | Minimum set velocity Range: 0-10000 | INT16 | RW | 0x0064 (100dec) |
8040:02 | Velocity max. | Maximum set velocity Range: 0-10000) | INT16 | RW | 0x2710 (10000dec) |
8040:03 | Acceleration pos. | Acceleration in positive direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8040:04 | Acceleration neg. | Acceleration in negative direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8040:05 | Deceleration pos. | Deceleration in positive direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8040:06 | Deceleration neg. | Deceleration in negative direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8040:07 | Emergency deceleration | Emergency deceleration (both directions of rotation) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8040:08 | Calibration position | Calibration position | UINT32 | RW | 0x00000000 (0dec) |
8040:09 | Calibration velocity (towards plc cam) | Calibration velocity towards the cam Rrange: 0-10000 | INT16 | RW | 0x0064 (100dec) |
8040:0A | Calibration Velocity (off plc cam) | Calibration velocity away from the cam Range: 0-10000 | INT16 | RW | 0x000A (10dec) |
8040:0B | Target window | Target window | UINT16 | RW | 0x000A (10dec) |
8040:0C | In-Target timeout | Timeout at target position Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8040:0D | Dead time compensation | Dead time compensation Unit: 1 µs | INT16 | RW | 0x0032 (50dec) |
8040:0E | Modulo factor | Modulo factor/position | UINT32 | RW | 0x00000000 (0dec) |
8040:0F | Modulo tolerance window | Tolerance window for modulo positioning | UINT32 | RW | 0x00000000 (0dec) |
8040:10 | Position lag max. | Max. permitted position lag | UINT16 | RW | 0x0000 (0dec) |
Index 8041 POS Features Ch.1
8041:0 | POS Features Ch.1 |
| UINT8 | RO | 0x16 (22dec) |
8041:01 | Start type | Standard start type 0: Idle | UINT16 | RW | 0x0001 (1dec) |
8041:11 | Time information | Time information in subindex 0x6040:22/0x6050:22 (“Actual drive time”) 0: Elapsed time ...: reserved | BIT2 | RW | 0x00 (0dec) |
8041:13 | Invert calibration cam search direction | Inversion of the direction of rotation towards the cam | BOOLEAN | RW | 0x01 (1dec) |
8041:14 | Invert sync impulse search direction | Inversion of the direction of rotation away from the cam | BOOLEAN | RW | 0x00 (0dec) |
8041:15 | Emergency stop on position lag error | Lag error monitoring has triggered As soon as "Position lag" = 1.
8041:16 | Enhanced diag history | TRUE: | BOOLEAN | RW | 0x00 (0dec) |
Index 8050 POS Settings Ch.2
8050:0 | POS Settings Ch.2 | Max. Subindex | UINT8 | RO | 0x10 (16dec) |
8050:01 | Velocity min. | Minimum set velocity Range: 0-10000 | INT16 | RW | 0x0064 (100dec) |
8050:02 | Velocity max. | Maximum set velocity Range: 0-10000 | INT16 | RW | 0x2710 (10000dec) |
8050:03 | Acceleration pos. | Acceleration in positive direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8050:04 | Acceleration neg. | Acceleration in negative direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8050:05 | Deceleration pos. | Deceleration in positive direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8050:06 | Deceleration neg. | Deceleration in negative direction of rotation Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8050:07 | Emergency Deceleration | Emergency deceleration (both directions of rotation) Unit: 1 ms | UINT16 | RW | 0x0064 (100dec) |
8050:08 | Calibration position | Calibration position | UINT32 | RW | 0x00000000 (0dec) |
8050:09 | Calibration velocity (towards plc cam) | Calibration velocity towards the cam Range: 0-10000 | INT16 | RW | 0x0064 (100dec) |
8050:0A | Calibration Velocity (off plc cam) | Calibration velocity away from the cam Range: 0-10000 | INT16 | RW | 0x000A (10dec) |
8050:0B | Target window | Target window | UINT16 | RW | 0x000A (10dec) |
8050:0C | In-Target timeout | Timeout at target position Unit: 1 ms | UINT16 | RW | 0x03E8 (1000dec) |
8050:0D | Dead time compensation | Dead time compensation Unit: 1 µs | INT16 | RW | 0x0032 (50dec) |
8050:0E | Modulo factor | Modulo factor/position | UINT32 | RW | 0x00000000 (0dec) |
8050:0F | Modulo tolerance window | Tolerance window for modulo positioning | UINT32 | RW | 0x00000000 (0dec) |
8050:10 | Position lag max. | Max. permitted position lag | UINT16 | RW | 0x0000 (0dec) |
Index 8051 POS Features Ch.2
8051:0 | POS Features Ch.2 | Max. Subindex | UINT8 | RO | 0x16 (22dec) |
8051:01 | Start type | Standard start type 0: Idle | UINT16 | RW | 0x0001 (1dec) |
8051:11 | Time information | Time information in subindex 0x6040:22/0x6050:22 (“Actual drive time”) 0: Elapsed time ...: reserved | BIT2 | RW | 0x00 (0dec) |
8051:13 | Invert calibration cam search direction | Inversion of the direction of rotation towards the cam | BOOLEAN | RW | 0x01 (1dec) |
8051:14 | Invert sync impulse search direction | Inversion of the direction of rotation away from the cam | BOOLEAN | RW | 0x00 (0dec) |
8051:15 | Emergency stop on position lag error | Lag error monitoring has triggered
8051:16 | Enhanced diag history | TRUE: | BOOLEAN | RW | 0x00 (0dec) |
