EJ41xx- Analog Output Modules (16 Bit)
EJ413x - Technical Data
Technical data
EJ4132
EJ4134
Connection technology
2-wire, single-ended
Number of outputs
2
4
Signal voltage
-10 V to +10 V
Distributed Clocks
yes
Maximum cable length to the sensor
30 m (see note)
Accuracy Distributed Clocks
<< 1 µs
Load
> 5 kΩ (short-circuit-proof)
Measuring error
< 0.1 % (at 0°C .. +55°C, relative to full scale value)
< ±0.2 % (when the extended temperature range is used)
Resolution
16 bit (including sign)
16-bit
Electrical isolation
500 V (E-bus/field voltage)
Conversion time
~ 40 µs
~ 200 µs
Current consumption load voltage (Up contacts)
typ. 40 mA
Current consumption via E-bus
typ. 185 mA
typ. 90 mA
Permissible ambient temperature range during operation
-25°C .. +60°C (extended temperature range)
Permissible ambient temperature range during storage
-40 °C .. +85 °C
Permissible relative air humidity
95 %, no condensation
Operating altitude
max. 2,000 m
Dimensions (W x H x D)
approx. 12 mm x 66 mm x 55 mm
Pollution degree
2
Weight
approx. 30 g
Mounting
on signal distribution board
Mounting position
1 and 7
Color coding
blue
Vibration / shock resistance
conforms to EN 60068-2-6 /EN 60068-2-27 (with corresponding signal distribution board)
EMC immunity / emission
conforms to EN 61000-6-2 /EN 61000-6-4 (with corresponding signal distribution board)
Protection class
EJ module: IP20
EJ system: dependent on the signal distribution board and housing
Approval
CE, UL
CE approval
The CE Marking refers to the EtherCAT plug-in module mentioned above.
If the EtherCAT plug-in module is used in the production of a ready-to-use end product (PCB in conjunction with a housing), the manufacturer of the end product must check compliance of the overall system with relevant directives and CE certification.
To operate the EtherCAT plug-in modules, they must be installed in a housing.
Without additional protective measures, the maximum cable length from the EtherCAT Module to the sensor is 30 m. For longer cable lengths, suitable surge protection should be provided.