Configuration data
Index 80n0 TC settings for 0 ≤ n ≤ 7 (Ch. 1 - 8)
80n0:0 | TC Settings | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
80n0:01 | Enable user scale | User scale is active. | BOOLEAN | RW | 0x00 (0dec) |
80n0:02 | Presentation | 0: Signed presentation 1: Absolute value with MSB as sign 2: High resolution (1/100 C°) | BIT3 | RW | 0x00 (0dec) |
80n0:05 | Siemens bits | The S5 bits are superimposed on the three low-order bits (value 0x60n0:11) Bit 0 = 1 (“overrange” or “underrange”) | BOOLEAN | RW | 0x00 (0dec) |
80n0:06 | Enable filter | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary | BOOLEAN | RW | 0x00 (0dec) |
80n0:0A | Enable user calibration | Enabling of the user calibration | BOOLEAN | RW | 0x00 (0dec) |
80n0:0B | Enable vendor calibration | Enabling of the vendor calibration | BOOLEAN | RW | 0x01 (1dec) |
80n0:0C | Coldjunction compensation | 0: internal 1: no 2: Extern process data | BIT2 | RW | 0x00 (0dec) |
80n0:11 | User scale offset | User scaling offset | INT16 | RW | 0x0000 (0dec) |
80n0:12 | User scale gain | This is the user scaling gain. | INT32 | RW | 0x00010000 (65536dec) |
80n0:15 | Filter settings | This object determines the digital filter settings, if it is active via Enable filter (index 80n0:06). 0: 50 Hz | UINT16 | RW | 0x0000 (0dec) |
80n0:17 | User calibration offset | User offset calibration | UINT16 | RW | 0x0000 (0dec) |
80n0:18 | User calibration gain | User gain compensation | UINT16 | RW | 0xFFFF (65535dec) |
80n0:19 | TC element | Thermocouple 0: K, -200°C to 1370°C | UINT16 | RW | 0x0000 (0dec) |
The filter characteristics are set via index 0x8000:15 The filter frequencies are set for all channels of the module centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set. |
Index 8080 RTD Settings Ch. 1
8080:0 | RTD Settings Ch1. | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
8080:19 | RTD element | RTD element 2: PT1000 (-200…850°C) | BOOLEAN | RW | 0x02 (2dec) |
8080:1A | Connection technology | Permitted values 0: Two-wire connection | BIT3 | RW | 0x00 (0dec) |
8080:1B | Wire calibration 1/32 Ohm | Offset-value for calibration of supply lines [1/32] Ohm | INT16 | RW | 0x0000 (0dec) |
Index 8090 RTD Settings Ch. 2
8090:0 | RTD Settings Ch2. | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
8090:19 | RTD element | RTD element 2: PT1000 (-200…850°C) | BOOLEAN | RW | 0x02 (2dec) |
8090:1A | Connection technology | Permitted values 0: Two-wire connection | BIT3 | RW | 0x00 (0dec) |
8090:1B | Wire calibration 1/32 Ohm | Offset-value for calibration of supply lines [1/32] Ohm | INT16 | RW | 0x0000 (0dec) |