Configuration data
Index 80n0 RTD settings for 0 ≤ n ≤ 3 (Ch. 1 - 4)
The filter characteristics are set via index 0x8000:15 The filter frequencies are set for all channels of the module centrally via index 0x8000:15 (channel 1). All other corresponding indices 0x80n0:15 have no parameterization function! The latest firmware version (see status table) returns an EtherCAT-compliant error message, if the filter characteristics of other channels (index 0x80n0:06, 0x80n0:15) are set. |
Index (hex) | Name | Meaning | Data type | Flags | Default value |
80n0:0 | RTD Settings | Maximum subindex | UINT8 | RO | 0x1B (27dec) |
80n0:01 | Enable user scale | User scale is active. | BOOLEAN | RW | 0x00 (0dec) |
80n0:02 | Presentation | 0: Signed presentation 1: Absolute value with MSB as sign 2: High resolution (1/100 C°) | BIT3 | RW | 0x00 (0dec) |
80n0:05 | Siemens bits | The S5 bits are superimposed on the three low-order bits (value 0x60n0:11) Bit 0 = 1 (“overrange” or “underrange”) | BOOLEAN | RW | 0x00 (0dec) |
80n0:06* | Enable filter | Enable filter, which makes PLC-cycle-synchronous data exchange unnecessary | BOOLEAN | RW | 0x00 (0dec) |
80n0:07* | Enable limit 1 | The status bits are set in relation to Limit 1 | BOOLEAN | RW | 0x00 (0dec) |
80n0:08* | Enable limit 2 | The status bits are set in relation to Limit 2 | BOOLEAN | RW | 0x00 (0dec) |
8010:09* | Enable automatic calibration | A calibration is cyclically started. (optional) | BOOLEAN | RW | 0x00 (0dec) |
80n0:0A | Enable user calibration | Enabling of the user calibration | BOOLEAN | RW | 0x00 (0dec) |
80n0:0B | Enable vendor calibration | Enabling of the vendor calibration | BOOLEAN | RW | 0x01 (1dec) |
80n0:11 | User scale offset | User scaling offset | INT16 | RW | 0x0000 (0dec) |
80n0:12 | User scale gain | This is the user scaling gain. | INT32 | RW | 0x00010000 (65536dec) |
80n0:13* | Limit 1 | First limit value for setting the status bits (resolution 0.1 °C) | INT16 | RW | 0x0000 (0dec) |
80n0:14* | Limit 2 | Second limit value for setting the status bits (resolution 0.1 °C) | INT16 | RW | 0x0000 (0dec) |
*) not for EJ3214
80n0:15 | Filter settings | This object determines the digital filter settings, if it is active via Enable filter (index 80n0:06). 0: 50 Hz | UINT16 | RW | 0x0000 (0dec) |
80n0:17 | User calibration offset | User offset calibration | INT16 | RW | 0x0000 (0dec) |
80n0:18 | User calibration gain | User gain compensation | UINT16 | RW | 0xFFFF (65535dec) |
80n0:19 | RTD element | RTD element 0: Pt100 1: Ni100 (-60°C to 250°) 2:Pt1000 (-200°C to 850°C) 3: Pt500 (-200°C to 850°C) 4: Pt200 (-200° C to 850°C) 5: Ni1000 (-60°C to 250°C) 6: Ni1000 ,100°C: 1500 Ohm (-30°C to 160°C) 7: Ni120 (-60°C to 320°C) 8: Output in Ohm, Resolution 1/16 Ohm (10 to 4095 Ohm) 9: Output in Ohm, Resolution 1/64 Ohm (10 to 1047 Ohm) 10-32: KT100/110/130/210/230 KTY10/11/13/16/19 | UINT16 | RW | 0x0000 (0dec) |
80n0:1A | Connection technology | Connection technology 0: Two-wire connection | UINT16 | RW | 0x0000 (0dec) |
80n0:1B | Wire calibration 1/32 Ohm | Calibration of the supply lines | INT16 | RW | 0x0000 (0dec) |
*) not for EJ3214