IN1MODE
ASCII - Command
IN1MODE
Syntax Transmit
IN1MODE [Data]
Syntax Receive
IN1MODE <Data>
Available in
Type
Variable rw
MMI
Yes
ASCII Format
Integer8
CANBus Object Number
3562 (hex)
DIM
PROFIBUS PNU
1698 (dec) IND = 0000xxxx (bin)
Range
0 .. 50
DPR
98 (dec)
Default
0
Opmode
All
Data Type Bus/DPR
Integer8
Drive State
Disabled + Reset (Coldstart)
Weightning
Start Firmware
1.20
Configuration
Yes
Revision
1.9
Function Group
Digital I/O
EEPROM
Yes
Short Description
Function of Digital Input 1
The IN1MODE command is used to configure the function of the digital input INPUT1. The amplifier must be switched off and then on again after an alteration of this parameter.
The following functions can be configured:
Status
Function
IN1MODE=0
Off
The state of the input 1 is read and can be used via fieldbus or Slot card.
IN1MODE=1
Reset
Software reset of the servo amplifier in the event of a fault. The high input signal is ignored, if the drive has no fault. All the functions and displays are set to
the initial status. Parameters that are not stored in the EEPROM are erased, the parameter set that
is stored in the EEPROM is loaded.
If any of the error messages F01, F02, F03, F05, F08, F13, F16 or F19 ( p.52) are present, then
no software-reset will be carried out, just the error message will be deleted. This means that, for
example, the encoder output signals are stable and can continue to be evaluated by the controls.
When the input is high, while the auxillary 24V supply is switched on, the drive waits, before the input is set to low. This state is symbolised in the display. The first of the three display positions displays a "A".
IN1MODE=2
Off
IN1MODE=3
Off
IN1MODE=4
Off
IN1MODE=5
Off
IN1MODE=6
Off
IN1MODE=7
Off
IN1MODE=8
SETP.1 / SETP.2
Switches over the setpoint inputs SW/SETP.1/2 at ANCNFG = 0. This function is only effective if the analog set-point
function 0,Xcmd=Setp.1 has been selected.
High level at the input : Setpoint input 2 (terminals X3/6,7) is active
Low level at the input : Setpoint input 1 (terminals X3/4,5) is active
IN1MODE=9
MT_No_Bit
Here you can select the motion tasks that are stored in the servo amplifier (numbers 1...7) or the
reference traverse/homing (0). The motion task number is presented externally at the digital inputs
as a logical word, with a width of max. 3 bits . An input is required to start the motion task (INxMODE =17,
Start_MT IO). If you wire up a reference/homing switch (INxMODE =12, Reference) and (also) want to start a
following task (INxMODE =15, Start_MT Next) externally, the number of inputs that are available for selecting
the motion tasks will be further reduced.
This function can also be used for the VCT entry functionality, to select the adress of the VCT's. The start of the VCT entry is done by selecting one input with INxMODE=35.
IN1MODE=10
Intg.Off
Switch off the integral component of the velocity controller, the P-gain remains at the set value, the
actual- (rotational) velocity feedback remains in operation.
IN1MODE=11
V / Torq.Contr.
Bypasses the velocity controller. The analog setpoint is taken 1:1 as the setpoint for current control,
i.e. change over from velocity control to current (torque) control.
High-level at the input : torque control
Low-level at the input : velocity control
Depending on OPMODE, it changes between OPMODE=0 (low) and OPMODE=2 (high) or OPMODE=1 (low) and OPMODE=3 (high).
IN1MODE=12
Reference
Polls the reference switch.
IN1MODE=13
ROD/SSI
Changeover of the encoder-emulation (position output) on connector X5.
High level at the input : SSI-compatible position signals (ENCMODE = 2)
High level at the input : ROD-compatible position signals (ENCMODE = 1)
IN1MODE=14
FError_clear
Clear the warning of a contouring error (display n03) or the response monitoring (display n04).
IN1MODE=15
Start_MT Next
The following task, that is defined in the motion task by “Start with I/O” is started. The target position
of the present motion task must be reached before the following task can be started.
IN1MODE=16
Start_MT No x
Start a motion task that is stored in the servo amplifier, by giving the motion task number. After the
function has been selected you can enter the motion task number as the auxiliary variable IN1TRIG.
Motion task number “0” (IN1TRIG=0) initiates homing/reference traverse. A rising edge starts the motion task, a
falling edge cancels the motion task.
IN1MODE=17
Start_MT IO
17, Start_MT IO Start of the motion task that has the number that is presented, bit-coded, at the digital inputs
(PSTOP/NSTOP/DIGITAL-IN1/DIGITAL-IN2, see function 9, MT_No_Bit ). A rising edge starts the
motion task a falling edge cancels the motion task by a STOP - command
IN1MODE=18
Ipeak2 x
Switch over to a second (lower) peak value of current. Scaled as x (0...100) % of the peak current
of the instrument. After the function has been selected you can enter the percentage value as the
Make the conversion according to the following equation:
IN1TRIG given in % of IPEAK
IN1MODE=19
Off
IN1MODE=20
Start_Jog v=x
Start of the setup mode "Constant velocity" with a defined speed. After selecting the
function, you can enter the speed in IN1TRIG. A rising edge starts the motion, a
falling edge cancels the motion. This function works in position control, so OPMODE=8 has to be selected. The speed is given in units of the position controller given by VUNIT.
IN1MODE=21
U_Mon.off
Turns off the undervoltage monitoring function of the servo amplifier.
IN1MODE=22
MT Restart
Continues the motion task that was previously interrupted by a STOP - command.
IN1MODE=23
Start2_MT No x
Start of a motion task that is stored in the servo amplifier, with definition of the motion task number.
After selecting the function, you can enter the motion task number in IN1TRIG
Motion task number “0” starts the homing run. A rising edge starts the motion task.
Warning !
The motion task does not stop automatically if the start signal is removed !
The motion task must be stopped by
— a falling edge on another digital input (configured with 16, FStart_Nr x)
— the ASCII command STOP
— the STOP function via Bus or digital input
IN1MODE=24
Switch over OPMODE
The two different OPMODEs, that can be selected for switching over via the digital input, are written in the IN1TRIG help variable of the this input. The lower byte consists the OPMODE that should be available when the input has a negative edge. The higher byte consists the OPMODE that should be available when the input has a positive edge. When the drive is switched on, the OPMODE is set automatically to the corresponding state of the input. The contents of the help variable must be in decimal !!
e.g.:
Input1=low OPMODE=4
Input1=high OPMODE=8
IN1MODE=24 (Activate Input)
IN1TRIG=2052 (Decimal 0804h)
2052 (Dec) = 0804 (Hex)
IN1MODE=25
Zero_latch
Sets the ROD zero pulse offset. The current position, depending on the ROD resolution that is set,
is calculated at the rising edge and stored as NI-Offset in ENCZERO. After that, an automatic SAVE is generated. This function is used to perform
an automatic setting of the zero pulse in one turn of the motor..
IN1MODE=26
Position Latch
A edge on this input latches the actual position. The position can then be read by LATCHX32 (positive edge) or LATCHX32N (negative edge). The actual 16-Bit position (absolute in one turn) can be read by LATCHX16 (positive edge) and LATCHX16N (negative edge). The status of the latching can be read by the equivalent bits of DRVSTAT.
The min. cycle time for a low/high to high/low transaction is 500µs. The min. time between two latch pulses is 8 msec.
The Latch function does not work with POSCNFG=1.
IN1MODE=27
Emergency Stop
Low state on the input starts an emergency stop function, that is executed with the ramp DECSTOP. Independently of the selected OPMODE, in this phase, the drive stops in velocity control. When it has stopped, it switches over to the original mode.
IN1MODE=28
Reserved
IN1MODE=29
Reserved
IN1MODE=30
Command Buffer 1
A positive or negative edge on the input starts a command buffer. This command buffer contains separate ASCII objects, that are separated with semicolon (;).
The command buffer for the positive edge is INHCMD, the command buffer for the negative edge is INLCMD.
The max. length of that buffers is 56 character for each.
If a digital input is configured with INxMODE=30, this input will proceed in that way.
When the drive is switched on, the Command buffer is set automatically started to the corresponding state of the input.
Remark: Only one of the digital inputs can use the INxMODE=30 function.
IN1MODE=31
Command Buffer 2
The command buffer for the positive edge is INHCMDX, the command buffer for the negative edge is INLCMDX.
If a digital input is configured with INxMODE=31, this input will proceed in that way.
Remark: Only one of the digital inputs can use the INxMODE=31 function.
IN1MODE=32
Brake
A rising edge at the input triggers the braking output of the servo amplifier.
This function is only available while the amplifier is disabled. If an error message is active, the
brake cannot be de-energized.
Warning !
With suspended loads, this function will lead to slipping of the axes ! Starting with 4.78, this function also works if the drive has an error.
IN1MODE=33
see 30
Different from the functionality 30, the resulting answers of the commands are not suppressed, but are send to the seriell communication channel RS232.
IN1MODE=34
see 31
Different from the functionality 31, the resulting answers of the commands are not suppressed, but are send to the seriell communication channel RS232.
IN1MODE=35
Select Velocity/Current Entry
A positive edge on the digital input causes a takeover of the corresponding VCT entry (see command VCT). The number of the VCT entry is defined by the digital inputs configured with mode 9.
IN1MODE=36
Give Offset to Gearing Function
Gearing mode OPMODE =4.
A high signal on the digital input configured with this INxMODE adds a difference velocity to the gearing. This allows a simple synchronisation of two axes. The difference velocity is given to IN1TRIG. The scaling is in 20Bit per revolution every 250µs. The difference velocity (n) must be known, then the IN1TRIG can be calculated:
IN1TRIG= n * 250 / ( 60 * rpm)
e.g.
n = 50 rpm
IN1TRIG = 208
IN1MODE=37
Change source of the actual position at EXTPOS=1.
= 0 Actual position is generated by the external encoder selected by GEARMODE
= 1 Actual position is generated by the first feedback device (resolver od high resolution feedback EnDAT or Hiperface)
IN1MODE=38
Enable signal for following motion task
Definition of a motion task with following motion tasks. If INxMODE=15 is used (start of an following motion task via I/O), IN1MODE=38 can be used, to have an additional enable for the start of the following motion tasks. Means, that the following motion task is started, if once a rising edge on digital input 1 was detected and then the INxMODE=15 input is enabled to start the following motion task.
IN1MODE=39
Constant velocity for defined time
This function starts a constant velocity for a defined time. The parameters for velocity and time are given by IN1TRIG. The velocity is given by the lower 16 bit (scaling by VUNIT) and the time by the upper 16 bit (given in msec) of the help variable IN1TRIG.
A rising edge at INPUT1 changes the OPMODE to 0 (digital velocity)
and gives the velocity that is given by IN1TRIG.
After the defined time or a falling edge at INPUT1 is detected, the digital velocity setpoint is set to "0". After the actual velocity has reached "0" the OPMODE is automatically switched back to the old one.
Example for defining the help variable IN1TRIG
1. Velocity = 1000 rpm
time = 10 sec = 10000 msec
IN1TRIG = 0x271003E8 = 655361000
2. Velocity = -500 rpm
time = 10 msec
IN1TRIG = 0x000afe0c = 720396
IN1MODE=40
Additional hardware input
The digital input works as an additional hardware input. Only if this input has a high signal, the power stage is enabled.
This Function can be used by several inputs. In this case, the inputs are configured in series. All inputs have to be high to enable the power stage. (Starting firmware 4.91)
IN1MODE=41
Fast emergency stop
If the input is going to low, the drive stops the motor using the DECSTOP ramp. If zero velocity is reached (V<VEL0), the power stage is disabled.
While stopping the motor the bit 24 (0x01000000) in TRJSTAT is set.
The input is read in the 250µs task.
IN1MODE=42
Activate/deactivate electronic gearing
Activate/deactivate electronic gearing in OPMODE = 4.
This function is practical only with slave axis.
A rising edge on the digital input starts the motion from 0 to the master speed and a falling edge changes the speed from master speed to 0.
The ramp times can be set by ACCR for the acceleration and DECR for deceleration time (stating with firmware 5.51).
IN1MODE=43
Activate/deactivate electronic gearing with position latch
In contrast to IN1MODE = 42, the master position is latched at the rising edge of the input and the position delay caused by the ramp is compensated. IN1TRIG gives the possibility to add an position offset (in PGEARI units) to the latched position(starting with Firmware 5.51).