Hidden Parameters
For the advanced operation and configuration of the Mover ID detection you have the option to use Hidden Parameters. For example, you can adjust various waiting times of the movers.
The following table shows the default parameters:
Hidden Parameters
Default
Min
Max
Unit
Tab
DetectionStandstillVelocityLimit
15
1
1000
mm/s
Init
DetectionStandstill­SwitchTime
0.015
0.00
1.0
s
Init
DetectionTimeOut
2
0
10
s
Init
DetectionInfoMessage
FALSE
FALSE
TRUE
Init
Hidden Parameters 1:
►Activate the checkbox Show Hidden Parameter to show the Hidden Parameters
Definition of the maximum velocity for the standstill monitoring.
Value < default parameter:
The search changes to the next phase later.
Value > default parameter:
The search changes to the next phase earlier.
DetectionStandstillSwitchTime
Time in which the velocity of the mover must be below the value of the parameter DetectionStandstillVelocityLimit .
The search is accelerated.
The search is decelerated.
DetectionTimeOut
Total timeout for the Mover ID detection. An error occurs if this time is reached. Possible causes:
You should always be able to achieve the DetectionMinMovement with the default parameter DetectionMaxCurrent.
Messages are displayed in the TwinCAT output window.