PressureControl.PID
This core function implements an extended PID controller functionality. The pressure value read by the Supervisor is used as the controlled variable. The velocity of the axis is controlled as the manipulated variable. Accordingly, this control structure can be used for a range of tasks:
- Holding pressure control in injection molding machines
- Back pressure control in injection molding machines
- Melt pressure control for extruders
- Others
Properties
Name | Type | Access | Description |
InitState | BOOL | Get, Set | The core function is not completely and successfully initialized. |
FB_PressureControl_PID | |||
Actual | BOOL | Get | Current actual pressure value. |
AllowSwitchOver | BOOL | Get, Set | Allows switching from another active Corefunction to pressure control. Currently, only |
Limiting | LREAL | Get, Set | Setpoint for the limitation (e.g., torque, pressure) during pressure control. |
I_PressureControlParams_PID | Get, Set | Parameter set that is used for control. The parameter sets can be switched by assignment. If a 0 is assigned, the internal parameter set is used. | |
PressureLookUp | I_PressureLookUp | Get, Set | Pressure setpoint table for sequential processing of Pressure setpoints. |
Target | LREAL | Get, Set | Command variable (setpoint) of the controller. |
IsEnabled1 | BOOL | Get | A TRUE signals the active state of the pressure switchover. |
FB_CorefunctionFeedback | |||
AbortedState | BOOL | Get, Set | Signals the abort of a command by another Corefunction. |
BusyState | BOOL | Get, Set | Signals the active execution of a command. |
DoneState | BOOL | Get, Set | Signals the successful execution of a command. |
IdleState | BOOL | Get, Set | The Corefunction is ready for operation and commandable. |
IsCommanded | BOOL | Get | Signals the pending of a command. |
FB_Corefunction | |||
FailedState | BOOL | Get, Set | If IsActivated is TRUE at the same time: Signals the failure of an accepted command. If IsActivated is FALSE at the same time: Signals the rejection of a command. |
HasFeedback | BOOL | Get | The core function has responded to a pending command. |
IsActivated | BOOL | Get | The core function has an accepted command pending. |
IsLocalCmd | BOOL | Get | Signals that the axis is assigned with a command of this core function. |
ReadyState | BOOL | Get, Set | The Corefunction is ready for operation, but is not commandable at this time. Possible reasons are: |
Methods
Name | Description |
Activate / deactivate the controller. | |
Activate the controller by switching another command. | |
Enable for automatic activation by a PressureHandler. | |
The actual value of the controller is determined. | |
An interface to the connected parameter set is determined. | |
A parameter set is connected to the controller. | |
Set the command variable (setpoint) of the controller. |
1Obsolete
Interfaces
Type | Description |
I_Corefunction | Standard interface on FB_Corefunction. |
I_PressureControl | Standard interfaces on FB_PressureControl_PID. |
I_CorefunctionFeedback | Standard interface on FB_CorefunctionFeedback. |
Example:
// Requires connected pressure input, e.g. via PressureControl.Supervisor.Sensor
// Start pressure control on application start signal
IF bStart THEN
// Assign pressure setpoint
iAxisBase.PressureControl.PID.Target := 20.0;
// parameterize once before activation and activate
IF iAxisBase.PressureControl.PID.IdleState THEN
iAxisBase.PressureControl.PID.Limiting := 80.0;
iAxisBase.PressureControl.PID.Parameters.Kp := 0.5;
iAxisBase.PressureControl.PID.Parameters.EnableI := TRUE;
iAxisBase.PressureControl.PID.Parameters.Tn := 1.0;
iAxisBase.PressureControl.PID.Activate(TRUE);
// wait until function is terminated
ELSIF bStop THEN
bStart := FALSE;
iAxisBase.PressureControl.PID.Activate(FALSE);
END_IF
END_IF
Development Environment | Target platform | PLC libraries to include |
TwinCAT v3.1.4024.66 | PC or CX (x64, x86) | Tc3_PlasticFunctions (>= v12.10.0.0) |