ST_TcPfw_SupplyParam
This structure describes the parameters and runtime data of a supply unit.
TYPE ST_TcPfw_SupplyParam :
(* last modification: 28.05.2008 *)
STRUCT
see cnv_SupplyParam_TcPfw for format definition
temperature controller pwm setup
fPwmCycleTime   : LREAL; (* will be updated to all temperature zones in supply group *)
fPwmMinOnTime   : LREAL;  (* will be updated to all temperature zones in supply group *)
fPwmMaxOnTime   : LREAL; (* will be updated to all temperature zones in supply group *)
fPwmMaxOnC      : LREAL;
fPwmMaxRampLoad : LREAL;        (* in kW, will be updated to all temperature zones in supply group *)
fActSupplyLoad  : LREAL;
fActSupplyCurrent: LREAL;
fSupplyLoad     : LREAL;
fSupplyMatch    : LREAL;
nPwmFactorC     : INT:=1; (* will be updated to all temperature zones in supply group *)
internal
fUsedLoad       : LREAL;
fUsedLoad_H     : LREAL;
fUsedLoad_C     : LREAL;
tpwmtimer       : LREAL:=0.0;
SaveDelay       : DINT:=-1;
FileErrId       : DINT;
refresh_H       : BOOL;
Unsaved         : BOOL;
bSavingParams   : BOOL:=FALSE; (* *)
bLoadParams     : BOOL:=FALSE; (* *)
FileErr         : BOOL:=FALSE; (* *)
END_STRUCT
END_TYPE
Parameter
Type
fPwmCycleTime
LREAL
The cycle time (in seconds) of the PWM signal generator.
fPwmMinOnTime
LREAL
The minimum switch-on component of the PWM signal. Range 0.1 to 1.0
fPwmMaxOnTime
LREAL
The maximum switch-on time from the PWM signal. Range 0.1 to 1.0
fPwmMaxOnC
LREAL
The maximum switch-on time of the cooling output from the PWM signal. If zero, the fPwmMaxOnTime is used. Range 0.1 to 1.0
fPwmMaxRampLoad
LREAL
reserved
fActSupplyLoad
LREAL
If a power measurement is performed, the current power can be read here.
fActSupplyCurrent
LREAL
If a power measurement is performed, the current currently measured can be read here.
fSupplyLoad
LREAL
The predicted total power of the supply line.
fSupplyMatch
LREAL
The ratio of fActSupplyLoad to fSupplyLoad.
nPwmFactorC
INT
The multiplier for the cooling PWM cycle time. Tpwm_cool := Tpwm_heat * nPwmFactorC.
fUsedLoad
LREAL
reserved
fUsedLoad_H
LREAL
reserved
fUsedLoad_C
LREAL
reserved
tpwmtimer
LREAL
Counter for the PWM cycles of the heating control.
SaveDelay
DINT
Memory delay in µs. After a time written to this variable by the application, the saving is triggered. (If the value is zero, the system is saved; if it is -1, the system is at rest; if the value is greater than zero, the system is saved after the time has elapsed)
FileErrId
DINT
In case of storage/loading of the zone, a coded information is provided here. However, only if saving and loading are performed via the machine and product parameters.
refresh_H
Trigger signals for heating and cooling PWM cycles.
Unsaved
Signals the application that parameters have changed from the library.
bSavingParams
Signals to the application that data are being saved.
bLoadParams
This flag triggers the saving of the parameters.
FileErr
In case of storage/charging of the zone, it is displayed here if the storage or charging process has failed.
The controller output is usually provided to the heating tape as a PWM signal. It is possible to provide a separate PWM configuration for each phase of a supply line.