FB_MTP_AlarmMgmt
FB_MTP_AlarmMgmt 1:
The function block FB_MTP_AlarmMgmt is an object used to describe, manage, and represent an alarm. It is described by the variables Message, Severity, and Acknowledge required, and has a state machine. In addition, an event is created for the TwinCAT Eventlogger during instantiation.
Initialization
Use the variable Message to specify the alarm message that should be displayed when an alarm is active.
You can specify the severity using the variable Severity. The value range is between 1 and 1000, with 1 representing the lowest severity.
Acknowledge required = TRUE states that the alarm must be acknowledged.
Use the variable OnDelay to specify the delay time (s) between the occurrence of an invalid state and the triggering of the alarm.
State machine
The function block has a state machine that corresponds to the IEC 62682 and has 4 main states: Normal, Unacknowledged alarm, Acknowledged alarm, and Return to normal unacknowledged.
In addition, there are 3 other states – Shelved, Suppressed, and Out of service– to temporarily disable the alarm. If this option is disabled, AlarmActive = FALSE and Acknowledge will be ignored.
If the input is ProcessAbnormal = TRUE, the Bit 1 of the output variable State is set to True after a start-up delay has elapsed. The start-up delay is set using the variable OnDelay.
If the alarm does not need to be acknowledged, the Alarm Acknowledged transition is set automatically.
FB_MTP_AlarmMgmt 2:
Synchronization of TwinCAT 3 event logger
Each function block FB_MTP_AlarmMgmt initializes an alarm in the TwinCAT 3 event logger. The event logger's alarm is synchronized with the main states of the alarm state machine.
By specifying a severity using the variable Severity, the alarm is assigned to an event class:
Severity
TwinCAT 3 event logger Event Class
001-200
Verbose
201-400
Info
401-600
Warning
601-800
Error
801-1000
Critical
The variable SourceName is used to store the name of the object associated with the alarm. The variable SourceID describes the alarm ID within the object to which the alarm belongs: for example, a pump (TagName = Pump) with 2 alarms, AlarmMgmt_Pump_Trip and AlarmMgmtSafePosAct:
<Pump> : FB_MTP_AnaDrv := (
    TagName := <Pump>,
    <initial values>);
<AlarmMgmt_Pump_Trip> : AlarmMgmt := (
    SourceName := <Pump>,
    SourceID   := <0>,
    <initial values>);
<AlarmMgmt_Pump_SafePosAct> : AlarmMgmt := (
    SourceID   := <1>,
    <initial values>);
Further properties
Name of the object
Object description
WQC
OSLevel
Implemented interfaces
I_MTP_AlarmMgmt
FB_MTP_AlarmMgmt 3: Inputs
Type
OPC UA access
TagName
STRING
Name of the interface
TagDescription
STRING
Description of the interface
WQC
BYTE
Worst Quality Code
Read
OSLevel
BYTE
Level must be defined for system. Value 0 is reserved for local operation.
Read/write
ProcessAbnormal
1: Process in invalid state
Message
STRING
Message to be displayed when the alarm is active.
Severity
INT
Alarm severity
Ackrequired
1: The alarm must be acknowledged.
0: The alarm does not need to be acknowledged.
Suppress
Unsuppress
SourceName
STRING
TagName of the object to which the alarm belongs.
SourceID
UDINT
Alarm ID
(Must be unique for each object.)
FB_MTP_AlarmMgmt 4: Outputs
Type
OPC UA access
State
BYTE
Bit-coded alarm status:
0: -
1: Alarm active
2: Acknowledged
3: Shelved
4: Suppressed
5: Out of service
6: -
7: -
Read
Internal variables
Type
OPC UA access
OnDelay
REAL
Time delay (s) between the occurrence of abnormal behavior and the setting of Alarm active
Read/write
Command
BYTE
Bit-encoded control words:
0: -
1: Acknowledge alarm
2: Shelve
3: Unshelve
4: Remove from Service
5: Return to service
6: -
7: -
Read/write
FB_MTP_AlarmMgmt 5: Methods
Type
GetAlarmState
E_MTP_AlarmState
Returns the current state of the finite-state machine.
IsAcknowledged
Returns the value of the bit Acknowledged from the status word.
IsAlarmActive
Returns the value of the bit IsAlarmActive from the status word.
IsOutOfService
Returns the value of the bit IsOutOfService from the status word.
IsShelved
Returns the value of the bit IsShelved from the status word.
IsSuppressed
Returns the value of the bit Suppressed from the status word.