FB_MTP_StringServParam
FB_MTP_StringServParam 1:
The function block FB_MTP_StringServParam is an object for string parameter value specifications from different sources: internal PLC logic and manual operation (e.g. via OPC UA). The values are managed via the state machines Service Mode.
The output value VOut corresponds to the current value specification limited to limit values and can be used within a service (see ParameterElements).
Applying values
Each parameter follows the same procedure when applying values. The values are applied in two steps:
  1. Preparing the value
  2. Applying of the value
The preparation of the value begins with the value specification via the variables VOp, VInt, VExt. Depending on the state of the Service Mode, a value is selected and limited via the value limit. The resulting requested value is displayed via the variable VReq.
To apply the value, the enabling is signaled on the PLC side via the variable ApplyEn = TRUE. The application can then be confirmed via variables ApplyOp, ApplyInt or ApplyExt, depending on the state of Service Mode. After successful application, the value of the variable VOut corresponds to the value of VReq.
FB_MTP_StringServParam 2:
Values can also be applied at service level using the same procedure. See the Parameters section at FB_MTP_ServiceControl.
Operation mode synchronization with higher-level service
The Service Mode of the parameter can be synchronized with the higher-level service via the variable Sync. The input variables for controlling the state machine are ignored and the state machine of the parameter automatically assumes the state of the Service Mode of the service.
FB_MTP_StringServParam 3:
Further characteristics
Name of the object
Object description
WQC
OSLevel
Service Mode
Read back
FB_MTP_StringServParam 4: Inputs
Type
OPC UA access
TagName
STRING
Name of the interface
TagDescription
STRING
Description of the interface
WQC
BYTE
Worst Quality Code
Read
OSLevel
BYTE
Level must be defined for system. Value 0 is reserved for local operation.
Read/write
VInt
STRING
Internal value specification (relevant if StateAutAct = TRUE and SrcIntAct = TRUE)
Read
VUnit
INT
Unit of value
Read
VMin
REAL
Upper limit of the value specification
Read
VMax
REAL
Lower limit of the value specification
Read
VFbk
REAL
Feedback value
Read
VSclMin
REAL
Scale start for value display
Read
VSclMax
REAL
Scale end for value display
Read
FB_MTP_StringServParam 5: Outputs
Type
OPC UA access
State*
Src*
See Service Mode
Vout
STRING
Current parameter value
Read
External variables
Type
OPC UA access
State*
Src*
See Service Mode
ApplyOp
Operator switching request to apply currently requested parameters (relevant if StateOpAct = TRUE):
1: Apply value.
0: Do not apply value
Read/write
ApplyExt
External switching request to apply currently requested parameters (relevant if SrcExtAct = TRUE and StateAutAct = TRUE):
1: Apply value.
Read/write
VOp
STRING
Operator value specification (relevant if StateOpAct = TRUE)
Read/write
VExt
STRING
External value specification (relevant if SrcExtAct = TRUE and StateAutAct = TRUE)
Read/write