FB_BA_MultiCalc_XX
The multi-calculation function blocks exist for the variable types LREAL and REAL, although they all have the same functionality.
The function block FB_BA_R08 is described as an example.
In enabled state (bEn=TRUE), the function block determines the following from the 8 input values r01...r08:
- the maximum value of all inputs rMax
- the input at which this maximum value occurs udiMinActv
- the minimum value of all inputs rMin
- the input at which this minimum value occurs udiMinActv
- the mean value of all inputs rAvrg
- the sum of all inputs rSum
- the difference between the maximum and minimum value rDiff
If not all inputs are used for the calculation, the number can be limited via an entry at udiNum: udiNum=6, for example, can be used to limit the calculations to inputs r01 to r06.
Any entry greater than 8 is automatically limited to 8, any entry less than 1 is automatically set to 1.
Sample:
Inputs | Output |
bEn = TRUE | rMax = 32 |
r01 = 32 | udiMaxActv = 1 |
r02 = 17 | rMin = 5 |
r03 = 5 | udiMinActv = 3 |
r04 = 9 | rAvrg = 18.5 |
r05 = 16 | rSum = 111 |
r06 = 32 | rDiff = 27 |
r07 = 25 |
r08 = 44 |
udiNum = 6 |
If bEn=FALSE, 0 is output at all outputs.
bEn : BOOL;
r01 : REAL;
r02 : REAL;
r03 : REAL;
r04 : REAL;
r05 : REAL;
r06 : REAL;
r07 : REAL;
r08 : REAL;
udiNum : UDINT;bEn: Activation of the block function.
r01...r08: Input values to be used for the calculation.
udiNum: Number of input values to be used for the calculation.
rMax : REAL;
udiMaxActv : UDINT;
rMin : REAL;
udiMinActv : UDINT;
rAvrg : REAL;
rSum : REAL;
rDiff : REAL;rMax: Maximum value of all inputs.
udiMaxActv: Input at which the maximum value is present.
rMin: Minimum value of all inputs.
udiMinActv: Input at which the minimum value is present.
rAvrg: Mean value of all inputs.
rSum: Sum of all inputs.
rDiff: Difference between maximum and minimum value.