FB_BA_Hys_03
FB_BA_Hys_03 1:
The template represents a sliding limit value monitoring with two switching points which, in contrast to FB_BA_Hys_02, are subject to switch-on and switch-off delays.
The switch-on and switch-off thresholds as well as the time delays are entered via analog objects.
FB_BA_Hys_03 2:
The initialization of the template takes place within the method FB_Init.
Block diagram
FB_BA_Hys_03 3:
FUNCTION_BLOCK FB_BA_Hys_03 EXTENDS FB_BA_View
  bEn                             : BOOL;
  fIn                             : REAL;
  bPresentValue                   : BOOL;
  bEvent                          : BOOL;
VAR_INPUT CONSTANT
  On                              : FB_BA_AV_Op;
  Off                             : FB_BA_AV_Op;
  DlyOn                           : FB_BA_AV_Op;
  DlyOff                          : FB_BA_AV_Op;
  Q                               : FB_BA_BV;
  Swi2P                           : FB_BA_Swi2P;
FB_BA_Hys_03 4: Inputs
Type
bEn
General enable of the function block.
fIn
REAL
Process value
FB_BA_Hys_03 5: Outputs
Type
bPresentValue
Output of the current state of the hysteresis function.
bEvent
Display of a fault or the BV object is active.
bEvent is only active if the property bEventDetectionEnable of the BV object was set to TRUE.
The monitoring of the binary feedback indicates a fault.
FB_BA_Hys_03 6: Inputs CONSTANT
Type
On
FB_BA_AV_Op
AV object for input of the upper limit of the hysteresis function.
Off
FB_BA_AV_Op
AV object for input of the lower limit of the hysteresis function.
DlyOn
FB_BA_AV_Op
AV object for entering the switch-on delay in seconds.
DlyOff
FB_BA_AV_Op
AV object for entering the switch-off delay in seconds.
Q
FB_BA_BV
The binary object indicates the current state of the hysteresis function.
Variables
Type
Swi2P
FB_BA_Swi2P
The function block Swi2P is the core of the hysteresis function.