FB_VenetianBlindEx1Switch
FB_VenetianBlindEx1Switch 1:
Blind function block with the same functionality as FB_VenetianBlindEx() but with an input bSwitch for jogging up and down.
Four different methods are available for controlling the blind:
The tSwitchOverDeadTime can be used to prevent damage to the drive motor caused by immediate changes in direction. In most cases, this value is between 0.5 s and 1.0 s. The drive manufacturer can give you a precise value.
Safety position
Travel to the safety position (e.g. because there is a strong wind or because maintenance is being carried out at the window) can be achieved by setting the bSafetyPosition input. The output bBlindUp is set and the output bBlindDown reset for the period specified by tDriveTime + 10%. Operation of the blinds is prevented for as long as the bSafetyPosition input is active.
Shading position
Under conditions of above-average sunshine, the blinds can be moved to the shading position. After applying a positive edge to the input bShadowPosition, the blind is moved to the position nShadowSetPosition. The blind is then moved upwards again for the period of time specified by tShadowTurnAroundTime. This prevents the room from being completely darkened. If the blind had moved upwards during the approach of the shading position, it is moved downwards for the time period tDriveSwitchOverTime - tShadowTurnAroundTime. The same angle will therefore be set as if the blind had been moved downwards for darkening purposes.
During a change of direction, a pause of duration tSwitchOverDeadTime is maintained. Travel to the shading position can be interrupted at any time by a new command.
Moving to an absolute position
Comments
In most cases a blind will not provide feedback about its current position. Therefore, this can only be calculated via the travel time. The precision depends on the uniformity of the blind speed. Furthermore, the speed differences between opening and closing should be as small as possible.
The positions are always specified in percent. 0% corresponds to fully up, 100% to fully down. If a value greater than 100 is specified, it will be limited to 100 within the function block.
Determining the parameters
First of all, certain blind parameters have to be determined. One parameter is the travel time. This is the time it takes for the blind to open or close fully. The second parameter is the time required for a change of direction. During a change of direction, the angle between the individual blades will change. The travel time is transferred to the parameter tDriveTime. The duration for a direction change is transferred to tDriveSwitchOverTime.
Referencing a function block
Since the current position of the blind has to be calculated, inaccuracies during operation will accumulate. In order to limit deviations, the function block will automatically reference itself as often as possible. This happens when the blind is moved fully up or down and the corresponding output is reset automatically. The corresponding time is tDriveTime + 10%.
bUp                    : BOOL;
bDown                  : BOOL;
bStop                  : BOOL;
bSwitch                : BOOL;
bStepUp                : BOOL;
bStepDown              : BOOL;
tStepTime              : TIME := t#200ms;
bPosition              : BOOL;
nSetPosition           : USINT;
bShadowPosition        : BOOL;
nShadowSetPosition     : USINT := 80;
tShadowTurnAroundTime  : TIME := t#0s;
bSafetyPosition        : BOOL;
tDriveTime          : TIME := t#60s;
tDriveSwitchOverTime   : TIME := t#200ms;
tSwitchOverDeadTime    : TIME := t#400ms;
bUp: Set the bBlindUp output and reset the bBlindDown output. The bBlindUp output remains latched.
bDown: Set the bBlindDown output and reset the bBlindUp output. The bBlindDown output remains latched.
bStop: Reset the bBlindUp and bBlindDown outputs.
bSwitch: Switching input for jogging the blind, see description above. Switches between moving, stopping, moving in the opposite direction, stopping and moving again. In each case the activated output immediately switches to latching.
bStepUp: Reset the bBlindDown output and set the bBlindUp output for the time tStepTime.
bStepDown: Reset the bBlindUp output and set the bBlindDown output for the time tStepTime.
tStepTime: If the blind is controlled through the bStepUp or bStepDown inputs, the outputs remain asserted for this period of time. The outputs are not set if the specified duration is 0.
bPosition: Move blind to specified position.
nSetPosition: Position (0%-100%) to which the blind is to be moved after a positive edge has been applied to input bPosition. 0% corresponds to fully up, 100% corresponds to fully down.
bShadowPosition: The shading position is approached.
nShadowSetPosition: Shading position (0%-100%) to which the blind is to be moved, after a positive edge has been applied to input bShadowPosition.
tShadowTurnAroundTime: Once the shading position has been reached, the blind is moved upwards for the period tShadowTurnAroundTime.
bSafetyPosition: The safety position is approached. To do this, the blind is moved upwards for the period tDriveTime + 10%. It is not possible to operate the blinds while this input is set.
tDriveTime: Travel time of the blind from fully up to fully down. If no input is activated, the outputs are reset after the period tDriveTime + 10%. The outputs are not automatically reset if the specified duration is 0. In this case, the blind cannot be moved to absolute positions.
tDriveSwitchOverTime: Period of time required for a change of direction of the blind.
tSwitchOverDeadTime: Dwell time at a change of direction. Both outputs are reset during this period.
bBlindUp           : BOOL;
bBlindDown         : BOOL;
nActualPosition    : USINT;
bCalibrated        : BOOL;
bBlindUp: The blind opens.
bBlindDown: The blind closes.
nActualPosition: Current position in percent.
bCalibrated: Indicates whether the blind is calibrated.
Development environment
Required PLC library
TwinCAT from v3.1.4020.32
Tc2_BABasic from v3.1.0.0
