Error Codes
udiErrorId | udiErrorId | Error |
0x0 | 0 | No error |
0x8001 | 32769 | FB_BARBlindPositionEntry: Values for lrSunElevation are not ascending or unequal |
0x8002 | 32770 | FB_BARBlindPositionEntry: Values for lrSunElevation are not within the valid range from 0°..90° |
0x8003 | 32771 | FB_BARBlindPositionEntry: Values for uiBlindPosition are not within the valid range from 0%..100% |
0x8004 | 32772 | FB_BARSunProtectionEx: The duration of the positioning interval is zero or exceeds 7200 s. |
0x8005 | 32773 | FB_BARSunProtectionEx: The longitude entered is not within the valid range from -180°..180°. |
0x8006 | 32774 | FB_BARSunProtectionEx: The latitude entered is not within the valid range from -90°..90°. |
0x8007 | 32775 | FB_BARSunProtectionEx: The value for the slat spacing (uiLouvreSpacing) is greater than or equal to the value for the slat width (uiLouvreWidth). |
0x8008 | 32776 | FB_BARSunProtectionEx: The "Values valid" bit (bValid) in the position table stBlindPositionTable is not set - invalid values, see FB_BARBlindPositionEntry. |
0x8009 | 32777 | FB_BARSunProtectionEx: The value entered for the fixed shutter height (uiFixedShutterHeight) exceeds 100% |
0x801A | 32778 | FB_BARSunProtectionEx: The value entered for the window height is zero |
0x801B | 32779 | FB_BARSunProtectionEx: The value entered for the slat spacing is zero |
0x801C | 32780 | FB_BARSunProtectionEx: The value entered for the slat width is zero |
0x801D | 32781 | FB_BARShadingObjectsEntry: The sum of the angles of the rectangle is not 360°. This means that the corners are not in the order P1, P2, P3 and P4 but rather P1, P3, P2 and P4. This results in a crossed-over rectangle. |
0x801E | 32782 | FB_BARShadingObjectsEntry: The corners of the square are not on the same level. |
0x801F | 32783 | FB_BARShadingObjectsEntry: The z-component of P1 is less than zero. This corner would thus lie behind the facade. |
0x8010 | 32784 | FB_BARShadingObjectsEntry: The z-component of P3 is less than zero. This corner would thus lie behind the facade. |
0x8011 | 32785 | FB_BARShadingObjectsEntry: P1 is equal to P2. The object entered is thus not a rectangle. |
0x8012 | 32786 | FB_BARShadingObjectsEntry: P1 is equal to P3. The object entered is thus not a rectangle. |
0x8013 | 32787 | FB_BARShadingObjectsEntry: P1 is equal to P4. The object entered is thus not a rectangle. |
0x8014 | 32788 | FB_BARShadingObjectsEntry: P2 is equal to P3. The object entered is thus not a rectangle. |
0x8015 | 32789 | FB_BARShadingObjectsEntry: P2 is equal to P4. The object entered is thus not a rectangle. |
0x8016 | 32790 | FB_BARShadingObjectsEntry: P3 is equal to P4. The object entered is thus not a rectangle. |
0x8017 | 32791 | FB_BARShadingObjectsEntry: The radius entered is zero |
0x8018 | 32792 | FB_BARShadingObjectsEntry: The z-component of the ball center is less than zero. This point would thus lie behind the facade. |
0x8019 | 32793 | FB_BARFacadeElementEntry: The group index is 0, but at the same time another entry of the facade element is not zero. Only if all entries of a facade element are zero is it considered to be a valid, deliberately omitted facade component, otherwise it is interpreted as an incorrect entry. |
0x801A | 32794 | FB_BARFacadeElementEntry: The X-component of the first corner (Corner1) is less than zero. |
0x801B | 32795 | FB_BARFacadeElementEntry: The Y-component of the first corner (Corner1) is less than zero. |
0x801C | 32796 | FB_BARFacadeElementEntry: The window width is less than or equal to zero. |
0x801D | 32797 | FB_BARFacadeElementEntry: The window height is less than or equal to zero. |
0x801E | 32798 | FB_BARDelayedHysteresis: The switch-on value bOnValue is smaller than the switch-off value bOffValue. |
0x801F | 32799 | FB_BARWithinRangeAzimuth: The beginning of the range lrBeginRange and the end of the range lrEndRange are the same. |
0x8020 | 32800 | FB_BARWithinRangeAzimuth: One of the range limits entered is greater than 360° or less than 0° |
0x8021 | 32801 | FB_BARWithinRangeAzimuth: The range entered is greater than 180°. |
0x8022 | 32802 | FB_BARWithinRangeElevation: The lower limit value lrLowLimit entered is greater than or equal to the upper limit value lrHighLimit. |
0x8023 | 32803 | FB_BARWithinRangeElevation: The upper limit value lrHighLimit is greater than 90° or the lower limit value lrLowLimit is less than 0°. |
0x8024 | 32804 | FB_BARShadingObjectsEntry: The number of the month when shading begins or when shading ends is zero or greater than 12. |
0x8025 | 32805 | FB_BARShadingObjectsEntry: Index error! iId lies outside the permissible limits 1..iShadingObjects. See list of shading elements. |
0x8026 | 32806 | FB_BARSunblindActuator/FB_BARSunblindActuatorEx: The shutter height entered is 0. |
0x8027 | 32807 | FB_BARSunblindActuator/FB_BARSunblindActuatorEx: The total "up" stroke time (uiTotalTimeUp/udiTotalTimeUp) or the total "down" stroke time (uiTotalTimeDown/udiTotalTimeDown) respectively is 0 ms. |
0x8028 | 30808 | FB_BARSunblindActuator/FB_BARSunblindActuatorEx: the slat "Up" turning time (uiTurningTimeUp) or the slat "Down" turning time (uiTurningTimeDown) is 0 ms. |
0x8029 | 32809 | FB_BARSunblindActuator/FB_BARSunblindActuatorEx: The upper slat angle limit value (iAngleLimitUp) is smaller than or equal to the lower slat angle limit value (iAngleLimitDown) |
0x802A | 32810 | FB_BARSunblindScene: The selected scene number exceeds the maximum number of 20. |
0x802B | 32811 | FB_BARSunblindThermoAutomatic: The preset room temperature values are in the wrong order. |
0x802C | 32812 | FB_BARSunblindThermoAutomatic: The brightness activation limit value is smaller than or equal to the deactivation limit value. |
0x802D | 32813 | FB_BARSunblindThermoAutomatic: The blind position (height in %) of the heating mode is greater than or equal to that of the cooling mode. |
0x802E | 32814 | FB_BARSunblindTwilightAutomatic: The brightness limit value for the activation of the automatic twilight function is greater than or equal to the deactivation value. |
0x802F | 32815 | FB_BARSunblindWeatherProtection: The frost limit value is greater than 10 °C. |
0x8030 | 32816 | FB_BARSunblindWeatherProtection: The limit value for the activation of the storm alarm is smaller than or equal to the deactivation value. |
0x8031 | 32817 | FB_BARSunblindWeatherProtection: The input of wind force limit values of less than 0 is not permissible. |
0x8032 | 32818 | FB_BARShadingCorrection / FB_BARShadingCorrectionSouth: The group index is 0. This index is intended only for facade elements that are to be marked as non-existent, for example if windows are omitted from an even facade grid or if a door is installed instead of a window. |
0x8033 | 32819 | FB_BARShadingCorrection / FB_BARShadingCorrectionSouth: A window element in the selected group is marked as invalid (bValid=FALSE). |
0x8034 | 32820 | FB_BARFacadeElementEntry: Index error! iColumn or iRow lies outside the permissible limits 1..iColumnsPerFacade or 1..iRowsPerFacade. respectively. |
0x8035 | 32821 | FB_BARSunProtectionEx: The façade inclination entered (lrFacadeAngle) is not within the valid range of -90°..90°. |
0x8036 | 32822 | FB_BARSunblindActuator/FB_BARSunblindActuatorEx: The time for extending the backlash (uiBacklashTimeUp) or (uiBacklashTimeDown) respectively is 0 ms. |
0x8037 | 32823 | FB_BARRollerBlind: The entire "Up" travel time (udiTotalTimeUp) or the total "Down" travel time (udiTotalTimeDown) is 0 ms. |
0x8038 | 32824 | FB_BARSMISunblindActuator: The value for wLouvreRange may not be 0. |
0x8039 | 32825 | FB_BARSMISunblindActuator: The ratio wLouvreRange / (iAngleLimitUp + iAngleLimitDown) must be greater than 0. |
0x803A.. | 32826.. | reserved for shading function blocks |
0x8100 | 33024 | FB_BARLightCircuit: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x8101 | 33025 | FB_BARLightCircuitDim: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x8102 | 33026 | FB_BARLightCircuitDim: The lower limit value, lrMinDimValue, is less than zero or greater than 100%. |
0x8103 | 33027 | FB_BARLightCircuitDim: The upper limit value, lrMaxDimValue, is less than zero or greater than 100%. |
0x8104 | 33028 | FB_BARLightCircuitDim: The lower limit value, lrMinDimValue, is greater than the upper limit value, lrMaxDimValue. |
0x8105 | 33029 | FB_BARLightCircuitDim: The value for "Manual On", lrManualDimValue, is less than zero or greater than 100%. |
0x8106 | 33030 | FB_BARAutomaticLight: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x8107 | 33031 | FB_BARAutomaticLight: The value for "Manual On", lrManualDimValue, is less than zero or greater than 100%. |
0x8108 | 33032 | FB_BARAutomaticLight: The light switch-on value, lrOnDimValue, is less than zero or greater than 100%. |
0x8109 | 33033 | FB_BARStairwellAutomatic: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x810A | 33034 | FB_BARTwilightAutomatic: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x810B | 33035 | FB_BARTwilightAutomatic: The value for "Manual On", lrManualDimValue, is less than zero or greater than 100%. |
0x810C | 33036 | FB_BARTwilightAutomatic: The ON value for the automatic function, lrDimOnValue, is less than zero or greater than 100%. |
0x810D | 33037 | FB_BARTwilightAutomatic: The OFF value for the automatic function, lrDimOffValue, is less than zero or greater than 100%. |
0x810E | 33038 | FB_BARTwilightAutomatic: The switch-on threshold value, uiSwitchOnValue, is greater than or equal to the switch-off threshold value, uiSwitchOffValue. |
0x810F | 33039 | FB_BARDaylightControl: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x8110 | 33040 | FB_BARConstantLightControl: The operation mode uiLightCtrlMode is greater than 2. However, only 0, 1 or 2 is permitted. |
0x8111 | 33041 | FB_BARConstantLightControl: The lower limit value, lrMinDimValue, is less than zero or greater than 100%. |
0x8112 | 33042 | FB_BARConstantLightControl: The upper limit value, lrMaxDimValue, is less than zero or greater than 100%. |
0x8113 | 33043 | FB_BARConstantLightControl: The lower limit value, lrMinDimValue, is greater than the upper limit value, lrMaxDimValue. |
0x8114 | 33044 | FB_BARConstantLightControl: The starting value of the controller, lrStartDimValue, is less than zero or greater than 100%. |
0x8115 | 33045 | FB_BARConstantLightControl: The value for "Manual On", lrManualDimValue, is less than zero or greater than 100%. |
0x8116.. | 33046.. | reserved for light function blocks |
0x8200 | 33280 | FB_BARPICtrl: The execution cycle number uiCtrlCycleCall is zero |
0x8201 | 33281 | FB_BARPICtrl: The proportional band rXp is zero. |
0x8202 | 33282 | FB_BARPICtrl: The lower control value limit value rYMin is greater than or equal to the upper limit value rYMax. |
0x8203 | 33283 | FB_BARPICtrl: The task cycle time tTaskCycleTime is set to 0. |
0x8204 | 33284 | FB_HVACOptimizedOn: The outside temperature values lrOutsideTemp[i] of the pre-start function stTempChangeFunction are not in ascending order or 2 values are the same. |
0x8205 | 33285 | FB_HVACOptimizedOn: One or more values of the room temperature change lrRoomTempChange[i] in the pre-start function stTempChangeFunction are higher than the upper limit value lrMaxTempChange. |
0x8206 | 33286 | FB_HVACOptimizedOn: One or more values of the room temperature change lrRoomTempChange[i] in the pre-start function stTempChangeFunction are lower than the lower limit value lrMinTempChange. |
0x8207 | 33287 | FB_HVACOptimizedOn: The control input eCtrlFct is set neither to heating nor to cooling mode (eBARCtrlFct_Heating or eBARCtrlFct_Cooling). |
0x8208 | 33288 | FB_HVACOptimizedOff: The outside temperature values lrOutsideTemp[i] of the pre-start function stTempChangeFunction are not in ascending order or 2 values are the same. |
0x8209 | 33289 | FB_HVACOptimizedOff: One or more values of the room temperature change lrRoomTempChange[i] in the pre-start function stTempChangeFunction are higher than the upper limit value lrMaxTempChange. |
0x820A | 33290 | FB_HVACOptimizedOff: One or more values of the room temperature change lrRoomTempChange[i] in the pre-start function stTempChangeFunction are lower than the lower limit value lrMinTempChange. |
0x820B | 33291 | FB_HVACOptimizedOff: The control input eCtrlFct is set neither to heating nor to cooling mode (eBARCtrlFct_Heating or eBARCtrlFct_Cooling). |
0x820C | 33292 | FB_HVACTempChangeFunctionEntry: The outside temperature values lrOutsideTemp[i] of the pre-start function stTempChangeFunction are not in ascending order or 2 values are the same. |
0x8C00.. | 35840.. | See SMI error codes Subtract the value 0x0C00 from the error code to obtain the SMI-specific error code. |
Development environment | required library | required function |
TwinCAT 3.1 build 4022.16 or higher | Tc2_HVAC V3.3.1.0 | TF8000 | TC3 HVAC V1.0.0.0 |
