FB_MBUdpWriteSingleReg (Modbus function 6)
This function is used to write to a single output register. 16 bit access is used.
sIPAddr : STRING(15);
nTCPPort : UINT:= MODBUS_TCP_PORT;
nUnitID : BYTE:=16#FF;
nMBAddr : WORD;
nValue : WORD;
bExecute : BOOL;
tTimeout : TIME;
END_VAR Name | Type | Description |
sIPAddr | STRING (15) | Is a string containing the IP address of the target device. |
nTCPPort | UINT | Port number of the target device. |
nUnitID | BYTE | Identification number of a serial sub-network device. If a device is addressed directly via TCP/IP, this value must be 16#FF. |
nMBAddr | WORD | Address of the output register (word offset). |
nValue | WORD | Value to be written to the register (data word). |
bExecute | BOOL | The function block is enabled by a rising edge at this input. |
tTimeout | TIME | States the length of the timeout that may not be exceeded by execution of the ADS command. |
Outputs
bBUSY : BOOL;
nErrId : UDINT;
bBusy | BOOL | When the function block is enabled, this output is set and remains set until a feedback is received. |
bError | BOOL | If an ADS error should occur during the transfer of the command, then this output is set once the bBusy output is reset. |
nErrId | UDINT | Returns the ADS error number when the bError output is set. |
TwinCAT v3.1.0 | IPC or CX (x86, x64, ARM®) | Tc2_ModbusSrv |
