Receiving data from I/O-Task
As mentioned bfore, the OPC-Server gives the possibility to read/write process values from ADS devices and therefore also from the TwinCAT I/O.
The following steps need to be taken to make an I/O task available via OPC:
- Step 1: Configuration of I/O Task
- Step 2: Configuration of the OPC-Server (one-time step)
Step 1: Configuration of I/O-Task
To make an I/O Task available via OPC, please open the TwinCAT Solution and navigate to "SYSTEM" - "Tasks" - "TaskName".
Activate the checkbox "Create Symbols" .
In the second step you need to configure the OPC-Server. This is a one-time configuration.
Start TwinCAT-OPC-Configurator "Start \ All Programs\ Beckhoff \ TwinCat3 Functions \ TF6120 OPC-DA"
In the left navigation tree please select "I/O Devices" with a right click the menu item "New".
Enter a name for that ADS device in field "Name". The name has to be OPC conform. Special characters are not allowed. The device-name will be part of the ItemID later. Sample: TwinCAT-PLC was defined with a variable "Temp". Choosing the devicename as "IO1" the opc-server present the variable as "IO1.Temp". With click on "OK" we get the new dialog for further settings of device :
The following table gives an overview about all possible settings:
Parameter | Beschreibung |
Name | Name of Name device, e.g. IO1. This will be the name under which the device will be accessible for the OPC-Client. |
Description [optional] | Optional description for the device. |
AutoCfg | 5 : Get symbolic via ADS |
AutoCfgSymFile | Not needed in this case. |
AdsPort | ADS port number of device, e.g. 351 for I/O Task |
AdsNetId [optional] | Address of the ADS device. By default this is 0.0.0.0.0.0 for local system. |
AdsTimeout [optional] | Timeout for ADS connection to the device, measured in [ms]. If the device is not reachable within that timeframe, the OPC-Server returns BAD_QUALITY to the OPC-Client. |
AdsTimeSuspend [optional] | Suspend time for the ADS device, measured in [ms]. If the ADS connection breaks, the OPC-Server waits this time before sending the next ADS request to the runtime. |
Disable [optional] | Deactivates the device. |
Save the configuration via "File" --> "Save As". After the configuration has been saved, you will be asked if this configuration should be set as the startup-configuration.
The configuration will be automatically activated on next restart of the OPC-Server.
![]() | Apply settings If you have activated a configuration and the OPC-Server does not seem to apply the settings, please make sure that the OPC-Server has been stopped and started once. |