MC_CamTableSelect
This function block selects the cam table. Internally the function block calls CamObject.Connect() if the cam object is linked to an existing cam table object, otherwise CamObject.Create(), and CamObject.Construct() are called based on CamRef data.
Definition:
FUNCTION_BLOCK MC_CamTableSelect
CamObject : Reference To MC_CamObject;
CamRef : MC_CAM_REF;
Execute : BOOL;
Periodic : BOOL;
ContinuityRequirement : EContinuity;
Done : BOOL;
Busy : BOOL;
Error : BOOL;
ErrorId : UDINT;
Name | Type | Default | Description |
CamRef |
| Data point information. | |
Execute | BOOL |
| Start cam select at rising edge. |
Periodic | BOOL |
| Set to TRUE for a periodic cam table. |
ContinuityRequirement |
| Minimum continuity requirement. The higher the requirement, the stricter the point validation. | |
Name | STRING(80) | "" | Only applicable if the cam object is not linked and creation of a new cam table object is required. |
Outputs
Name |
Type |
Description |
Done |
BOOL |
Selection succeeded |
Busy |
BOOL |
Function block is not finished and new output values are to be expected. |
Error |
BOOL |
Error occurred within function block. |
ErrorId |
UDINT |
Error identifier |
Possible error codes
For this function block, the following values, among others, are possible for the ErrorId output:
Error(Hex) | Error(Dec) | Error type | Description |
0x8145 | 33093 | Function Block | Mapping of cyclic interface between NC and PLC is missing (e.g., AXIS_REF, AXES_GROUP_REF, ...). A reference used by the function block (e.g., to an axis, group, mover or other motion object) is not linked to the corresponding NC object, or its cyclic mapping is incomplete. |
0x8169 | 33129 | Function Block | Master axis does not exist or cannot be used. The axis passed as master does not exist or has no cyclic mapping and therefore cannot be used as master (e.g., for camming or gearing). |
0x81af | 33199 | Function Block | Invalid object or object reference passed to function block. An invalid or missing object reference was passed to the function block (e.g., missing CamObject reference on MC_CamIn, MC_CamTableSelect or MC_CamScaling). |
0x81b0 | 33200 | Function Block | Object not allowed (e.g., object is already in use). The supplied object is not allowed in the current context (e.g., source and target are identical in CopyFrom(), the object is already used by another axis). |
0x81b1 | 33201 | Function Block | Invalid size passed to function block (e.g., invalid array size or invalid number of elements). An invalid size was passed to the function block (e.g., CamRef.NumberOfPoints less than two on MC_CamTableSelect). |
0x81b2 | 33202 | Function Block | The given cam activation settings are invalid. The activation settings of the cam table (e.g., ActivationMode and ActivationPosition) are invalid or inconsistent. |
0x81b3 | 33203 | Function Block | The given cam scaling is invalid. The supplied cam table scaling parameters are invalid (e.g., scale factor of zero, or master offset mode Auto which is not supported in the executed operation). |
0x81b4 | 33204 | Function Block | The given cam data point is invalid. At least one data point of the cam table is invalid (e.g., the first or last point is being ignored). |
0x81c2 | 33218 | State | A queued cam command could not be transitioned from queued to active. An error occurred while transitioning a queued cam command (e.g. MC_CamIn, MC_CamAdd, MC_CamExchange, MC_CamScaling or MC_CamRemove) to the active state. This typically happens when the camming state changed between queuing and activation, for example because the referenced cam table is already coupled or no longer coupled, or because the setpoint or activation time could not be computed. |
An overview of all NC error codes can be found here:
Version information
- TwinCAT Standard >= v3.1.4026.23.1
- TF5550 MC3 Camming >= v4.0.6 (includes TF5500 MC3 Base >= v4.0.6)
Required License
TC3 MC3 Camming
