Data Area
In general, TcCOM objects can contain data areas that can be used by the environment (e.g., by a PLC instance or by the TwinCAT I/O area). For TwinCAT MC3 TcCOM objects, you have a choice of data structures to use via the Data Area tab.
PulseTrain Drive / PulseTrain Inputs
Enable (default)
Type
Data Area 1:
WcState
BIT
Working counter
Data Area 2:
InputToggle
BIT
Level change upon receipt of a new telegram
Data Area 3:
Counter value
UDINT
Meter reading
Data Area 4:
ENC Sync error
BIT
The Sync error bit is required only for distributed clocks mode and indicates whether a synchronization error occurred during the previous cycle.
Data Area 5:
ENC TxPDO State
BIT
Validity of the data in the associated TxPDO (0=valid, 1=invalid).
Data Area 6:
ENC TxPDO Toggle
BIT
The TxPDO toggle is set by the slave when the data in the corresponding TxPDO has been updated.
Data Area 7:
DcInputShift
DINT
Used for dead-time compensation of the drive.
Data Area 8:
DcOutputShift
DINT
PulseTrain Drive / PulseTrain Outputs
Enable (default)
Type
Data Area 9:
PTO Automatic direction
BIT
The terminal selects the direction of travel based on the position difference (actual and target values) in such a way that the shorter distance is preferred.
Data Area 10:
Target counter value
UDINT
Target meter reading
Notice
Warning in the error log window caused by selected entries that are not linked to an I/O device
Entries in the data areas of drive and encoder objects that are enabled (Enable = True) but are not linked to the I/O drive object result in a warning in the error log window. If the link for a function used at runtime is missing, this results in a runtime error. For example, an axis cannot be started if the status word from the I/O drive object is not linked.
  • Link the required entries for the interface between the axis and the I/O device
  • Deselect the entry that is not required to avoid generating a warning.