Init Parameter
General
Homing Position
Default value
Unit
Type
Homing Position
0.0
[PosUnit]
LREAL
The parameter Homing Position defines the absolute reference position. The axis is set to this position after a successful homing procedure. This parameter has an effect when the value #Default is used for the reference position input in the command to start a homing procedure (e.g., MC_Home).
Sequence
A homing process has several phases. The following parameters can be used to enable and configure individual phases.
Move to Fixed Stop Enabled
Default value
Unit
Type
FALSE
Move to Fixed Stop Distance
10.0
[PosUnit]
LREAL
Move to Fixed Stop Velocity
30.0
[PosUnit]/s
LREAL
Torque Limit
30.0
LREAL
Enabling the Move To Fixed Stop Enabled parameter (value: TRUE) adds a sequence in the form of an axis movement to the initialization process.
Move from Fixed Stop Enabled
Default value
Unit
Type
FALSE
Move from Fixed Stop Velocity
30.0
[PosUnit]/s
LINT
Enabling the Move From Fixed Stop Enabled parameter (value: TRUE) adds a sequence in the form of an axis movement to the initialization process. The axis continues to move until the force/torque level falls below the expected threshold again.
Move to Sync Enabled
Default value
Unit
Type
FALSE
Move to Sync Distance
10.0
[PosUnit]
LREAL
Move to Sync Velocity
30.0
[PosUnit]/s
LREAL
Move to Sync Source
ZeroImpulseCoE
MC.EHomingSyncSource
Move to Sync Edge
Positive
MC.ETouchProbeTriggerSource
Enabling the Move To Sync Enabled parameter (value: TRUE) adds a sequence in the form of an axis movement to the initialization process. The axis continues to move until a configured event is detected in touch probe unit 1 of the drive. The touch probe unit can be activated for the homing process using the parameter Move To Sync Source. In the cyclic interface (Data Area tab) between the axis or the subordinate drive object and the I/O device, the touch probe unit must be added and linked (it is recommended to configure the touch probe unit using Drive Manager 2).
Move to Initial Position Enabled
Default value
Unit
Type
FALSE
10.0
[PosUnit]
LREAL
Move to Initial Position Velocity
30.0
[PosUnit]/s
LREAL
Optionally, a homing process can be completed with a movement to an absolute target position if the parameter Move To Initial Point Enabled is set to TRUE.
Init Parameter 1:
View of subordinate objects
Depending on the Show Hidden Children setting in the context menu of an overlying parent object, child objects are hidden. Parameters and data areas of the child object are visible in the parent object when this setting is disabled.
  • To display child objects, right-click the parent object (context menu) > and click Show Hidden Children.
The following parameters originate from the nested Touch Probe object.
Detection Thresholds
Default value
Unit
Type
Torque/Force Threshold
10.0
LREAL
Velocity Threshold
10.0
[PosUnit]/s
LREAL
Lag Threshold
2.0
[PosUnit]
LREAL
Threshold value for the actual motor torque value. If the torque exceeds this value during evaluation, this serves as an indicator that a hard stop has been detected. The value #Ignore disables this threshold.
Velocity Threshold
Threshold value for the actual axis velocity during evaluation. The power/torque threshold is evaluated only if the actual velocity is below this threshold value. The value #Ignore disables this threshold.
Lag Threshold
Threshold value for the position lag. If the actual position lag exceeds this value during evaluation, this serves as an indicator that a hard stop has been detected. The value #Ignore disables this threshold.
Init Parameter 2:
Disabling all thresholds
If all thresholds are disabled, the module immediately reports a detected event. In the case of homing, this is instantly recognized as the encoder having reached the end stop.
  • Enter at least a real number for the torque/force threshold or position lag threshold to enable hard stop detection.
Init Parameter 3:
Behavior of an accelerating axis with a velocity threshold
If, for example, the axis accelerates from a standstill and the touch probe module's evaluation is already active, the axis's velocity may still be below the set threshold value. Depending on the other threshold values, this may cause the touch probe module to report a detected event. In the case of homing, this can be detected as reaching the end stop.
  • If necessary, start an axis movement before activating the touch probe unit.