Init Parameter
General
Default value
Unit
Type
Control Value Type
Velocity
MC.EControlValueType
Enabled
TRUE
Velocity Feed-Forward Factor
1.0
LREAL
Control Value Type
Specifies the type of the controller's output variable. For example, Velocity means that the controller output is a velocity.
Enabled
Enabled indicates whether the position controller is being used or not. The controller output is 0.0 when it is disabled.
The product of Velocity Feed Forward Factor and the velocity setpoint is added to the sum of P, I, and D to produce the controlled variable.
Control Parameter
Default value
Unit
Type
Proportional Gain (Kp)
1.0
[ControlVariableUnit] / [PosUnit]
LREAL
Derivative Gain (Kd)
0.0
[ControlVariableUnit]/ ([PosUnit] / s)
LREAL
Integral Gain (AI)
0.0
[ControlVariableUnit] / ([PosUnit] * s)
LREAL
Integrator Threshold Minimum Velocity
#Ignore
[PosUnit]/s
LREAL
Integrator Threshold Maximum Velocity
#Ignore
[PosUnit]/s
LREAL
Integrator Lag Window Minimum
#Ignore
[PosUnit]
LREAL
Integrator Lag Window Maximum
#Ignore
[PosUnit]
LREAL
The proportional gain (Kp) is multiplied by the current control error, resulting in a term in the controlled variable.
The derived gain (Kd) is multiplied by the derivative of the error, resulting in a term in the controlled variable.
Integral Gain (AI)
The integral gain (Ki) is multiplied by the integral of the control error, resulting in a term in the controlled variable.
The integrator does not change if the actual velocity is less than the minimum velocity. The minimum velocity must be less than or equal to 0.0.
Integrator Threshold Minimum Velocity ≤ 0,0
The integrator does not change if the current velocity is greater than the maximum velocity. The maximum velocity must be greater than 0.0.
Integrator Threshold Maximum Velocity > 0,0
The integrator does not change if the actual delay falls outside this interval. The value for the integrator's minimum delay must be greater than 0.0.
Integrator Lag Window Minimum > 0,0
The integrator does not change if the actual delay falls outside this interval. The value for the integrator's maximum delay must be greater than the minimum delay.
Integrator Lag Window Maximum > Integrator Lag Window Minimum
Output Limitation
Default value
Unit
Type
Integrator Minimum Output
#Ignore
LREAL
Integrator Maximum Output
#Ignore
LREAL
Minimum output
#Ignore
LREAL
Maximum output
#Ignore
LREAL
Minimum output of the integrator. The value Integrator Minimum Output must be less than or equal to the value Integrator Maximum Output.
Maximum output of the integrator. The Integrator Maximum Output value must be greater than or equal to the Integrator Minimum Output value.
Minimum output
Minimum output of the controller. The Minimum Output value must be less than or equal to the Maximum Output value.
Maximum output
Maximum output of the controller. The Maximum Output value must be greater than or equal to the Minimum Output value.
