Parameters
Required input parameters
Cycle parameters
@P6
Measurement path in the direction of the negative Z axis, only positive values permitted
@P87
Diameter of sphere
Optional input parameters
Cycle parameters
@P13
Safety clearance for pre-positioning
Default value = diameter of touch probe
@P14
Probe angle of the first lateral measurement in relation to the positive X axis [degrees]
Default value = 0
@P15
Difference of the probe angle between the lateral measurements [degrees]
Default value = 90
@P33
Crossover range during measurement process
Additional motion path that exceeds the expected workpiece edge/workpiece surface
Default value = @P87/4 (calibration at sphere)
@P64
Definition of the path to approach to pre-position
0: linear (default value)
1: circular
@P86
Z reference of top sphere edge. If parameters are specified, the length of the touch probe is modified.
@P88
Measurement repetition with calculated parameters at height of equator for enhanced accuracy
1: yes
2: no (default value)
Notice
If circular approach of the pre-position was selected in @P64, collision detection is disabled. This option may only be enabled if safe approach to the pre-position is ensured.
It is recommended to use the Syntax check to verify whether the input parameters are correctly assigned.
Logging
The logging function is enabled for this cycle.