Acceleration feedforward control
Configuration
To apply acceleration feedforward control, first configure acceleration feedforward control in P-AXIS-00223 and the output of the acceleration feedforward control value as an additive command value:
ration feedforward
#0x200: Output as additive
torque command value
In addition, configure the additive torque/current command values in the cyclic process data:
![]() | If the output of acceleration feedforward control is activated as an additive command value and no additive torque/current command value is configured in the cyclic process data, the error message ID 70351 is output. |
Torque calculation
With acceleration feedforward control using an additive torque or an additive current command value, the required motor torque is calculated by the equation below.
M = Jtot*a
or
F = mtot*a
This torque is rescaled to the format used by the motor and then output to the drive.
Since specific knowledge of the mechanical structure of the axis is required to calculate angular acceleration, it is advisable to configure the path resolution of the axis by specifying the parameters P-AXIS-00092, P-AXIS-00233, P-AXIS-00234, and P-AXIS-00362 and P-AXIS-00363.
If a value unequal to 1 is assigned to one of the two parameters P-AXIS-00362 and P-AXIS-00363, the path resolution is calculated by the equation:
Parameter set
The following parameter set results for an axis with a motor encoder resolution of 220 increments per revolution, a gearbox ratio of 3 and a spindle pitch of 5 mm/rev:
per revolution
antr.feed_const_denom 1
getriebe[0].incr_per_rev 1048576 #2**20 increments per motor revolution
getriebe[0].gear_fact_num 3 #gearbox ratio: input revolutions
getriebe[0].gear_fact_denom 1 #gearbox ratio:
output revolutions
A further parameter requires the total motor load (Jtot).
Jtot consists of:
- Total of motor moments of inertia and
- load torque referred to the motor shaft.
Enter the resulting value in the parameter P-AXIS-00391 in the unit kg*m2.
0.48 kg*m**2
The required motor torque can be calculated using the parameters now available. The following parameters are also required to calculate the torque/current command value output to the drive:
- Motor nominal torque as reference value for torque scaling in P-AXIS-00392.
- Torque scaling factor in the parameters P-AXIS-00325 and P-AXIS-00326.
The value for P-AXIS-00392 is contained in the motor data sheet:
Enter the value which must be output as additive torque command value for the parameters P-AXIS-00325 and P-AXIS-00326 so that the motor outputs its nominal torque. This value depends on the torque scaling used in the drive.
For example, if a percentage weighting is used in 0.1% referred to the maximum current of the drive amplifier, the following results for a maximum current of 3.16 A and a nominal current of 1.58 A for the parameters P-AXIS-00325 and P-AXIS-00326:
P-AXIS-00325/P-AXIS-00326 = 1,58A/3,16A * 1000 = 500
The possible values for P-AXIS-00325 and P-AXIS-00326 would then be, for example:
antr.torque_scale_denom 1
In addition, the output of the acceleration feedforward value can still be delayed in relation to the position command value; this delay can be set by the P-AXIS-00390 parameter.
![]() | The maximum delay time that can be set is one position controller cycle. If a longer delay time is parameterised, the error message ID 70348 is output and the delay time is set to 0. |
The feedforward value to be output can be weighted by the parameters P-AXIS-00225 and P-AXIS-00226. In the following example the feedforward value is 1.2.
vorsteuer.vs_a_nenner 10 # Weighting acceleration feedforward denominator
The resulting parameter set is therefore:
ration feedforward
antr.feed_const_num 50000 #feedconstant 5mm per revolution
antr.feed_const_denom 1 #
getriebe[].incr_per_rev 1048576 #2**20 increments
getriebe[].wegaufz 3 #gearbox ratio:
input revolutions
getriebe[].wegaufn 1 #gearbox ratio:
output revolutions
antr.acc_reference_value 0.45 #stall torque in Nm
antr.torque_scale_num 500
vorsteuer.acceleration_delay_time 150 # Delay accele-
ration feedforward
against
# position
command value in us
vorsteuer.vs_a_faktor 12 # Weighting acceleration feedforward numerator