Overview
ID
Parameter
P-AXIS-00230
lr_hw[i].vz_istw
Sign reversal of actual sensor values
P-AXIS-00328
lr_param.distance_control_on
Enabling of distance control
P-AXIS-00413
kenngr. dist_ctrl[i].n_cycles
Smoothing of sensor data
P-AXIS-00414
kenngr.dist_ctrl[i].max_deviation
Maximum position offset [0.1 µm]
P-AXIS-00415
kenngr. dist_ctrl[i].v_max
Maximum permissible velocity for distance control [µm/s]
P-AXIS-00416
kenngr. dist_ctrl[i].a_max
Maximum permissible acceleration for distance control [mm/s^2]
P-AXIS-00417
kenngr. dist_ctrl[i].max_act_value_change
Maximum permissible change speed of measured distance [0.1 µm/cycle]
P-AXIS-00418
kenngr. dist_ctrl[i].ref_offset
Offset to reference point
P-AXIS-00419
kenngr. dist_ctrl[i].max_pos
Upper limit of sensor
P-AXIS-00420
kenngr. dist_ctrl[i].min_pos
Lower limit of sensor
P-AXIS-00421
kenngr. dist_ctrl[i].tolerance
Tolerance band
P-AXIS-00422
lr_hw[i].encoder_resolution_num
Resolution of the sensor measuring system (numerator) [increments]
P-AXIS-00423
lr_hw[i].encoder_resolution_denom
Resolution of the sensor measuring system (denominator) [0.1 µm]
P-AXIS-00424
lr_hw[i].mode_act_pos
Definition of the sensor value range: Linear scale or modulo handling of sensor values
P-AXIS-00428
kenngr. dist_ctrl[i]. check_sw_limit_switch
Consideration of the calculated offset of distance control in software limit switch monitoring
P-AXIS-00500
mode_dist_use_both_encoder
Option: distance sensor and motor encoder
P-AXIS-00501
use_adaptive_acceleration
Option: weighting of acceleration as a function of distance deviation.
P-AXIS-00502
kenngr. dist_ctrl[i].a_min
P-AXIS-00504
kenngr. dist_ctrl[i].dist_error_a_min
P-AXIS-00505
kenngr. dist_ctrl[i].dist_error_a_max
P-AXIS-00507
kenngr. dist_ctrl[i].low_pass_filter_order
P-AXIS-00508
kenngr. dist_ctrl[i].low_pass_filter_fg_f0
P-AXIS-00509
kenngr. dist_ctrl[i].optimized_scheduling
Option: dead time reduction
P-AXIS-00533
kenngr. dist_ctrl[i].v_weight_down
Option: dynamic weighting for the lowering movement
P-AXIS-00534
kenngr. dist_ctrl[i].a_weight_down
P-AXIS-00759
kenngr. dist_ctrl[i].kp
Weighting the distance control output values
P-AXIS-00764
kenngr. dist_ctrl[i].i_tn
Integral action time of the PID controller
P-AXIS-00765
kenngr. dist_ctrl[i].d_tv
Derivative action time of the PID controller
P-AXIS-00782
kenngr. dist_ctrl[i].filter_type
P-AXIS-00783
kenngr. dist_ctrl[i].kalman_sigma
P-AXIS-00784
kenngr. dist_ctrl[i].smoothing_factor
P-AXIS-00868
kenngr.dist_ctrl[i].window
Tolerance window in which the control deviation must be in order to fulfil the waiting condition.
P-AXIS-00869
kenngr.dist_ctrl[i].cycles_in_window
Number of cycles that the control deviation must remain within the tolerance window in order to fulfil the waiting condition.
P-AXIS-00870
kenngr.dist_ctrl[i].max_wait_time
Maximum permissible waiting time to fulfil the waiting condition