ID 70615
With negative axis velocity the actual position of modulo axis is out of range of the software limit switches.
The current position of the modulo axis with a negative velocity has reached an invalid range defined by the software limit switches.
This error only occurs if a software limit switch is shifted to a value outside the modulo range by the specified tolerance. See figure:
ID 70615 1:
Possible causes:
  • Incorrect the NC program
  • Axis oscillations are too large.
For further information, see [FCT-A2// Description]
Response
Class
7
Controlled halt of the axis, the control loop is closed.
Solution
Class
6
Possible solutions:
  • Check and correct the NC program
  • Check the gain factor (P-AXIS-00099) to reduce axis oscillations
  • Check and increase the tolerance P-AXIS-00179
Parameter
%1:
Logical axis number [-]
Logical axis number P-AXIS-00016 of axis affected
%2:
Current value [0.1 10^-3 mm or ø]
Current actual position of the axis
%3:
Lower limit value [0.1 10^-3 mm or ø]
Lower limit of the invalid modulo range defined by the software limit switches
%4:
Configured tolerance P-AXIS-00179 of the software limit switch
%5:
Block number [-]
Block number of the NC program where the error occurred.
Error type