ID 110541
Coarsening of encoder resolution requires drive command/actual values without modulo treatment. | ||||
Description | The axis parameter P-AXIS-00405 can be used to coarsen the encoder resolution of the drive. However, this requires drive command values and actual values for which no upper module calculation is performed (see P-AXIS-00122, P-AXIS-00123). | |||
Response | Class | 1 | Warning, parameter P-AXIS-00405 is set to zero. | |
Solution | Class | 1 | Correct parameter P-AXIS-00405. Check if the drive supports a linear coordinate system. | |
Logical axis number P-AXIS-00016 of axis affected | ||||
%2: | Incorrect value [-] | |||
Incorrect value for coarsening factor P-AXIS-00405 | ||||
%3: | Current value [-] | |||
Normalisation of drive command position P-AXIS-00122 | ||||
%4: | Current value [-] | |||
Normalisation of drive actual position P-AXIS-00123 | ||||
%5: | Corrected value [-] | |||
Corrected value for coarsening factor P-AXIS-00405 | ||||
Error type | 2, Error message on data transfer of parameter lists to controller. | |||