ID 70249
Invalid resolution of slave axis for cross compensation. | ||||
Description | Compensation values for cross compensation were specified in increments in the associated compensation value list. This is only permitted for a measuring system path resolution of one (see P-AXIS-00234, P-AXIS-00233). However, the slave axis to be compensated uses a path resolution unequal to one.
See: [COMP// Section: Cross compensation]] [FCT-C5// Section: Cross compensation] | |||
Response | Class | 7 | Closed-loop controlled axis stop. The cross compensation is turned off for affected axis | |
Solution | Class | 7 | Change the value of parameter P-COMP-00003 in the compensation value list to one and enter the compensation values metrically (in 0.1 µm). | |
Logical axis number of the affected slave axis see P-AXIS-00016 | ||||
%2: | Error value [-] | |||
Path resolution of measuring system of slave axis, see P-AXIS-00233, P-AXIS-00234 | ||||
%3: | Expected value [-] | |||
Expected path resolution of the measuring system, see P-AXIS-00233, P-AXIS-00234 | ||||
Error type | 11, Error message from position controller. | |||