Measurement methods (P-AXIS-00516)
P-AXIS-00516
Measurement methods
The parameter defines the source of the probing signal during a measuring travel, e.g. the probing position can be latched in the drive or the probing signal can be provided by the PLC. The probing signal source can also be changed in the NC program with the #MEAS command ([[PROG//Extended programming]).
This parameter replaces the following old configuration parameters:
  • kenngr.mess_signal_taster (P-AXIS-00117)
  • kenngr.mess_signal_sercos (P-AXIS-00116)
  • kenngr.mess_signal_achs_steuer (P-AXIS-00115)
  • kenngr.probing_signal_via_plc (P-AXIS-00257)
  • kenngr.meas_signal_drive (P-AXIS-00269)
  • kenngr.meas_signal_fixed_stop (P-AXIS-00330)
Parameter
kenngr.measure.signal
Data type
STRING
Data range
DRIVE_TYPE_DEFAULT
PLC
FIXED_STOP
DRIVE
PLC_EXT_LATCH_CONTROL
PLC_FIRST_EVENT
PLC_TIMESTAMP
EXT_PROBE_WITH_DRIVE (as of V3.1.3080.05)
PLC_EXT_LATCH_CONTROL_TIMESTAMP (as of V3.1.3132.0)
Axis types
T, R, S
Dimension
T: ----
R,S: ----
Default value
Drive types
Remarks
If the parameter P-AXIS-00516 is not defined, the measurement method resulting from previous parameters is used for backward compatibility reasons.
* Note: The default value of variables is a blank string.
The meaning of the parameter settings is described in the following table:
Value
Meaning
DRIVE_TYPE_DEFAULT
The CNC uses the default measuring method of the given drive type (see table below /*/)
PLC
With this parameter setting, the probing signal is read by the lr_mc_control.probing_signal control unit on the [HLI]. The probed value is the actual value at the moment when the probing signal occurred. As an alternative, the probing position can be specified explicitly by the lr_mc_control.probing_position control unit
NOTE:
Due to the scanning of the probing signal in the cycle time of the PLC, the accuracy of the probed value is less than the accuracy achieved by using drive-internal probing latches.
This setting corresponds to the old parameter kenngr.probing_signal_via_plc (P-AXIS-00257).
FIXED_STOP
This setting searches for a fixed stop during a measurement run. In addition the measuring type 7 (see P-CHAN-00057) must be selected.
CAUTION:
The user must ensure that, during the Move to fixed stop function in the drives affected, a torque limitation is active and the speed is low enough.
This setting corresponds to the old parameter kenngr.meas_signal_fixed_stop (P-AXIS-00330)
DRIVE
This parameter defines that the probing signal is supplied by the drive. Additional settings in the drive are required (see [FCT-C4]).
This setting corresponds to the old parameters kenngr.mess_signal_taster (P-AXIS-00117), kenngr.mess_signal_sercos (P-AXIS-00116), kenngr.meas_signal_drive (P-AXIS-00269)
PLC_EXT_LATCH_­CONTROL
This setting defines that operation requires external hardware for the measurement run. Therefore the CNC informs the PLC via the external measuring interface about the start and stop of a measurement run, so that the PLC can enable or disable the probing hardware accordingly (see [HLI//Measuring with external probing hardware]). This method specifies the probing signal and the probed value via the lr_mc_control.probing_signal and lr_mc_control.probing_position control units.
PLC_FIRST_EVENT
This setting corresponds to the value “PLC“. However, the measurement run terminates as soon as the measuring event is detected in one of the axes measured using this setting. On the other hand, in “PLC” mode, a measuring event must occur on each of the measured axes in the lr_mc_control.probing_signal control unit.
This setting corresponds to the old parameter mess_signal_achs_steuer (P-AXIS-00115)
This setting defines that operation requires external hardware for the measurement run. Therefore the CNC informs the PLC via the external measuring interface about the start and stop of a measurement run, so that the PLC can enable or disable the probing hardware accordingly (see [HLI//Measuring with external probing hardware]). With this method, the probing signal and the point in time are specified by the control units, PLC parameters and control commands of an axis. The CNC calculated the exact measured value at the measurement time transferred.
/*/ Drive type dependent default setting for probing signal source (DRIVE_TYPE_DEFAULT ):
Drive type (see P-AXIS-00020)
Probing signal source default setting
Conventional
Sercos
Profidrive
Beckhoff Lightbus
+-10V via field bus (terminal)
RT Ethernet
CANopen
CAN bus
DRIVE
Drive simulation
Virtual axis
PLC_FIRST_EVENT
Permissible measurement methods dependent on drive type:
PLC
FIXED_STOP
DRIVE
PLC_­FIRST_-EVENT
Conventional
X
X
X
X
X
Sercos
X
X
X
X
X
Profidrive
X
X
X
X
Beckhoff Lightbus
X
X
X
X
X
X
X
X
RT Ethernet
X
X
X
X
CANopen
X
X
X
X
CAN bus
X
X
X
X
Drive simulation
X
X
(X)*
X
X
Virtual axis
X
X
(X)*
X
X
(*) Using the measurement simulation (see P-AXIS-00112,[PROG//Extended programming])