Example of a compensation value list
The diagram below shows a compensation value table with the properties:
- Non-equidistant interpolation points (kw.ssfk.interval = 0)
- Bilateral compensation table (kw.ssfk.bilateral = 1)
- Position specifications in metric system (kw.ssfk.unit = 1)
- Compensation value table with 140 entries (kw.ssfk.kw_nr_max = 140). The index of the position and setpoint entries goes from 0 to 139.
- The following values were measured at the third gauged position (table[2]):
Programmed | Measured value pos | Measured value neg | pos calculated | neg calculated |
19866.7 μm | 19856.5 μm | 19874.7 μm | -102 x 0.1 μm | 80 x 0.1 μm |
Programming Example
kopf.log_achs_nr 2
kopf.log_achs_name Y-ACHSE
kw.ssfk.interval 0
kw.ssfk.kw_startpos -200000
kw.ssfk.kw_nr_max 140
kw.ssfk.unit 1
kw.ssfk.bilateral 1
kw.ssfk.table[0].setpoint -200000
kw.ssfk.table[1].setpoint -199306
kw.ssfk.table[2].setpoint -198667
kw.ssfk.table[3].setpoint -198001
kw.ssfk.table[138].setpoint 334488
kw.ssfk.table[139].setpoint 335591
kw.ssfk.table[0].pos 0
kw.ssfk.table[1].pos 24
kw.ssfk.table[2].pos -102
kw.ssfk.table[139].pos -55
kw.ssfk.table[0].neg 0
kw.ssfk.table[1].neg 67
kw.ssfk.table[2].neg 80
kw.ssfk.table[139].neg 114
ith setpoint
ith actual value