MC_CamAdd
MC_CamAdd 1:
MC_CamAdd adds a cam plate to a multi-cam coupling. The cam plate coupling is initially created with MC_CamIn_V2.
Alternatively, a cam plate can be added with MC_CamIn_V2.
The status flag Axis.Status.CamTableQueued (AXIS_REF) can be used to check whether a cam plate is queued for addition or switchover.
Important:
ActivationMode (time or position from which the operation takes place)
CamOperationMode (adding, switching or removal of superimposed cam plates)
ScalingMode
MC_CamAdd 2: Inputs
   Execute            : BOOL;
   ActivationMode     : MC_CamActivationMode := MC_CAMACTIVATION_INSTANTANEOUS;
   ActivationPosition : LREAL;
   CamTableID         : MC_CAM_ID;
   Scaling            : ST_CamScalingData;
   Options            : ST_CamAddOptions;
Type
Execute
The command is executed with a rising edge at Execute input.
ActivationMode
The ActivationMode is used to specify the time or position at which the cam plate coupling or switchover is to take place.
ActivationMode can also be specified when a slave is coupled for the first time.
ActivationPosition
LREAL
Optional master position at which a cam plate is switched, depending on the ActivationMode.
(Not required for first coupling.)
If the MC_CAMACTIVATION_ATMASTERCAMPOS ActivationMode is used, the position refers to the unscaled cam plate. If the position in the application refers to the scaled cam plate, it can be divided by the MasterScaling before the function block is called.
CamTableID
MC_CAM_ID
ID of the cam plate used for the coupling.
Scaling
ST_CamScalingData
Optional scaling parameters for the cam plate.
Options
ST_CamAddOptions
InterpolationType
Interpolation type for position tables. Not required for motion functions.
MC_CamAdd 3: Inputs/outputs
   Master : AXIS_REF;
   Slave  : AXIS_REF;
Type
Master
AXIS_REF
Axis data structure of the master.
Slave
AXIS_REF
Axis data structure of the Slave.
The axis data structure of type AXIS_REF addresses an axis unambiguously within the system. Among other parameters, it contains the current axis status, including position, velocity or error state.
MC_CamAdd 4: Outputs
   InSync         : BOOL;
   Busy           : BOOL;
   Active         : BOOL;
   CommandAborted : BOOL;
   Error          : BOOL;
   ErrorID        : UDINT;
Type
InSync
Becomes TRUE if the cam plate operation was completed successfully. In operations with activation position, InSync only becomes TRUE after the actual activation.
Busy
The Busy output becomes TRUE when the command is started with Execute and remains TRUE for as long as the command is processed. If Busy becomes FALSE again, the function block is ready for a new order. At the same time one of the outputs, InSync or Error, is set.
Active
Active indicates that the command is executed. For cam plate switching, Active becomes TRUE if the coupling command was executed successfully but the cam plate is still queued. If the cam plate is activated depending on the ActivationMode, Active becomes FALSE and InSync is set.
CommandAborted
Becomes TRUE if the command could not be fully executed. The axis may have become decoupled during the coupling process (simultaneous command execution).
Error
Becomes TRUE as soon as an error occurs.
ErrorID
UDINT
If the error output is set, this parameter supplies the error number.