FB_CTRL_TempController
The temperature controller function block FB_CTRL_TempController has various inputs and outputs, which are described below. All the controller's parameters are passed to it via structures.
Interface
eCtrlMode : E_CTRL_MODE;
bSelSetpoint : BOOL;
fW1 : LREAL;
fW2 : LREAL;
fX : LREAL;
fYManual : LREAL;
bOpenThermocouple : BOOL; (* thermocouple *)
bReverseThermocouple : BOOL;
bBackVoltage : BOOL;
bLeakage : BOOL; (* heating system *)
bShortCircuit : BOOL;
bOpenCircuit : BOOL;
sParaControllerExternal : ST_CTRL_ParaController
END_VARName | Unit | Value range | Description |
eControlMode | 1 | E_CTRL_MODE | Mode switching |
bSelSetpoint | 1 | [TRUE,FALSE] | Selects one of two possible setpoints. FALSE selects the normal setpoint, while TRUE selects the standby setpoint. |
fW1 | °C | LREAL | Setpoint |
fW2 | °C | LREAL | Standby setpoint is usually smaller than fW1. fSelSetpoint can be used to switch between fW1 and fW2. |
fX | °C | LREAL | Actual value |
fYManual | -100% - +100% | LREAL | Control value in manual operation |
bOpenThermocouple | 1 | [TRUE,FALSE] | The thermocouple is open if TRUE. Must be indicated by the hardware. |
bReverseThermocouple | 1 | [TRUE,FALSE] | TRUE indicates that the thermocouple has been connected with the wrong polarity. Must be indicated by the hardware. |
bBackVoltage | 1 | [TRUE,FALSE] | TRUE indicates that the input voltage at the thermocouple is too high. Must be indicated by the hardware. |
bLeakage | 1 | [TRUE,FALSE] | TRUE indicates that leakage current has been detected at the heating element. Must be indicated by the hardware. |
bShortCircuit | 1 | [TRUE,FALSE] | TRUE indicates that a short circuit has been detected at the heating element. Must be indicated by the hardware. |
bOpenCircuit | 1 | [TRUE,FALSE] | TRUE indicates that an open circuit has been detected at the heating element. Must be indicated by the hardware. |
sControllerParameter | none | Structure | General parameters (sampling time etc.) are passed to the function block in this structure. |
sParaControllerExternal | none | Structure | An external controller parameter set is passed to the function block in this structure. |
fYAnalog : LREAL;
bYPWMPos : BOOL;
bYPWMNeg : BOOL;
bYDigPos : BOOL;
bYDigNeg : BOOL;
dwAlarm : DWORD;
fMaxOverShoot : LREAL;
tStartUpTime : TIME;
eCtrlState : E_CTRL_STATE := eCTRL_STATE_IDLE;
sParaControllerInternal : ST_CTRL_ParaController;
eErrorId : E_CTRL_ErrorCodes;
END_VAR Name | Unit | Value range | Description |
fYAnalog | none | LREAL | Analog control value |
bYPWMPos | none | [TRUE,FALSE] | Boolean output, pulse width modulated. Positive/heating mode |
bYPWMNeg | none | [TRUE,FALSE] | Boolean output, pulse width modulated. Negative/cooling mode |
bYDigPos | none | [TRUE,FALSE] | Boolean output of a three-step controller (TRUE control value 100%, FALSE control value off) |
bYDigNeg | none | [TRUE,FALSE] | Boolean output of a three-step controller (TRUE control value -100%, FALSE control value off) |
dwAlarm | none | DWORD | Alarm messages (see ENUM ...) |
fMaxOverShoot | °C | LREAL | Max. overshoot in °C above/below setpoint. |
tStartUpTime | TIME | - | Startup time until the setpoint is reached for the first time |
eCtrlState | none | E_CTRL_STATE | current controller status (see ENUM ...) |
sParaControllerInternal | none | Structure | In this structure the internal controller parameter set (determined by the tuning) is made available. |
bError | none | [TRUE,FALSE] | If an error is present, then |
iErrorId | none | INT | If |
sControllerParameter : ST_CTRL_TempCtrlParameter; (* controller parameter set *)
sController | ST_CTRL_TempCtrl | Parameter structure of the function block |
TwinCAT 3.1.4016 | PC or CX | Tc2_TempController |