ST_ParaControlValue
ST_ParaControlValue 1:
This version of the function block is obsolete.
Do not use this function block anymore.
TYPE ST_ParaControlValue :
STRUCT
  (* general parameters *)
  iMode                   : E_ControlMode;
  iReactionOnFailure    : E_ReactionOnFailure;
  fYTune                : LREAL;
  fYStable              : LREAL;
  dwAlarmSupp           : DWORD;
  tCtrlCycleTime        : TIME;
  tTaskCycleTime        : TIME;
  (* setpoint parameters *)
  fWMin                 : LREAL;
  fWMax                 : LREAL;
  (* start up *)
  fWStartUp             : LREAL;
  tStartUp              : TIME;
  bStartUpRamping       : BOOL;
  fWStartUpVeloPos      : LREAL;
  fWStartUpVeloNeg      : LREAL;
  fWVeloPos             : LREAL;
  fWVeloNeg             : LREAL;
  (* actual value parameters *)
  bFilter               : BOOL;
  tFilter               : TIME;
  (* control value parameters *)
  fYMin                 : LREAL;
  fYMax                 : LREAL;
  fYManual              : LREAL;
  fYOnFailure           : LREAL;
  tPWMCycleTime         : TIME;
  (* controller settings *)
  bEnablePreController  : BOOL;
  bEnableZones          : BOOL;
  bEnableCVFilter       : BOOL;
  iFilterType           : E_FilterType;
  iControllerType       : E_ControllerType;
  (* min max temperatures *)
  TempLow               : LREAL;
  TempLowLow            : LREAL;
  TempHigh              : LREAL;
  TempHighHigh          : LREAL;
  TempAbsoluteHigh      : LREAL;
  TempAbsoluteLow       : LREAL;
  (* internal tuning parameters *)
  fTuneKp               : LREAL := 1.2;
  fTuneTn               : LREAL := 2.0;
  fTuneTv               : LREAL := 0.42;
  fTuneTd               : LREAL := 0.25;
END_STRUCT
END_TYPE
ST_ControllerParameter
Unit
Value range
iMode
none
INT
Controller operation mode (1 = heating, 2 = cooling, 3 = heating & cooling) (see below)
iReactionOnFailure
none
INT
Parameterizable reaction to errors (see below)
fYTune
none
LREAL
Control value during the self-tuning (normally 100%)
fYStable
none
LREAL
Control value during the settling phase (normally 0%)
dwAlarmSupp
none
DWORD
Masks out the alarms (see below)
tCtrlCycleTime
s
TIME
Controller's sampling time. In the course of the sampling time the controller re-calculates the control value.
tTaskCycleTime
s
TIME
Task cycle time. The FB is called with this time interval.
fWMin
K
LREAL
Minimum setpoint
fWMax
K
LREAL
Maximum setpoint
fWVeloPos
K/s
LREAL
Rate of rise (of ramp)
fWVeloNeg
K/s
LREAL
Rate of fall (of ramp).
fWStartUp
K
LREAL
Setpoint at start-up
tStartUp
s
TIME
Time with the fWStartUp setpoint
bStartUpRamping
none
[TRUE,FALSE]
Switches on ramping during the start-up phase.
fWStartUpVeloPos
K/s
LREAL
Rate of rise (of ramp) during the start-up phase
fWStartUpVeloNeg
K/s
LREAL
Rate of fall (of ramp) during the start-up phase
fYMin
none
LREAL
Minimum value of the manipulated variable
fYMax
none
LREAL
Maximum value of the manipulated variable
fYManual
none
LREAL
Control value in manual operation
fYOnFailure
none
LREAL
Control value in case of error (parameterizable)
tPWMCycleTime
s
TIME
Cycle time of the PWM signal
tFilter
s
TIME
Time constant of the actual value filter (first order P-T1 filter)
bFilter
none
[TRUE,FALSE]
The actual value filter is actuated if TRUE.
none
[TRUE,FALSE]
Switches pre-controller on.
bEnableZones
none
[TRUE,FALSE]
Switches open loop characteristic on until close to setpoint.
bEnableCVFilter
none
[TRUE,FALSE]
Switches on control value filter following the main controller.
iFilterType
none
ENUM
Selection of a filter type for the control value filter following the main controller (see below).
iControllerType
none
ENUM
Selection of a control algorithm (see below).
TempLow
K
LREAL
Relative lower temperature limit in the first band
TempLowLow
K
LREAL
Relative lower temperature limit in the second band
TempHigh
K
LREAL
Relative upper temperature limit in the first band
TempHighHigh
K
LREAL
Relative upper temperature limit in the second band
TempAbsoluteHigh
K
LREAL
Absolute upper temperature limit
TempAbsoluteLow
K
LREAL
Absolute lower temperature limit
fTuneKp
none
LREAL
FineTuning parameters for the PID controller (only for advanced users)
fTuneTn
none
LREAL
fTuneTv
none
LREAL
fTuneTd
none
LREAL