ST_ControllerParameter
TYPE ST_CTRL_TempCtrlParameter:
STRUCT
  (* general parameters *)
  iMode                     : E_CTRL_ControlMode;
  iReactionOnFailure        : E_CTRL_ReactionOnFailure;
  bSelCtrlParameterSet      : BOOL;
  dwAlarmSupp               : DWORD;
  tCtrlCycleTime            : TIME;
  tTaskCycleTime            : TIME;
  (* tuning parameteer *)
  iTuningMode               : E_CTRL_TuneMode;
  tTuneStabilisation        : TIME       := T#20S;
  fEndTunePercentHeating    : LREAL      := 80.0;
  fYTuneHeating             : LREAL;
  fYStableHeating           : LREAL;
  fEndTunePercentCooling    : LREAL      := 20.0;
  fYTuneCooling             : LREAL;
  fYStableCooling           : LREAL;
  fScalingFactor            : LREAL      := 1.0;
  (* setpoint parameters *)
  fWMin                     : LREAL;
  fWMax                     : LREAL;
  (* start up *)
  bEnableSoftStart          : BOOL;
  bEnableRamping            : BOOL;
  fWStartUp                 : LREAL;
  tStartUp                  : TIME;
  bStartUpRamping           : BOOL;
  fWStartUpVeloPos          : LREAL;
  fWStartUpVeloNeg          : LREAL;
  fWVeloPos                 : LREAL;
  fWVeloNeg                 : LREAL;
  (* actual value parameters *)
  bFilter                   : BOOL;
  tFilter                   : TIME;
  (* deadband parameters *)
  bDeadband                 : BOOL;
  fEDeadband                : LREAL;
  (* control value parameters *)
  fYMin                     : LREAL;
  fYMax                     : LREAL;
  fYManual                  : LREAL;
  fYOnFailure               : LREAL;
  tPWMCycleTime             : TIME;
  tPWMMinOffTime            : TIME;
  tPWMMinOnTime             : TIME;
  tPWMWaitingTime           : TIME;
  fYThresholdOff            : LREAL;
  fYThresholdOn             : LREAL;
  nCyclesForSwitchOver      : INT        := 100;
  (* controller settings *)
  bEnablePreController      : BOOL;
  bEnableZones              : BOOL;
  bEnableCVFilter           : BOOL;
  iFilterType               : E_CTRL_FilterType;
  iControllerType           : E_CTRL_ControllerType;
  (* min max temperatures *)
  TempLow                   : LREAL;
  TempLowLow                : LREAL;
  TempHigh                  : LREAL;
  TempHighHigh              : LREAL;
  TempAbsoluteHigh          : LREAL;
  TempAbsoluteLow           : LREAL;
  (* internal tuning parameters *)
  fTuneKp                   : LREAL     := 1.2;
  fTuneTn                   : LREAL     := 2.0;
  fTuneTv                   : LREAL     := 0.42;
  fTuneTd                   : LREAL     := 0.25;
END_STRUCT
END_TYPE
Unit
Value range
General parameters
iMode
none
INT
Controller operation mode (1 = heating, 2 = cooling, 3 = heating & cooling) (see below)
iReactionOnFailure
none
INT
Parameterizable reaction to errors (see below)
none
TRUE = external parameter set, FALSE = internal parameter set (determined by tuning)
dwAlarmSupp
none
DWORD
Masks out the alarms (see below)
tCtrlCycleTime
s
TIME
Controller's sampling time. In the course of the sampling time the controller re-calculates the control value.
tTaskCycleTime
s
TIME
Task cycle time. The FB is called with this time interval.
Tuning parameters
iTuningMode
K
E_CTRL_TuneMode
Determination of the tuning sequence (see below.)
tTune stabilization
s
TIME
Waiting time until the section is stable for tuning.
LREAL
Percentage value of setpoint, from which the system switches to Closed Loop Control.
fYTuneCooling
K
LREAL
Step change in control value during tuning.
fYStableCooling
K
LREAL
Control value when switching to tuning during cooling.
fScalingFactor
none
LREAL
Scaling factor for parameter switching if no tuning is performed for cooling.
Setpoint parameters
fWMin
K
LREAL
Minimum setpoint
fWMax
K
LREAL
Maximum setpoint
bEnableSoftStart
none
FALSE = no soft start, TRUE = soft start
bEnableRamping
none
FALSE = no ramping, TRUE = ramping
fWStartUp
K
LREAL
Setpoint at start-up
tStartUp
s
TIME
Time with the fWStartUp setpoint
bStartUpRamping
none
[TRUE,FALSE]
Switches on ramping during the start-up phase.
fWStartUpVeloPos
K/s
LREAL
Rate of rise (of ramp) during the start-up phase
fWStartUpVeloNeg
K/s
LREAL
Rate of fall (of ramp) during the start-up phase
fWVeloPos
K/s
LREAL
fWVeloNeg
K/s
LREAL
Rate of fall (of ramp).
Actual value parameters
tFilter
s
TIME
Time constant of the actual value filter (first order P-T1 filter)
bFilter
none
[TRUE,FALSE]
The actual value filter is actuated if TRUE.
Deadband parameters
bDeadband
none
[TRUE,FALSE]
TRUE = deadband on, FALSE = deadband off
fEDeadband
K
LREAL
Size of the deadband in degrees
Control value parameters
fYMin
none
LREAL
Minimum value of the manipulated variable
fYMax
none
LREAL
Maximum value of the manipulated variable
fYManual
none
LREAL
Control value in manual operation
fYOnFailure
none
LREAL
Control value in case of error (parameterizable)
tPWMCycleTime
s
TIME
Cycle time of the PWM signal
tPWMMinOffTime
s
TIME
PWM: minimum switch-off time
tPWMMinOnTime
s
TIME
PWM: minimum switch-on time
tPWMWaitingTime
s
TIME
PWM: waiting time when switching from heating to cooling
fYThresholdOff
LREAL
3-point: switch-off threshold
fYThresholdOn
LREAL
3-point: switch-on threshold
none
INT
Number of cycles for transition from one parameter set to another
Controller parameters
none
[TRUE,FALSE]
Switches pre-controller on.
bEnableZones
none
[TRUE,FALSE]
Switches open loop characteristic on until close to setpoint.
bEnableCVFilter
none
[TRUE,FALSE]
Switches on control value filter following the main controller.
iFilterType
none
ENUM
Selection of a filter type for the control value filter following the main controller (see below).
iControllerType
none
ENUM
Selection of a control algorithm (see below).
Alarming parameters
TempLow
K
LREAL
Relative lower temperature limit in the first band
TempLowLow
K
LREAL
Relative lower temperature limit in the second band
TempHigh
K
LREAL
Relative upper temperature limit in the first band
TempHighHigh
K
LREAL
Relative upper temperature limit in the second band
TempAbsoluteHigh
K
LREAL
Absolute upper temperature limit
TempAbsoluteLow
K
LREAL
Absolute lower temperature limit
Expert parameters
fTuneKp
none
LREAL
FineTuning parameters for the PID controller (only for advanced users)
fTuneTn
none
LREAL
fTuneTv
none
LREAL
fTuneTd
none
LREAL