FB_CTRL_TempController_DistComp
This temperature controller function block adds disturbance compensation to the FB_CTRL_TempController function blocks. The structure is described here.
eCtrlMode : E_CTRL_MODE;
bSelSetpoint : BOOL;
fW1 : LREAL;
fW2 : LREAL;
fX : LREAL;
fYManual : LREAL;
bOpenThermocouple : BOOL;
bReverseThermocouple : BOOL;
bBackVoltage : BOOL;
bLeakage : BOOL;
bShortCircuit : BOOL;
bOpenCircuit : BOOL;
fD : LREAL;
bCompensateDisturbance : BOOL;
stParaControllerExternal : ST_CTRL_ParaController;
END_VARName | Unit | Area | Description |
eControlMode | Obsolete | E_CTRL_MODE | Switches mode. |
bSelSetpoint | Obsolete | [True, False] | Selects one of the two possible setpoints; TRUE selects the standby setpoint. |
fW1 | °C | LREAL | Setpoint |
fW2 | °C | LREAL | Standby setpoint (normally less than fW1, bSelSetpoint is used to switch between fW1 and fW2). |
fX | °C | LREAL | Actual value |
fYManual | % | [-100%, +100%] | Control value in manual mode |
bOpenThermocouple | Obsolete | [True, False] | The thermocouple is open when TRUE; must be specified by the hardware. |
bReverseThermocouple | Obsolete | [True, False] | The thermocouple is connected with incorrect polarity if TRUE; must be specified by the hardware. |
bBackVoltage | Obsolete | [True, False] | The input voltage at the thermocouple is too high if TRUE; must be specified by the hardware |
bLeakage | Obsolete | [True, False] | Leakage current was detected if TRUE; must be specified by the hardware. |
bShortCircuit | Obsolete | [True; False] | Short circuit was detected if TRUE; must be specified by the hardware. |
bOpenCircuit | Obsolete | [True, False] | Open circuit was detected if TRUE; must be specified by the hardware. |
fD | Obsolete | LREAL | Actual value of the measured disturbance variable |
bCompensateDisturbance | Obsolete | [True, False] | Disturbance compensation is enabled if TRUE. |
sParaControllerExternal | Obsolete | Structure | An external controller parameter set was transferred to the controller. |
fYAnalog : LREAL;
bYPWMPos : BOOL;
bYPWMPos : BOOL;
bYPWMNeg : BOOL;
bYDigPos : BOOL;
bYDigNeg : BOOL;
dwAlarm : DWORD;
fMaxOverShoot : LREAL;
tStartUpTime : TIME;
eCtrlState : E_CTRL_STATE;
sParaControllerInternal : ST_CTRL_ParaController;
eErrorId : E_CTRL_ErrorCodes;
END_VARVAR_IN_OUT
sControllerParameter : ST_CTRL_TempCtrlParameter;
sCompensatorParameter : ST_CTRL_DistCompParameter;
sController | ST_CTRL_TempCtrl | Parameter structure of the function block |
sCompensatorParameter | ST_CTRL_DistComp | Parameter structure of the function block |
TwinCAT 3.1.4016 | PC or CX | Tc2_TempController |