FB_CTRL_PID
The function block provides a PID transfer element in the functional diagram.
Transfer function
The following transfer function can be specified if the boolean inputs bPInTheFeedbackPath
and bDInTheFeedbackPath
are FALSE. Otherwise the transfer function only describes part of the transfer behavior of the function block.
![FB_CTRL_PID 2:](Images/png/9007208001574667__Web.png)
Functional diagram
The standard functional diagram of a PID controller in additive form has been expanded by the two active boolean inputs bPInTheFeedbackPath
(which act as "switches"), so that a modified functional diagram can be activated.
Control background: due to the differential component of the control algorithm, large control values are generated at setpoint step-changes, which cause a strain on the control elements and may cause the control system to oscillate. A control algorithm whose differential component is only applied to the control value (bDInTheFeedbackPath := TRUE
) avoids this problem.
The bPInTheFeedbackPath
inputs permit the closed control loop to implement the following transfer functions:
bPInTheFeedbackPath | bDInTheFeedbackPath | G(s) |
false | false | |
true | false | |
false | true | |
true | true |
with:
![FB_CTRL_PID 8:](Images/png/9007208001730187__Web.png)
![FB_CTRL_PID 9:](Images/png/9007208001732363__Web.png)
![FB_CTRL_PID 10:](Images/png/9007208001747339__Web.png)
The standard setting for the two bPInTheFeedbackPath
inputs is FALSE. The PID controller then corresponds to a standard PID controller in additive form.
Step response
ARW
fSetpointValue : FLOAT;
fActualValue : FLOAT;
fManSyncValue : FLOAT;
bSync : BOOL;
eMode : E_CTRL_MODE;
bHold : BOOL;
Name | Type | Description |
fSetpointValue | FLOAT | Setpoint of the controlled variable |
fActualValue | FLOAT | Actual value of the controlled variable |
fManSyncValue | FLOAT | Input, to whose value it is possible to set the internal state of the PID-element. |
bSync | BOOL | A rising edge at this input sets the PID-element to the value "fManSyncValue". |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
bHold | BOOL | A TRUE at this input will hold the internal state (and therefore also the output) constant at its current value, independently of the control deviation. |
fOut : FLOAT;
bARWactive : BOOL;
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
fOut | FLOAT | Output of the PID element |
bARWactive | BOOL | A TRUE at this output indicates that the PID-element is being restricted. |
eState | E_CTRL_STATE | State of the function block |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
stParams : ST_CTRL_PID_PARAMS;
stParams | ST_CTRL_PID_PARAMS | Parameter structure of the PID element |
stParams
consists of the following elements:
TYPE
ST_CTRL_PID_PARAMS :
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
fKp : FLOAT := 0;
tTn : TIME := T#0ms;
tTv : TIME := T#0ms;
tTd : TIME := T#0ms;
fOutMaxLimit : FLOAT := 1E38;
fOutMinLimit : FLOAT := -1E38;
bPInTheFeedbackPath : BOOL;
bDInTheFeedbackPath : BOOL;
bARWOnIPartOnly : BOOL;
END_STRUCT
END_TYPE
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
fKp | FLOAT | Controller amplification / controller coefficient |
tTn | TIME | Integral action time; if this is parameterized to T#0s, the I component is deactivated. |
tTv | TIME | Derivative action time; if this is parameterized to T#0s, the D component is deactivated. |
tTd | TIME | Damping time |
fOutMaxLimit | FLOAT | Upper limit at which integration is halted and to which the output is limited (ARW measure). Reaching this limit is indicated by a TRUE at the |
fOutMinLimit | FLOAT | Lower limit at which integration is halted and to which the output is limited (ARW measure). Reaching this limit is indicated by a TRUE at the |
bPInTheFeedbackPath | BOOL | Input value of the internal P-element can be selected with this input (see functional diagram). Standard setting: FALSE |
bDInTheFeedbackPath | BOOL | Input value of the internal D-element can be selected with this input (see functional diagram). Standard setting: FALSE |
bARWOnIPartOnly | BOOL | If this parameter is FALSE (the standard setting), the integration of the I-component is halted if the complete controller output reaches the upper or lower limit. If it is TRUE, the integration is halted if the I-component (the output of the integrator) reaches some limit. (Cf. functional diagram.) |