Setting rules for the P, PI and PID controllers
This page summarizes some of the setting rules found in the relevant literature. The setting rule to be used for a particular case has to be determined depending on the controlled system.
Ziegler and Nichols
The Ziegler and Nichols setting rules can be used if the controlled system can be approximated by a dead time element and 1st order delay element.
Setting rules for the P, PI and PID controllers 1:
Setting rules for the P, PI and PID controllers 2:
Tt = dead time of the controlled system
Ks = gain factor of the controlled system
Ts = time constant of the controlled system
Setting rules for the P, PI and PID controllers 3:
Chien, Hrones and Reswick
If this procedure is to be used, the step response of the system must show delay characteristics and be free from overshoot effects.
From the step response the delay time TU, the compensation time Tg and the system amplification Ks are determined.
The system amplification is calculated from the following quotient:
Setting rules for the P, PI and PID controllers 4:
Setting rules for the P, PI and PID controllers 5:
Optimization of the interference behavior:
Setting rules for the P, PI and PID controllers 6:
Optimization of the control behavior
Setting rules for the P, PI and PID controllers 7: