FB_CTRL_SETPOINT_GENERATOR
The function block provides a setpoint generator that outputs the setpoint selected from a table. Changing from one setpoint to another can be implemented continuously or discontinuously.
Behavior of the output value
Example table:
Index |
1 | 12 |
2 | 42 |
3 | 25 |
… | 73 |
The individual setpoints are stored in the array. The array must be made known to the function block through the appropriate parameters. One of the setpoints stored in the table is selected by means of the nSetpointIndex input. This is then made available at the output, and can be used as the setpoint for the controller. Changing from one value to another can be implemented in a linear fashion or as a jump. The velocity of a continuous transition is specified by the fVeloPos and fVeloNeg parameters. The bValueReached output indicates that the chosen setpoint has been reached.
nSetpointIndex : INT;
fManValue : FLOAT;
eMode : E_CTRL_MODE;
nSetpointIndex | INT | Index of the selected setpoint |
fManValue | FLOAT | Input whose value is output in manual mode. |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
Outputs
fOut : SETPOINT_TABLE_ELEMENT;
bValueReached : BOOL;
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
fOut | SETPOINT_ | Output of the setpoint generator |
bValueReached | BOOL | The output is TRUE when the selected setpoint has been reached, i.e. the ramp leading to the selected value has finished. |
eState | E_CTRL_STATE | State of the function block |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
Inputs/ outputs
stParams : ST_CTRL_SETPOINT_GENERATOR_PARAMS;
stParams | ST_CTRL_SETPOINT_ | Parameter structure of the ramp generator |
stParams consists of the following elements:
TYPE ST_CTRL_SETPOINT_GENERATOR_PARAMS:
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
pDataTable_ADR : POINTER TO
INTERPOLATION_TABLE_ELEMENT := 0;
nDataTable_SIZEOF : UINT := 0;
nDataTable_NumberOfRows : UINT := 0;
fVeloPos : FLOAT;
fVeloNeg : FLOAT;
bDisableRamping : BOOL := FALSE;
END_STRUCT
END_TYPEName | Type | Description |
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
pDataTable_ADR | POINTER TO INTERPOLATION_ | Address of the data array |
nDataTable_SIZEOF | UINT | Size of the data array |
nDataTable_NumberOfRows | UINT | Number of rows in the data array |
fVeloPos | FLOAT | Velocity in unit/s, with which the output is changed from a lower value to a higher one. |
fVeloNeg | FLOAT | Velocity in unit/s, with which the output is changed from a higher value to a lower one. |
bDisableRamping | BOOL | A continuous output value is not calculated if this parameter is TRUE. There is a step change between the output values. |