FB_CTRL_FLOW_TEMP_SETPOINT_GEN
This function block enables specification of a flow temperature depending on the outdoor temperature.
The setpoint for the flow temperature (fOut) is determined from the ambient temperature (fAmbientTemperature). A straight line that can be moved via an offset (fOffsetTemperature) is used for this purpose. The slope is determined based on the specified ambient and flow temperature corners. A flag (bLimitFlowTemp) is used to specify whether or not the flow temperature is restricted to its limit values. The offset temperature can be used to realize a night setback or pre-control.
Behavior of the output value
fAmbientTemperature : FLOAT;
fOffsetTemperature : FLOAT;
bLimitFlowTemp : BOOL;
fAmbient | FLOAT | Start of ramp generation |
fOffset | FLOAT | Start value of the ramp |
bLimitFlowTemp | BOOL | Target value of the ramp |
Outputs
fOut : FLOAT;
eErrorId : E_CTRL_ERRORCODES;
fOut | FLOAT | Setpoint of the flow temperature |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE as soon as an error situation occurs. |
Inputs/ outputs
stParams : ST_CTRL_FLOW_TEMP_SETPOINT_GEN_PARAMS;
stParams | ST_CTRL_FLOW_TEMP_ | Parameter structure of the ramp generator |
stParams consists of the following elements:
TYPE ST_CTRL_FLOW_TEMP_SETPOINT_GEN_PARAMS:
STRUCT
tTaskCycleTime : TIME;
tCtrlCycleTime : TIME;
fForeRunTempMax : FLOAT;
fForeRunTempMin : FLOAT;
fAmbientTempMax : FLOAT;
fAmbientTempMin : FLOAT;
END_STRUCT
END_TYPEName | Type | Description |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every task cycle this corresponds to the task cycle time of the calling task. |
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
fForeRunTempMax | FLOAT | Maximum flow temperature (see diagram) |
fForeRunTempMin | FLOAT | Minimum flow temperature (see diagram) |
fAmbientTemp | FLOAT | outdoor temperature for which the minimum flow temperature is specified. |
fAmbientTemp | FLOAT | outdoor temperature for which the maximum flow temperature is specified. |