FB_CTRL_STEPPING_MOTOR_OUT
This function block generates a control value for a stepper motor.
Behavior of the output
fIn : FLOAT;
bUpperLimitSwitch : BOOL;
bLowerLimitSwitch : BOOL;
fManSyncValue : FLOAT;
bSync : BOOL;
eMode : E_CTRL_MODE;
fIn | FLOAT | Controller's control value (controller output) |
bUpperLimit | BOOL | Limit switch, becomes TRUE when the upper stop is reached. |
bLowerLimit | BOOL | Limit switch, becomes TRUE when the lower stop is reached. |
fManSyncValue | FLOAT | Input with which the internal state of the motor setting can be adjusted, or whose value is adopted in manual mode. |
bSync | BOOL | With a rising edge at this input the internal step counter is set to the step that corresponds to the value "fManSyncValue". |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
![]() | For synchronization with the current valve position, this function block has the mode eCTRL_MODE_SYNC_MOVEMENT. In this mode, pulses for closing the valve are output until the valve is safely closed. The function block is then synchronized with this valve position. Once the synchronization process is completed, eCTRL_STATE_ACTIVE mode is automatically activated. |
Outputs
bOutBitPos : BOOL;
bOutBitNeg : BOOL;
nActualStep : DINT;
eState : E_CTRL_STATE;
eErrorId : E_CTRL_ERRORCODES;
bOutBitPos | BOOL | Output required to drive the motor in a positive direction. |
bOutBitNeg | BOOL | Output required to drive the motor in a negative direction. |
nActualStep | DINT | Actual step at which the motor is positioned. |
eState | E_CTRL_STATE | State of the function block |
eErrorId | E_CTRL_ERRORCODES | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
Inputs/ outputs
stParams : ST_CTRL_STEPPING_MOTOR_OUT_PARAMS;
END_VAR Name | Type | Description |
stParams | ST_CTRL_STEPPING_MOTOR_ | Parameter structure of the function block |
stParams consists of the following elements:
TYPE
ST_CTRL_STEPPING_MOTOR_OUT_PARAMS:
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
tOnTime : TIME;
tOffTime : TIME;
nMaxMovingPulses : DINT;
nMinMovingPulses : UINT := 0;
bHoldWithOutputOn : BOOL;
nAdditionalPulsesAtLimits : DINT;
bMoveOnLimitSwitch : BOOL;
fCtrlOutMax : FLOAT := 100.0;
fCtrlOutMin : FLOAT := 0.0;
END_STRUCT
END_TYPEName | Type | Description |
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
tOnTime | TIME | Pulse length |
tOffTime | TIME | Pause length |
nMaxMoving | DINT | Max. number of pulses required to move from one limit to another. |
nMinMoving | UINT | Min. number of pulses required to move from one limit to another. |
bHoldWith | BOOL | If this parameter is set to TRUE, then an output remains set when the drive is stationary. This will result in braking. |
nAdditionalPulsesAtLimits | DINT | Number of supplementary pulses that are output to reliably ensure that limits are reached. |
bMoveOnLimit | BOOL | If this is TRUE, then pulses are output when the control value is either 0% or 100% until the limit switch is reached. |
fCtrlOutMax | FLOAT | Control value for which the valve will be driven to 100%. |
fCtrlOutMin | FLOAT | Control value for which the valve will be driven to 0%. |