FB_CTRL_TuTg
FB_CTRL_TuTg 1:
The function block provides a TuTg transfer element (a dead time delay element) in the functional diagram.
Transfer function
FB_CTRL_TuTg 2:
FB_CTRL_TuTg 3:
FB_CTRL_TuTg 4: Inputs
    fIn              : FLOAT;
    fManSyncValue    : FLOAT;
    bSync            : BOOL;
    eMode            : E_CTRL_MODE;
    bHold            : BOOL;
Type
fIn
FLOAT
Input value of the TuTg element
fManSyncValue
FLOAT
Input value to which the TuTg element can be set, or that is issued at the output in manual mode.
bSync
A rising edge at this input sets the TuTg element to the value "fManSyncValue".
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
bHold
FLOAT
A TRUE at this input will hold the internal state (and therefore also the output) constant at its current value, independently of the input value.
FB_CTRL_TuTg 5: Outputs
    fOut                  : FLOAT;
    bSampleRateChanged    : BOOL;
    eState                : E_CTRL_STATE;
    eErrorId              : E_CTRL_ERRORCODES;
    bError                : BOOL;
Type
fOut
FLOAT
Output of the TuTg element
bSampleRate
Changed
Output that indicates whether the function block has internally reduced the sampling rate because of the array being used to delay the input signal not otherwise providing sufficient room.
eState
E_CTRL_STATE
State of the function block
eErrorId
E_CTRL_
ERRORCODES
Supplies the error number when the output bError is set.
Becomes TRUE, as soon as an error occurs.
FB_CTRL_TuTg 6: Inputs/ outputs
    stParams      : ST_CTRL_TuTg_PARAMS;
Type
stParams
ST_CTRL_TuTg_PARAMS
Parameter structure of the TuTg element
stParams consists of the following elements:
TYPE ST_CTRL_TuTg_PARAMS :
STRUCT
    tCtrlCycleTime    : TIME  := T#0ms;
    tTaskCycleTime    : TIME  := T#0ms;
    fKp               : FLOAT := 0;
    tTu               : TIME  := T#0ms;
    tTg               : TIME  := T#0ms;
END_STRUCT
END_TYPE
Type
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
fKp
FLOAT
Controller amplification / transfer coefficient
tTu
TIME
Dead time
tTg
TIME
time constant