FB_CTRL_PTt
The function block provides an PTt transfer element in the functional diagram.
Transfer function
This function block contains internally an array of 500 elements with which the input values can be delayed. When using the tCtrlCycleTime this results in a maximum delay of "500 * tCtrlCycleTime". If this maximum delay is insufficient, the sampling time is extended internally to make it possible to reach the requested dead time. It should, however, be remembered that this process involves increasing the time between the discretization steps. If a new sampling time has been calculated, this is indicated by a TRUE on the bSampleRateChanged output.
fIn : FLOAT;
fManSyncValue : FLOAT;
bSync : BOOL;
eMode : E_CTRL_MODE;
fIn | FLOAT | Input value of the PTt element |
fManSyncValue | FLOAT | Input value to which the PTt element can be set, or that is issued at the output in manual mode. |
bSync | BOOL | A rising edge at this input sets the PTt element to the value "fManSyncValue". |
eMode | E_CTRL_MODE | Input that specifies the operation mode of the function block. |
Outputs
fOut : FLOAT;
bSampleRateChanged : BOOL;
eErrorId : E_CTRL_ERRORCODES;
fOut | FLOAT | Output of the PTt element |
bSampleRate | BOOL | Output that indicates whether the function block has internally reduced the sampling rate because of the array being used to delay the input signal not otherwise providing sufficient room. |
eErrorId | E_CTRL_ | Supplies the error number when the output |
bError | BOOL | Becomes TRUE, as soon as an error occurs. |
Inputs/ outputs
stParams : ST_CTRL_PTt_PARAMS;
stParams | ST_CTRL_PTt_ | Parameter structure of the PTt element |
stParams consists of the following elements:
TYPE ST_CTRL_PTt_PARAMS :
STRUCT
tCtrlCycleTime : TIME := T#0ms;
tTaskCycleTime : TIME := T#0ms;
fKp : FLOAT := 0;
tTt : TIME := T#0ms;
END_STRUCT
END_TYPE Name | Type | Description |
tCtrlCycleTime | TIME | Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle. |
tTaskCycleTime | TIME | Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task. |
fKp | FLOAT | Controller amplification / transfer coefficient |
tTt | TIME | Dead time |