FB_CTRL_DIGITAL_FILTER
FB_CTRL_DIGITAL_FILTER 1:
This function block calculates a discrete transfer function with the structure described below. This structure allows either an FIR filter (Finite Impulse Response) or an IIR filter (Infinite Impulse Response) to be implemented. The transfer function here can be of any order, n.
The coefficients for the following transfer structure are stored in the parameter arrays:
FB_CTRL_DIGITAL_FILTER 2:
FB_CTRL_DIGITAL_FILTER 3:
The programmer must create the following arrays in the PLC if this function block is to be used:
aCoefficientsArray_a        : ARRAY[1..nFilterOrder+1] OF FLOAT;
aCoefficientsArray_b        : ARRAY[1..nFilterOrder+1] OF FLOAT;
aStDigitalFilterData        : ARRAY[1..nFilterOrder] OF
ST_CTRL_DIGITAL_FILTER_DATA;
The coefficients "b1" to "bn" are stored in the array aCoefficientsArray_b. This must be organized as follows:
aCoefficientsArray_b[1] := b1;
aCoefficientsArray_b[2] := b2;
aCoefficientsArray_b[n-1] := bn-1;
aCoefficientsArray_b[n]   := bn;
The coefficients "a1" to "an" are stored in the array aCoefficientsArray_a.
aCoefficientsArray_a[1] := xxx; (* not being evaluated *)
aCoefficientsArray_a[2] := a2;
aCoefficientsArray_a[n-1] := an-1;
aCoefficientsArray_a[n]   := an;
The internal data required by the function block is stored in the array aStDigitalFilterData. This data must never be modified from within the PLC program. This procedure is also illustrated in the sample program listed below.
FB_CTRL_DIGITAL_FILTER 4: Inputs
    fIn        : FLOAT;
    fManValue  : FLOAT;
    eMode      : E_CTRL_MODE;
Type
fIn
FLOAT
Input of the digital filter
fManValue
FLOAT
Input whose value is present at the output in manual mode.
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
FB_CTRL_DIGITAL_FILTER 5: Outputs
    fOut      : FLOAT;
    eState    : E_CTRL_STATE;
    bError    : BOOL;
    eErrorId  : E_CTRL_ERRORCODES;
Type
fOut
FLOAT
Output of the digital filter
eState
E_CTRL_STATE
State of the function block
Becomes TRUE, as soon as an error occurs.
eErrorId
E_CTRL_ERRORCODES
Supplies the error number when the output bError is set.
FB_CTRL_DIGITAL_FILTER 6: Inputs/ outputs
    stParams        : ST_CTRL_DIGITAL_FILTER_PARAMS;
Type
stParams
ST_CTRL_
Parameter structure of the function block
stParams consists of the following elements:
TYPE
ST_CTRL_DIGITAL_FILTER_PARAMS :
STRUCT
    tTaskCycleTime                 : TIME;
    tCtrlCycleTime                 : TIME := T#0ms;
    nFilterOrder                   : USINT;
    pCoefficientsArray_a_ADR       : POINTER TO FLOAT := 0;
    nCoefficientsArray_a_SIZEOF    : UINT;
    pCoefficientsArray_b_ADR       : POINTER TO FLOAT := 0;
    nCoefficientsArray_b_SIZEOF    : UINT;
    pDigitalFilterData_ADR         : POINTER TO ST_CTRL_DIGITAL_FILTER_DATA;
    nDigitalFilterData_SIZEOF      : UINT;
END_STRUCT
END_TYPE
Type
tTaskCycleTime
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
nFilterOrder
USINT
Order of the digital filter [0... ]
POINTER TO FLOAT
Address of the array containing the a coefficients
UINT
Size of the array containing the a coefficients, in bytes
POINTER TO FLOAT
Address of the array containing the b coefficients
UINT
Size of the array containing the b coefficients, in bytes
POINTER TO ST_CTRL_
DIGITAL_
FILTER_DATA
Address of the data array
UINT
Size of the data array in bytes
TYPE
STRUCT
 Internal structure. This must not be written to.
END_STRUCT
END_TYPE
Sample:
PROGRAM PRG_DIGITAL_FILTER_TEST
    fbDigitalFilter        : FB_CTRL_DIGITAL_FILTER;
    aCoefficientsArray_a    : ARRAY[1..3] OF FLOAT;
    aCoefficientsArray_b    : ARRAY[1..3] OF FLOAT;
    aStDigitalFilterData    : ARRAY[1..2] OF ST_CTRL_DIGITAL_FILTER_DATA;
    bError            : BOOL;
    fIn                : FLOAT := 0;
    fOut                : FLOAT;
    bInit                : BOOL := TRUE;
IF bInit THEN
    aCoefficientsArray_a[1] := 0.0; (* not used *)
    aCoefficientsArray_a[2] := 0.2;
    aCoefficientsArray_a[3] := 0.1;
    aCoefficientsArray_b[1] := 0.6;
    aCoefficientsArray_b[2] := 0.4;
    aCoefficientsArray_b[3] := 0.2;
    stParams.tTaskCycleTime := T#2ms;
    stParams.tCtrlCycleTime := T#2ms;
    stParams.nFilterOrder := 2;
    eMode := eCTRL_MODE_ACTIVE;
    bInit := FALSE;
END_IF
stParams.pCoefficientsArray_a_ADR := ADR(aCoefficientsArray_a);
stParams.nCoefficientsArray_a_SIZEOF := SIZEOF(aCoefficientsArray_a);
stParams.pCoefficientsArray_b_ADR := ADR(aCoefficientsArray_b);
stParams.nCoefficientsArray_b_SIZEOF := SIZEOF(aCoefficientsArray_b);
stParams.pDigitalFilterData_ADR := ADR(astDigitalFilterData);
stParams.nDigitalFilterData_SIZEOF := SIZEOF(aStDigitalFilterData);
fbDigitalFilter ( fIn := fIn,
                eMode := eMode,
                stParams := stParams,
                fOut => fOut,
                eErrorId => eErrorId,
                bError => bError);