FB_CTRL_ACTUAL_VALUE_FILTER
FB_CTRL_ACTUAL_VALUE_FILTER 1:
The function block allows a measured input value to be checked for plausibility and filtered.
Behavior of the output
FB_CTRL_ACTUAL_VALUE_FILTER 2:
This function block allows a plausibility check to be carried out on a measured input value. If the difference between two sampling values in sequence (measurements) is larger than the specified window, fDeltaMax, then the current input value is suppressed for a maximum of three cycles. During this time the output value is extrapolated from the previous input values. If the specified window is exceeded for more than three cycles, the output will again follow the input value. The behavior of the output is illustrated in the diagram above.
FB_CTRL_ACTUAL_VALUE_FILTER 3: Inputs
    fIn        : FLOAT;
    fManValue  : FLOAT;
    eMode      : E_CTRL_MODE;
Type
fIn
FLOAT
Input value of the filter
fManValue
FLOAT
Input value that is output in manual mode.
eMode
E_CTRL_MODE
Input that specifies the operation mode of the function block.
FB_CTRL_ACTUAL_VALUE_FILTER 4: Outputs
    fOut      : FLOAT;
    eState    : E_CTRL_STATE;
    eErrorId  : E_CTRL_ERRORCODES;
    bError    : BOOL;
Type
fOut
FLOAT
Output of the function block
eState
E_CTRL_
STATE
State of the function block
eErrorId
E_CTRL_
ERROR
CODES
Supplies the error number when the output bError is set.
Becomes TRUE, as soon as an error occurs.
FB_CTRL_ACTUAL_VALUE_FILTER 5: Inputs/ outputs
    stParams    : ST_CTRL_ACTUAL_VALUE_FILTER_PARAMS;
Type
stParams
PARAMS
Parameter structure of the actual value filter element
stParams consists of the following elements:
TYPE
ST_CTRL_ACTUAL_VALUE_FILTER_PARAMS:
STRUCT
    tCtrlCycleTime    : TIME := T#0ms;
    tTaskCycleTime    : TIME := T#0ms;
    fDeltaMax         : FLOAT;
END_STRUCT
END_TYPE
Type
tCtrlCycleTime
TIME
Cycle time with which the control loop is processed. This must be greater than or equal to the TaskCycleTime. The function block uses this input value to calculate internally whether the state and the output values have to be updated in the current cycle.
tTaskCycleTime
TIME
Cycle time with which the function block is called. If the function block is called in every cycle this corresponds to the task cycle time of the calling task.
fDeltaMax
FLOAT
Maximum difference between two input values in sequence. See description above.